Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Replacing Storage Heaters with a Heat Pump in a Stone Cottage

68 Posts
8 Users
10 Reactions
4,357 Views
bobflux
(@bobflux)
Reputable Member Member
Joined: 9 months ago
Posts: 211
 

https://www.ubakus.de/en/r-value-calculator/

This tool lets you input the makeup of your wall, ceiling, roof, etc, and calculates U/R-values.

It can also simulate summer comfort, thermal mass, dew points, condensation in the insulation, whether it will dry in the summer or not, etc. Extremely useful.

 



   
ReplyQuote
cathodeRay
(@cathoderay)
Famed Member Moderator
Joined: 5 years ago
Posts: 3123
 

Posted by: @bobflux
↑

This tool lets you input the makeup of your wall, ceiling, roof, etc, and calculates U/R-values.

Excellent find, thanks for posting the link here.


Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote
(@paul1098)
Eminent Member Member
Joined: 2 months ago
Posts: 26
Topic starter  

@bobflux Thanks, that gives me something to check the inbuilt u values with. There looks like a lot more once you've found your way around it.



   
ReplyQuote
(@paul1098)
Eminent Member Member
Joined: 2 months ago
Posts: 26
Topic starter  

@cathoderay https://www.stelrad.com/starsapp/login - you have to setup an account and I can't remember how onerous it is as it was 10 years ago when I started using it.

MCS and British standards do have air change values that generally seem to be 0.5 (I assume that's room volumes but not fully checked that yet) they also include for chimneys and extractors so comprehensive.

Just had my first quote of over £18k so if that's the general cost of an ASHP + central heating install for a small 2 bed cottage then my journey will be stopping and i'll go for LPG.


This post was modified 1 month ago by Paul1098

   
ReplyQuote
cathodeRay
(@cathoderay)
Famed Member Moderator
Joined: 5 years ago
Posts: 3123
 

Posted by: @paul1098
↑

you have to setup an account and I can't remember how onerous it is as it was 10 years ago when I started using it.

I fully sympathise with any wish not to have to sign up to spurious accounts but the link I posted was for the correction factor table, which is freely available, you then do your own calculations.

Posted by: @paul1098
↑

MCS and British standards do have air change values that generally seem to be 0.5

ACH value recommendations have come down recently, but again best to use numbers that make sense to you. I've always taken the value to .mean what it says' 1 ACH means the volume of air in the room is replaced every hour.

Posted by: @paul1098
↑

Just had my first quote of over £18k so if that's the general cost of an ASHP + central heating install for a small 2 bed cottage then my journey will be stopping and i'll go for LPG.

Is that with or without the BUS grant? And how much extra work does it include?

 


Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5629
 

Posted by: @cathoderay
↑

I fully sympathise with any wish not to have to sign up to spurious accounts but the link I posted was for the correction factor table, which is freely available, you then do your own calculations

Standard rad output is proportinal to dt^1.3 where DT is the difference between room temp and average rad temp.

No need to sign up you can calculate it yourself unless you are using funky rads.

 

Posted by: @paul1098
↑

Just had my first quote of over £18k so if that's the general cost of an ASHP + central heating install for a small 2 bed cottage

Unless there are some major difficulties this is high, very high.  It's standard practice throughout the construction industry to provide a very high quote if you don't want the work.

My recommendation is get more quotes and as @cathoderay invites tell us about the job so we can give you a steer.


This post was modified 1 month ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
cathodeRay
(@cathoderay)
Famed Member Moderator
Joined: 5 years ago
Posts: 3123
 

Posted by: @jamespa
↑

Standard rad output is proportinal to dt^1.3 where DT is the difference between room temp and average rad temp.

No need to sign up you can calculate it yourself unless you are using funky rads.

The freely available table I linked to just simplifies the calculation to a single multiplication:

 

image

 

As you can see, the correction factor is about 0.5 at typical to higher (eg my system) heat pump delta t values, hence the half the delta 50 output rule of thumb. For lower delta t values, one third of the delta t output isn't a bad estimate. But for a full spec, you need to use the correct correction factor for your particular delta t. 

 


Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote
(@rob-of-york)
Reputable Member Member
Joined: 3 months ago
Posts: 168
 
Posted by @paul1098
 
Just had my first quote of over £18k so if that's the general cost of an ASHP + central heating install for a small 2 bed cottage then my journey will be stopping and i'll go for LPG.
 
