Samsung ASHP scheduling help
@broadsman the #2093 setting should be "Room Temp. only ON / OFF" for the Gen 6 controller.
Please make sure #2091 and #2092 are set to "not use" and any external third party thermostats are disconnected.
I did get an error myself but it looked like a flow interruption if I remember correctly. I think it is caused by the change in mode, I just pressed OK and it cleared then everything was running ok. The error for me was "Indoor (200000) / E121" for your info.
Regards
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat
@mike-h I do have the 12Kw Samsung Gen 6 model.
Just to clarify, if you go to the Zone screen you should have the target room or water temp on the left and "Water Outlet" and "Indoor" temperatures on the right. These indicate the actual temperatures the system is seeing
Regards
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat
@mike-h my pump does switch off when the room temp goes 0.5C above my target temp but this only happens with solar gain or my hand is near the controller too long. Most of the time it appears to keep the room at the target temp of 20.5C and the pump running continuously.
Here is my firmware version info
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat
Posted by: @mike-hI wonder if your ability to keep room temperature at +/- 0.3C is because you have got your water law settings perfectly set rather than feedback from the controller.
I did a little experiment last night and changed my water law setting to a flat 37C (WL-1) to verify if the controller configured as the thermostat still used this water law or calculated its own water temperatures based on the outside temperatures. It appears that the controller still uses the water law set in WL-1 in my case. The pump continuously runs due to the On /Off only setting in #2093 but the water outlet temperature basically stabilised at 37C for an outside temperature of 6.5C (should be around 44Cish).
In my case @mike-h your assumption is correct and my water law is set about right and is still being used.
This is not the behaviour implied in the video I posted in an earlier posting which indicates the pump "looks at the outside temperature and decides the required temperature to set your radiators to to achieve the indoor temperature set point. When the temperature is reached the pump is reduced to maintain the internal temperature set point" (not verbatim). The radiator temperature seems to still be based on the water law settings for the Gen 6 not some implied clever internal feature.
Apologies for misleading anyone 🙂
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat
- 26 Forums
- 2,153 Topics
- 47.3 K Posts
- 31 Online
- 5,673 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Failing heat pump system - seeking thoughts on a rebuild
Will do! Thanks for everyone’s thoughts so far, it’s al...
By Cleardene-ashp , 8 minutes ago
-
RE: Electricity price predictions
Community energy installations are a great idea, but th...
By Scalextrix , 3 hours ago
-
RE: Can you help with our research: solar panels, EV chargers, home batteries, heat pumps?
I have signed up as well. @belsnugg could you outline ...
By JamesPa , 11 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Ooh, heat pumps in neon blue wrap 🤣 🤣 &...
By Old_Scientist , 11 hours ago
-
@profzarkov Good to know in case it ever happens to me...
By bontwoody , 1 day ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
I mean, is this surprising? The local installers in my ...
By Alex , 1 day ago
-
@old_scientist sorry, I should have made it clear that ...
By GrahamF , 1 day ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@thundermink can you provide photos to illustrate your ...
By Morgan , 1 day ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 1 day ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
After our rather lengthy meander off piste, I thought I...
By GrahamF , 1 day ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - to collect the IAT/OAT data, can I sugges...
By cathodeRay , 2 days ago
-
RE: Ecodan software update. Real or scam?
@vinz86 Contact Mitsubishi and an engineer attends and ...
By ASHP-BOBBA , 2 days ago
-
@drei When I was in local government we were of cours...
By JamesPa , 2 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Sufficient system volume is also essential for ensuring...
By Old_Scientist , 2 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 3 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 3 days ago
-
RE: Octopus tariffs - a quick comparison
@tim441 I’d agree wholeheartedly with that, with 2 x Po...
By Toodles , 3 days ago