@technogeek congrats on the high quality install. It’s great to read success stories. Is the installer a sole trader or a company. Would be worth recommending him.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
Follow our sustainability journey at My Home Farm: https://myhomefarm.co.uk
@editor Hi Mars, he is a sole trader who has installed a system at a neighbours property including my own. As he is a sole trader I will forward details to him and if he wants to promote his business on this site (via yourself) then he can take it further 🙂
All I need now is the price of electricity to come down and things will be peachy! 🤣 🤣
" A heat Pump OR an Oscillator ?"
" Four Pipe Buffer Tanks OR Volumisers"
My Heat Pump continues to Oscillate or "Short Cycle " :
Taking the advice from Samsung, DECC , Kensa and the MCS to fit a "50 litre Buffer Tank " :
My "Installer " fitted a 50 Litre Buffer Tank in October 2022.
The 50 Litre Buffer tank was fitted with a Valve to experimentally limit Energy Consumption .
When selected the Buffer makes a very limited change to the oscillations.
I have now found that the 4 pipe Buffer Tank water Temperature differs from the Temperature of the water in the Buffer Connecting pipe:
Clearly, the Buffer Water Temperature SHOULD be the INTEGRAL of the TEMPERATURE at the Buffer Input PORT.
It Clearly is NOT the Integral of the Water Temperature.
The Conclusion is that my Heat Pump has been fitted with a 4 pipe Buffer instead of a Volumiser!
A second conclusion is that the Volumiser SHOULD HAVE BEEN FITTED ACROSS THE OUTPUT PORTS OF THE HEAT PUMP!
My Heat Pump NEEDS a TWO PORT VOLUMISER OF 50 litre capacity fitted across the Heat Pump Output ports to Reduce these Violent Oscillations.
Given that my Oscillator Heat Pump has already cost ~£14K I have No confidence in my "installers" or the "Experts".
" Short Cycling", Thermal-Syphoning
My Heat Pump displays "Short Cycling":
The Standard Solution to "Short Cycling is the use of a Buffer Tank :
My Buffer tank appears to provide no solution to the Cycling Problem:
The graph showing the Temperature Difference between my Buffer feed pipe and the Buffer Water Temperature itself!,
with DS18B20 Temperature Sensors being used to measure Water Temperature in the Buffer Tank and the Buffer Tank feed pipe.
Notice the Buffer Water Temperature going Negative with respect to the Radiator Feed Temperature!
The Buffer appears to be dumping it's Heat Energy when the Heat Pump switches OFF
This effect , Thermal-Syphoning is shown at
https://blog.heatspring.com/2-pipe-versus-4-pipe-buffer-tank-configurations/
with the solution to "short Cycling" being the introduction of Thermal Swing Check-Valves or Spring loaded Check-Valves.
When the Heat Pump is warmer than the Buffer the Check valve is OPEN , when, however the Buffer Tank is Hotter than the Heat Pump the Valve closes.
The Thermal efficiency should be improved with the introduction of "Swing Check Valves between the buffer and the Heat Pump and Spring loaded Check valves between the Buffer and the load.
Two Port OR Four Port Tanks?
Two Port Buffer Tanks are used extensively in Europe while the USA prefers the use of Four Port Buffer Tanks.
"Black Pipe Water "?
Both TWO PORT & Four Port Buffer Tanks store Black Particulates on to the floor of the Buffer tank, requiring removal by pressure cleaning.
The Short Cycling itself tends to exacerbate the "Black Ink" Problem as shown in the BS7593:2019 .
Quite some time ago it was pointed out that because your system has a buffer tank and a plate heat exchanger, that it could not work efficiently.
Since you ignored the advice provided at the time, your system will continue to work inefficiently and short cycle until you resolve these problems. I'm afraid continually posting on the forum will not resolve these problems.
Attacking other "experts" Does NOT inspire confidence!
Heat Pump Thermal-Syphoning
My Samsung 5kW Heat Pump , now in it's second Spring Season of "Short Cycling" shows every sign of destroying itself!
With Spring Weather my Heat Pump, like many others, cannot reduce it's power below it's minimum Inverter power of 2.5 Kw, and oscillates :
My Samsung 5kw Heat Pump is inefficient with a current loss of 26% of Energy:
The NIC having STRUCK_OFF my "Installer" now says that " You are NOT GOING to like this ............but Nothing CAN be DONE!!"
The Heat Pump , fitted with a 50 Litre Buffer , continues to exhibit "Thermal-Syphoning " :
with a negative -10/-15 C Temperature Drop between the Buffer output Pipe and the Buffer Water Temperature itself!
This is Thermal -Syphoning, the dumping of energy stored within the Buffer back into the Heat Pump itself.
This Thermal -Syphoning is used by the Heat Pump during de-icing.
The Buffer was originally to be fitted by SAMSUNG-DALLIAM to fix another problem ............. DE-icing !!