Wow, that is expensive; however, I assume that it is for an air-to-water heat pump system with all the extra work and upheaval that fitting pipework and radiators entails, plus all the gold-plating required to get the BUS grant. Perhaps consider forgetting about the large subsidy that effectively pushes you down a route that is far from economically viable without it. Rather, I would suggest that you get multiple quotes for a simple air-to-air system with a multi-split outdoor unit and indoor units in only those rooms that really need them, likely no more than three. Some simple direct electric heating in other rooms (e.g. electric radiator, electric towel rail) and retain your existing immersion heater. A good competitive quote for that and you may well be looking at less than 1/3rd of the price you have been quoted for air-to-water. As a bonus you get highly efficient cooling in summer too! 
 
Compared with A2A, LPG would be very expensive in terms of running costs, particularly if the property was occupied all year. I've just run the numbers for my brother based on 6000 kWh of heating with his new A2A system on a heat pump tariff. It is going to save him about £425 a year compared to mains gas. Considering A2A SCOP 5.2, 15p per unit electricity on a heat pump tariff, 9p per unit for gas 0.9 efficiency, £173 for A2A, £600 for gas. I think LPG works out around 14p per kWh at present, boiler still 0.9 efficiency, so that would be about £933 or over £760 per year more expensive than A2A - ouch!
 
If you want hot water and air-to-air via a heat pump then take a look at the Daikin Multi+ split system that does it all in one unit. That would be quite a lot more expensive assuming that you got a new hot water tank with it, but arguably a very good solution overall.
 

This post was modified 1 month ago 3 times by Rob of York

   
ReplyQuote
(@paul1098)
Eminent Member Member
Joined: 2 months ago
Posts: 26
Topic starter  

Posted by: @cathoderay
↑

ACH value recommendations have come down recently, but again best to use numbers that make sense to you. I've always taken the value to .mean what it says' 1 ACH means the volume of air in the room is replaced every hour.

I always thought the same but I have seen m3/m2 quoted which is got me wondering but that could just be a mis-quote.

Posted by: @cathoderay
↑

Is that with or without the BUS grant? And how much extra work does it include?


That included the BUS. It included for 5 rads, HWT, controller and central heating pipework.

 



   
ReplyQuote
(@paul1098)
Eminent Member Member
Joined: 2 months ago
Posts: 26
Topic starter  

@rob-of-york My reasoning for the move away from storage heaters was to make life easy when the house is sold.
I think that if i can get A2W at a sensible price then it would be more acceptable to the general public than A2A although A2A is probably preferable to storage heaters.
LPG might not be ideal but it is what a lot of people are used to when 'off grid' and not able to fit oil storage.

The first quote was a toe in the water to confirm that it was possible to fit an A2W system. More quotes required and probably from good old fashioned plumbers that do full systems as well as A2W and also some companies doing A2A.

The self imposed constraint i have is value for money, if the new heating system can be close to cost neutral when compared to the increase in house value then it's worth doing if not i'll stick with my storage heaters.



   
ReplyQuote
cathodeRay
(@cathoderay)
Famed Member Moderator
Joined: 5 years ago
Posts: 3123
 

Posted by: @paul1098
↑

I always thought the same but I have seen m3/m2 quoted which is got me wondering but that could just be a mis-quote.

I have just had a look at how the freedom Heat Loss uses and calculates ACH values. The actual values are by default look up values based on room type from a hidden table, which has by it "m^3/hr per m^2 of xternal area at 50pa". Go figure... The actual calculation to get the resultant loss in watts for bedroom 1 is =((B25-$B$13)*0.33*(B31*B26)*C39) which breaks down to (design room IAT - design OAT) x 0.33 x (room height x floor area) x the looked up ACH value (1.00 in this case). Most online sources say the ACH number represents the number of total air changes within one hour, ie a value of 1 means all the air is changed once an hour, 2 means twice an hour etc ie our general understanding is correct. How that simple concept then ends up with units of "m^3/hr per m^2 of xternal area at 50pa" is beyond me. To me, the unit is 'air changes per hour' and it simply means what it says! 1 ACH means the air changes once an hour! No doubt others (@jamespa? @rob-of-york?) can enlighten us further.

Posted by: @paul1098
↑

That included the BUS. It included for 5 rads, HWT, controller and central heating pipework.

Just to be absolutely sure, total cost is just over £18k, of which you would pay that less any grant you get?   

 


Midea 14kW (for now...) ASHP heating both building and DHW


   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5629
 

Posted by: @cathoderay
↑

1 ACH means the air changes once an hour! No doubt others (@jamespa? @rob-of-york?) can enlighten us further.

Exactly that.  Dimensional analysis (the powerful and occasionally useful technique of working out what the answer and the formula is measured in, in terms of the fundamental dimensions of the universe - length, time, mass etc) will confirm.  I will post the full explanation later if nobody else does and anyone is interested (both of which seem unlikely)


This post was modified 1 month ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   