And we are now back down to 7.2lpm but heating is still goingÂ
If removing that strainer made a difference, then it's possible that something has become dislodged within the pipework.
We can't tell if that 'something' was an object within the body of the strainer,
or possibly elsewhere, and that the sudden loss of flow has moved it.
Equally, you will definitely have introduced fresh air by opening the strainer,
and that will require purging from the various release-valves over an hour or two.
Save energy... recycle electrons!
So, looks like it might be an incorrect sizing of primary pump. The installer (who was the subcontractor to who I used) came out and advise he was never given the heating design by the company who contracted him despite asking multiple times. When installing he pointed out that there was no primary pump ordered so the main contractor went and purchased one (the Evosta 3 60/130). What the installer and I think has happened is the main contractor has seen the price difference between the 60/130 and the 80/130 and went for the cheaper 60/130 (without actually understanding what those values mean).
Â
I am in the process of requesting the full heating design (they did come out and survey everything) which brought them to the conclusion of not needing any new radiators and an 8kW system. Will let you all know how I get on.
Â
P.S We also notice that even when the heating wasnt on, the secondary Grundfos pump was still running which seems to make the radiators cool down super quick if it's still pumping the water around and the ASHP isnt heating it. When we set DHW to on, the secondary pump goes off. Is this normal or has some mis-wiring occured?
Â
Thanks
@netdonkey The primary pump should stop after a while when there is no DHW or Heating demand, it may have an overrun to dissipate the small amount of heat left over but I am sure this is only for 30s on some systems. This pump should also be wired through the ASHP control and not on an independent supply with a switch on the wall.
Â
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
To add, the primary pump also can run for a while before the system fires up to confirm flow.
Â
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @ashp-bobba@netdonkey The primary pump should stop after a while when there is no DHW or Heating demand, it may have an overrun to dissipate the small amount of heat left over but I am sure this is only for 30s on some systems. This pump should also be wired through the ASHP control and not on an independent supply with a switch on the wall.
Â
Â
So the primary pump ( EVOSTA 3) does this, only comes on when required. The secondary pump which is at the bottom right of my setup picture which is attached the the flow towards the radiators is on all the time.
Â
Going to trace where it goes on the MIMÂ
Â
@netdonkey OK, so this Grundfoss pump should only turn on an off when required in heating mode as your system runs through a buffer, there will be some form of stat that controls this, its should ideally through the ASHP controls if you are using their smart controls linked to a main stat, or through the ASHP control when engaging heating mode which can also be via a 3rd party stat or controls. So it depends how they have set up your system.
Â
 Â
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba -Â any chance of a diagram please?
Pencil on the back of an envelope will do!
Save energy... recycle electrons!
@netdonkey Primary pump should run as follows:
Heating demand onÂ
DHW demand onÂ
Defrost demand onÂ
Secondary pump should run as follows:
Heating demand onÂ
Defrost demand on (only of the volume of the buffer is not enough for the min volume for the ASHP to defrost)
Â
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Do all ASHPs have that Primary Pump inside the building?
Or is it sometimes within the external heat-pump / heat-exchanger unit itself?
Save energy... recycle electrons!
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
8 months ago
-
Sudden drop in COP
1 year ago
-
Samsung's Cold Shoulder: Should Heat Pump Manufacturers Be More Accountable?
1 year ago
-
Any installer recommendations for Samsung ASHP?
1 year ago
-
Issue with Samsung A2W Heat Pump - Water Outlet Temperature
3 years ago
- 23 Forums
- 2,098 Topics
- 46.2 K Posts
- 54 Online
- 3,385 Members
Join Us!
Latest Posts
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 4 hours ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 4 hours ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 10 hours ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
Hmm Before doing that I would want to be certain that...
By JamesPa , 16 hours ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 16 hours ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 1 day ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 1 day ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 2 days ago
-
If you are thinking of heating on the immersion conside...
By JamesPa , 3 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness, I think your best bet would be using ...
By Aventus Eco , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles all depends on asking the right questions! And...
By Tim441 , 3 days ago
-
RE: Commencing on an ASHP Installation Process
I received confirmation this morning that my Greener Ho...
By Sheriff Fatman , 4 days ago
-
@jamespa Thanks for the advice - very helpful. I had al...
By abam48 , 5 days ago
-
RE: Adding battery storage to SolarEdge PV system
@chandykris No need to apologise at all! I forgot to ad...
By Toodles , 5 days ago
Members Online
No online members at the moment