Having Spent circa £14K on the Heat Pump I have neither confidence nor money!
Many "engineers" and "experts" have now inspected my Heat Pump .......but none have inspired confidence!
Many "experts" have voiced their opinions , usually completely contrary to each other!
Attacking other "experts" Does NOT inspire confidence!
@derek-m @iantelescope @editor
I am probably making a mistake wading into this but...
Sometimes in life bad things happen, its a fact.
In this case it appears that @iantelescope has a bad experience with his heat pump. As the 'victim' of bad things one has a choice. Accept it, however unfortunate, and try to do something about it (if necessary trying several things until one of them works), or forever suffer from it.
The former has the distinct advantage that you regain some level of control and hope, the latter cedes all control and hope to others (or nobody if there is nobody who cares). Obviously there are times when the former is literally impossible, such as if the bad thing is fatal, but some poor building work is unlikely to be one of those times. In this particular case I would argue that the way out (if there is a way out), is to accept it and try to do something about it.
The options involving 'the industry' stepping in, admitting responsibility, and fixing it seem (sadly) to have been exhausted. That's a pity, but appears to be a fact. Fortunately there are communities of people, who have no vested interest, yet are willing to offer advice. Furthermore, unlike many 'experts' in the industry, they are willing to explain their reasoning. This is important because it exposes their suggestions to peer review, and allows you to judge what you do believe and what you don't.
This being the case the only remaining 'do something' option appears to be to try what the community has suggested and peer-reviewed. If this is, for any reason not acceptable, then 'forever suffering from it' appears to be the inevitable result. Put simply, if you don't change something then nothing will change.
If I were in the position that @iantelescope is in, then I think I would listen to the community, on the grounds that the alternative appears to be too depressing to contemplate. I have done this many times with software that doesn't perform as one might expect it to do (I admit its a lesser problem, but the same principle).
Of course its entirely a personal choice how to proceed. However, if doing nothing is the direction of choice, then it is perhaps a bit unfair on the community who is trying to help not (a) to declare that the intent is to do nothing, so that the community knows that offering suggestions is pointless and (b) to continue raising the issue when there are many other problems that the community is trying to solve and where action might actually occur.
I acknowledge that the above is, in essence, a long winded way of saying what @derek-m said above, but perhaps it explains some of the thought processes that are going through my head in relation to this knotty problem.
I must apologise to yourself for my Scottish Scepticism.
Many thanks James, Believe me when I say I Appreciate your response .
Some of the Correspondents on this site seem intent on derision , merely generating paranoia by their Very tone..........very Twitter or "X " like !
My last confrontation with my , now former "installer " and an Engineer from the NIC finished with the "Experts" leaving with my Heat Pump completely inoperative, issuing numerous Warnings . I later successfully undid the "experts" settings.
My previous confrontation was with a French SAMSUNG Engineer who left, later producing a "secret" Report only shown to my then "installer".
The "Secret Report" was briefly shown before being spirited away by my "installer " literally when my back was turned!
Apparently you cannot have the customer understanding his Heat Pump problems!
These confrontations follow a sequence of "discoveries " where my "installer" failed to install a Flow Switch (Four times!) ,Expansion vessel , PRV , Thermostat and Buffer .........on and on. Confidence in "my Installer" , SAMSUNG-DALLIAM and NIC Completely destroyed!
Two years of this have completely destroyed any confidence in this industry ...........However, I must apologise to yourself for my Scottish Scepticism.
My final plea is for some appreciation of the statement from the NIC :
" You are NOT Going to like This ........................................But Nothing Can be Done for your Heat Pump!".
This statement follows many previous Verbal statements from the NIC that :
" If All else fails ...........the NIC will repair and Replace the Heat Pump!".
As a matter of interest have a look at the presentation in the Book :
Modern Hydronic Heating & Cooling by John Siegenthaler
This is How to teach about Heat Pumps . Loads of Diagrams Heat equations , numbers , confidence.
Posted by: @iantelescopeApparently you cannot have the customer understanding his Heat Pump problems!
That attitude isn't unique to heat pumps, many tradesmen exhibit it. The number of times I have either been told that it's 'complex' or simply given a load of BS, is too large to count.
It makes my blood boil. Internally my reaction is always the same - if you can't explain it to me, then obviously you don't actually understand it. Sometimes I will say this out loud, most often I will just tell them to go away. The people who actually understand things can explain them to any reasonably intelligent person, the rest are just chancers.
@jamespa When I had the heat pump installed and later, when a second Powerwall was added to the existing setup by the the same teams, I frequently came across comments relating to my desire to know the technical details. One said to me; ‘I’m not trying to be funny but we come across customers much younger than yourself who don’t have the technical understanding to ask the questions you have!’ I found that the leaders of the teams (both electrical and plumbing) were only too pleased to be asked about their installation work. I also spent a fair amount of time with the MD of the company discussing various aspects of the installation - he listened, he answered and where necessary made the changes I requested.
