Secondary pump speed - how much slower should it be?
Posted by: @derek-mPosted by: @davidalgarveThanks JamesPa - have only just picked this up.
I have the contractor visiting who is primarily a solar installer but he added the DHW system and I have a lot of respect for him, although he has some fixed ideas.
I have started to explain the perceived benefits of taking the buffer tank out of circulation, but it occurred to me that I am uncertain how I will decide on the speed of the built in Ecodan pump.
What method will I use to evaluate the performance at the available speeds?
I agree with James. I think that I am correct in saying that the water pump speed on the Ecodan can be varied from 1 to 5, so probably start with the pump set at 3 and see what DT you get. You may find that you need the pump speed lower in Summer and higher in Winter.
There is a recommended flow rate range for each model (its quite a large range), and I think you might be able to display measured flow rate. if you can, set it in the middle to start with.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Derek M is correct in that the Ecodan has a 5 speed pump and this is currently set at max of 5. I was just hoping for a meaningful measure of performance, either to optimise the system or to have reason to switch back to a two pump system, possibly with a better (and this time variable speed) secondary pump.
Posted by: @davidalgarveThanks JamesPa - have only just picked this up.
I have the contractor visiting who is primarily a solar installer but he added the DHW system and I have a lot of respect for him, although he has some fixed ideas.
I have started to explain the perceived benefits of taking the buffer tank out of circulation, but it occurred to me that I am uncertain how I will decide on the speed of the built in Ecodan pump.
What method will I use to evaluate the performance at the available speeds?
I have just remembered that with Ecodan's the water pump is external to the heat pump, and the water pump speed may not actually be controlled by the controller, it will just be started and stopped. If this is the case then the speed will have to be set on the pump itself, as James suggest with reference to the flowrate reading on the controller.
If you have two cables connected to the water pump, power and control, then it should be possible to vary the speed using the heat pump controller.
James / Derek. Over the last year or more there has been a lot of debate and speculation about the optimum flow rate for the Ecodan range. Some people favouring a high flow rate and some targeting a low flow rate. It would also appear that Mitsubishi have responded to this contradicting debate by issuing a new data book (October 2023) which now quotes a single optimum flow rate for each size heat pump model.
however a good flow rate is needed.... if the flow rate has been adjusted towards the lower flow range it will never be able to reach the full heat output potential when it’s needed. Likewise if the flow rate is too high the DT May drop too low.
What I've seen with out Ecodan is that it doesn’t need a variable pump with PWM control. The system selects one of the 4 part-load outputs then modulates within its range. This makes it very versatile in its output range. And provided with only one fixed flow rate.
the below chart shows the new optimum flow rates.
The new data book has also renamed the 4 compressor outputs see below
I also know the heat pump, when fitted with Mitsubishi cylinder they are usually fitted with plate heat exchanger and an integrated (adjustable) circulation pump. But when they have a 3rd party cylinder the circulation pump usually needs to be adjusted manually.
I am finding that this topic is becoming more complicated than I can handle.
As I understand the Ecodan Hydrobox, it has a single pump with 5 speeds available and I don't see anything which indicates that it compensates in any way, after a speed is selected. The resultant flow must, surely, depend on the pump curve at the chosen speed and the head imposed by the radiator system.
I have no means of measuring flow and I suggest that it is not a meaningful parameter. At the moment, I don't have temperature measuring on the radiator flow and return, but I can arrange for it to be fitted if I go ahead with the modifications involving removal of the secondary pump.
Am I correct in thinking, therefore, that the optimum pump speed setting must be the based on flow vs return temperatures and that a reasonable aiming point would be 5C.?
You are correct there are 5 speeds available set through the settings menu, under pump speed, these are fixed rates and the ecodan cannot change them. You can see the flowrate you are getting at each pump speed. In the same settings menu look for running information then type in code 540 and this shows the flow rate in litres/min.
Thanks Gary. That is a new, and interesting bit of inside information that I am pleased to learn. I think this may be useful in balancing the radiators and seeing how SRV's affect things.
However, I still do not see how knowing the flow in litres/ minute helps me to evaluate the best pump speed setting. Am I correct in saying that it it is Delta T that counts and if so, what figure am I aiming for?
The quantity of thermal energy being transferred from the heat pump to the heat emitters is dependent upon the flowrate and the DT. If you were to increase the flowrate from say 10 lpm to 20 lpm then you double the quantity of thermal energy, provided that the DT remains constant.
Reducing the DT from say 5C to 2.5C would halve the quantity of thermal energy being supplied.
Neither flowrate or DT are that critical, provided that both are within a range that allows the transfer of sufficient thermal energy under all expected operating conditions.
I would suggest that the water pump speed should be set to provide a DT of approximately 5C,when the heating demand is in the 50% to 75% of overall maximum. Don't be concerned if the DT varies from 5C, provided that your home achieves the desired indoor temperatures.
- 22 Forums
- 2,043 Topics
- 44.5 K Posts
- 43 Online
- 3,260 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Help me understand my Mitsubishi Ecodan system
@jamespa What was the date of the plot and what was...
By GergoH , 40 minutes ago
-
@fillib what a wonderful result, both for you personall...
By Judith , 2 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
Thanks for confirming you connected your 2 port valve t...
By Steam Powered , 4 hours ago
-
RE: Revised version of MCS-020 (noise standards for heat pumps)
As you say this is no change, which I personally think ...
By JamesPa , 5 hours ago
-
RE: What happens when the outside temperature exceeds the upper WC point?
@editor not via the WC curve but as @old_scientist ment...
By bontwoody , 6 hours ago
-
RE: MHHS and Heat Pump compatibility
@toodles to be clear I don't know if there will be a re...
By Scalextrix , 17 hours ago
-
I did not know this concept, although others might. I...
By Morgan , 22 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk it's probably filtering different providers in t...
By Mars , 24 hours ago
-
RE: why solar diverters for HW instead of the heat pump?
I should probably add to my comments above that, whilst...
By JamesPa , 2 days ago
-
RE: Commencing on an ASHP Installation Process
Lots of reading and questioning which the background ma...
By JamesPa , 2 days ago
-
RE: The Great British Heat Pump Quiz
Not sure how that happened 🤣 I suspect that it ...
By Mars , 2 days ago
-
RE: Help with understanding my Mitsubishi Ecodan air source heat pump
@patch I think @ashp-bobba gave you some great pointers...
By SUNandAIR , 3 days ago
-
RE: Installing your own ASHP - DIY
Hi @tomasmcguinness, how are you progressing with this?...
By Ashfp , 3 days ago
-
RE: Say hello and introduce yourself
Welcome to the forum. If you are new to ASHPs I sug...
By JamesPa , 3 days ago
-
RE: The Rise and Fall of Europe’s Most Generous Green Subsidy
This is where the cold water storage tank was situated;...
By Dwynwen , 4 days ago
-
RE: Air Source Heat Pump - Side Alley Suitability
Thats probably fair enough. The degree-days calculatio...
By JamesPa , 4 days ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
That’s interesting, but obviously concerning also…. Do ...
By SUNandAIR , 5 days ago
-
RE: In the middle of an ASHP installation - a few questions (and issues)
Thank you @robs - that very useful data. The issue wa...
By Transparent , 5 days ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
@trebor12345 The Auto function is supposed to adapt au...
By Heatgeek , 6 days ago
-
RE: help sizing rads based on room by room heat loss
If its 1988W at DT 50, which is how most radiators are ...
By JamesPa , 6 days ago