And we are now back down to 7.2lpm but heating is still going
If removing that strainer made a difference, then it's possible that something has become dislodged within the pipework.
We can't tell if that 'something' was an object within the body of the strainer,
or possibly elsewhere, and that the sudden loss of flow has moved it.
Equally, you will definitely have introduced fresh air by opening the strainer,
and that will require purging from the various release-valves over an hour or two.
Save energy... recycle electrons!
So, looks like it might be an incorrect sizing of primary pump. The installer (who was the subcontractor to who I used) came out and advise he was never given the heating design by the company who contracted him despite asking multiple times. When installing he pointed out that there was no primary pump ordered so the main contractor went and purchased one (the Evosta 3 60/130). What the installer and I think has happened is the main contractor has seen the price difference between the 60/130 and the 80/130 and went for the cheaper 60/130 (without actually understanding what those values mean).
I am in the process of requesting the full heating design (they did come out and survey everything) which brought them to the conclusion of not needing any new radiators and an 8kW system. Will let you all know how I get on.
P.S We also notice that even when the heating wasnt on, the secondary Grundfos pump was still running which seems to make the radiators cool down super quick if it's still pumping the water around and the ASHP isnt heating it. When we set DHW to on, the secondary pump goes off. Is this normal or has some mis-wiring occured?
Thanks
@netdonkey The primary pump should stop after a while when there is no DHW or Heating demand, it may have an overrun to dissipate the small amount of heat left over but I am sure this is only for 30s on some systems. This pump should also be wired through the ASHP control and not on an independent supply with a switch on the wall.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
To add, the primary pump also can run for a while before the system fires up to confirm flow.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @ashp-bobba@netdonkey The primary pump should stop after a while when there is no DHW or Heating demand, it may have an overrun to dissipate the small amount of heat left over but I am sure this is only for 30s on some systems. This pump should also be wired through the ASHP control and not on an independent supply with a switch on the wall.
So the primary pump ( EVOSTA 3) does this, only comes on when required. The secondary pump which is at the bottom right of my setup picture which is attached the the flow towards the radiators is on all the time.
Going to trace where it goes on the MIM
@netdonkey OK, so this Grundfoss pump should only turn on an off when required in heating mode as your system runs through a buffer, there will be some form of stat that controls this, its should ideally through the ASHP controls if you are using their smart controls linked to a main stat, or through the ASHP control when engaging heating mode which can also be via a 3rd party stat or controls. So it depends how they have set up your system.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Save energy... recycle electrons!
@netdonkey Primary pump should run as follows:
Heating demand on
DHW demand on
Defrost demand on
Secondary pump should run as follows:
Heating demand on
Defrost demand on (only of the volume of the buffer is not enough for the min volume for the ASHP to defrost)
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Do all ASHPs have that Primary Pump inside the building?
Or is it sometimes within the external heat-pump / heat-exchanger unit itself?
Save energy... recycle electrons!
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
-
First time wall mounting an ASHP
1 month ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
2 months ago
-
Samsung problems
3 months ago
-
Sudden drop in COP
4 months ago
-
Samsung's Cold Shoulder: Should Heat Pump Manufacturers Be More Accountable?
2 years ago
- 26 Forums
- 2,342 Topics
- 53 K Posts
- 289 Online
- 6,000 Members
Join Us!
Worth Watching
Latest Posts
-
I thought this might be the most appropriate place to r...
By F1p , 19 minutes ago
-
RE: Commencing on an ASHP Installation Process
Fair play for giving this a go, and please do report ba...
By benson , 2 hours ago
-
RE: LiFePO4 lithium battery fires and explosions
Yes, more than an adjustment... This is the only comb...
By Batpred , 9 hours ago
-
RE: Poll for Time of Use, tariffs, technology
@old_scientist Interesting point, but I suspect that's ...
By Sheriff Fatman , 10 hours ago
-
RE: Different dT on each radiator?
I cant sorry. Its based on some calculations I did fro...
By JamesPa , 12 hours ago
-
RE: Setback savings - fact or fiction?
Maybe this: or maybe that the effect you are seein...
By JamesPa , 13 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@simonf thats interesting as I’ve noticed my flow and r...
By AdamK , 21 hours ago
-
RE: MELcloud scheduling misbehaviour
No, it gets to set temperature easily even during perio...
By Abernyte , 22 hours ago
-
RE: Free Ecoheat Heat Pump Install
Sorry hit 'add reply' too early, this forum layout will...
By Deltona , 23 hours ago
-
And arguably even more important, sodium will be hopefu...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
I've been thinking of emailing Homely to ask for a few ...
By JohnnyB , 2 days ago
-
Max output of Heat pump (Daikin 4Kw EDLA04)
Hello, I am a bit puzzled that according to pcdb tes...
By GeorgeA , 2 days ago
-
In that case, @technogeek, I’d sign up for the free sol...
By Majordennisbloodnok , 2 days ago
-
RE: Has Anyone Else Noticed a Decline in Tradesmanship?
@cathoderay Hence my rider about ‘all else being equal’...
By Toodles , 2 days ago
-
RE: Heat Pump Performance Analysis Web App using Modbus Data
@redzer_irl — all my heat pump data is in csv files, me...
By cathodeRay , 2 days ago
-
RE: Configuration issues with 10kW Midea R32 heat pump
@benson I believe there are quite a few of these instal...
By Toodles , 2 days ago
-
RE: 10kw heat pump run in 24*7 data?
I would say you most likely do need 10kW. My gas consu...
By JamesPa , 2 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@thundermink I managed to find the fault. I did it a lo...
By meehow , 2 days ago