This is fine in a way but, what happens when a customer does not know enough about what is required and has little interest in doing so but wants to just ‘Leave it to the Experts’? They may be even less inclined to want to carry out any investigating to ensure their system is optimised for them. Yes a good installer should ensure that this is a satisfactory situation and the heating system will require minimal attention from the householder - it should just work … and work well.
I think that most readers of the RHH are similar to myself, and many like me will have had a good experience; there are unfortunately, others who have not. Again, if we are to believe the MCS blurb, we are all concerned unnecessarily!😉 Regards, Toodles. (Cloud Cuckoo Land costs extra Luv)
Toodles, 76 years young and hoping to see 100 and make some ROI on my renewable energy investment!
Logically, addressing hard water issues with a water softening solution seems like common sense ie to preserve good flow rates for an ASHP system, but I’m keen to hear any views from the experts.
Moved in a few years ago, heat pump already installed. Heating bills very high and looking to optimise performance as much as possible (from browsing these forums, my system appears to show many other red flags too!)
thanks
@mjw321 welcome to the forums. Please start a new topic dedicated to your system and share some of the red flags.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
Follow our sustainability journey at My Home Farm: https://myhomefarm.co.uk
-
Mid terrace - ASHP Install location
1 month ago
-
Any installer recommendations for Samsung ASHP?
2 months ago
-
Ecodan - optimal external installation?
2 months ago
-
Does your heat pump calculate and provide you with a COP figure?
4 months ago
-
Any recommendations for ASHP installers in the North West?
11 months ago
- 24 Forums
- 1,413 Topics
- 29.7 K Posts
- 42 Online
- 1,199 Members
Join Us!
Latest Posts
-
RE: Gas Combi to ASHP - Making sense of survey results and proposal.
@irmartini 😄
By Toodles , 24 mins ago
-
RE: Fossil Fuel Fired Heating v Heat Pump?
Another aspect was the DHW heating; the coal fire in th...
By Toodles , 50 mins ago
-
In an ideal world a heat pump unit would contain two co...
By Derek M , 14 hours ago
-
RE: ASHP Advice: High Temperature vs. Low Temperature Heat Pump For Microbore
@jamespa I fully agree with James that a HT heat pump...
By Derek M , 15 hours ago
-
RE: Installing your own ASHP - DIY
@tomasmcguinness Have you been able to perform any sani...
By IanMK13 , 19 hours ago
-
RE: Viessmann Vitocal 250-A in the UK
For reference, I have a 10 kWh Viessmann 151-A installe...
By GC61 , 21 hours ago
-
RE: Vaillant Arotherm Settings for New Installation
@drew-pa Ah thanks. Good to know I dont have a misconce...
By bontwoody , 22 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
On the whole marketing claims vs reality on performance...
By GunboatDiplomat , 22 hours ago
-
RE: Microbore Central Heating Plumbing, will it be a barrier / pain?
@mattc All the existing (designed for T50) radiators ar...
By IanMK13 , 2 days ago
-
The temporary fix has reconnected about 60% of users, a...
By Abernyte , 2 days ago
-
RE: What is Wrong with our Heat Pump Installation?
Having to run the heat pump during the summer for DHW s...
By Toodles , 2 days ago
-
Issues with Vaillant connectivity via the MyCONNECT gateway
I'm sensing a variety of issues with Vaillant connectiv...
By dr_dongle , 2 days ago
-
Interesting heat pumps installations
Thought it would be cool to share photos of interesting...
By Mars , 2 days ago
-
RE: Say hello and introduce yourself
@Toodles That's very interesting to hear, thanks. I ha...
By dr_dongle , 2 days ago
-
RE: Massive Electricity Cost for Running My Air Source Heat Pump
@allyfish In fairness installer has replied stra...
By Holts , 2 days ago
-
-
RE: Are Solar Diverters Necessary for Homes with ASHPs and Solar PV?
@zzxap19 that's a fair point. With the eddi, is it poss...
By Mars , 3 days ago
-
RE: Delivering a smart and secure electricity system: government consultation
"I don't think I'll need to refer to past iterations of...
By eggnchips , 3 days ago
-
RE: Error on Immersun – Error 8 Load Short Circuit
@julesmp8 fingers crossed. I have to say our Immersu...
By Mars , 4 days ago
-
Latest Topics
-
Interesting heat pumps installations
By Mars 2 days ago
-
What is Wrong with our Heat Pump Installation?
By Mars 3 days ago
-
Fossil Fuel Fired Heating v Heat Pump?
By Toodles 3 days ago
-
Viessmann Vitocal 250-A in the UK
By treehugger 4 days ago
-
By HUBB84 7 days ago
-
By jswhite 7 days ago