What happens during the transition from winter to summer with your heat pump?
just curious as obviously if i go down the route of weather comp open loop system setup, which most seem to say is the most efficient, what happens as the weather warms to the point where the house needs less and less heat to maintain 20c say? surely you get to a point where the HP starts cycling as it can no longer modulate down any further, and conversely as autumn approaches when it starts to need more heat.
as ive watched lots of HG and QA vids but most talk about the other end where its maybe -3 and getting to the limit of the HP maybe.
You are correct the heat pump will cycle on and off at any temperature if it cannot modulate down far enough to maintain the flow temperature. Open loop gives the system the best chance of delaying that point by having the maximum amount of water engaged and no rads or ufh zones shut off.
This is when a simple on/off thermostat is useful as the house will get to temp and then shut off the heating till the thermostat calls for heat that could be hours later.
Cycling is only bad for the heat pump compressor when you are stopping and starting multiple times an hour, how many is acceptable is debatable but multiple stop/starts are bad.
My system will go down to 25C flow temp but it won't go below 32C flow without cycling 2/3 times an hour so I don't run it lower than that.
You should also be able to set an outside air temperature at which the system will turn off.
- 26 Forums
- 2,342 Topics
- 53 K Posts
- 272 Online
- 6,000 Members
Join Us!
Worth Watching
Latest Posts
-
RE: LiFePO4 lithium battery fires and explosions
Yes, I think we need to move away from the Sodium alter...
By Transparent , 3 minutes ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
@jamespawhite, if you could be bothered, you could also...
By Mars , 17 minutes ago
-
RE: Poll for Time of Use, tariffs, technology
The cynical answer is that perhaps they don't want us m...
By Majordennisbloodnok , 31 minutes ago
-
Let's not forget that "good enough" is a variable term....
By Majordennisbloodnok , 1 hour ago
-
Mitsubishi Ecodan 11.2kW heat pump with low COP
Hello everyone, I’m new here.Here are some details abou...
By Ciocoiu Alexandru , 1 hour ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
@ksim, I agree with you that HG has essentially evolved...
By Mars , 1 hour ago
-
RE: Commencing on an ASHP Installation Process
I've got a bit of time to draft something today, so the...
By Sheriff Fatman , 16 hours ago
-
RE: Setback savings - fact or fiction?
The predicted values are based on assumptions and it is...
By RobS , 16 hours ago
-
RE: Help with heat pump sizing
@amin I dont think materially relative to t...
By JamesPa , 18 hours ago
-
@majordennisbloodnok I have decided to take the plunge....
By TechnoGeek , 19 hours ago
-
RE: Configuring third party dongle for Ecodan local control
@sheriff-fatman might be interested in this, f...
By F1p , 1 day ago
-
RE: Different dT on each radiator?
I cant sorry. Its based on some calculations I did fro...
By JamesPa , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@simonf thats interesting as I’ve noticed my flow and r...
By AdamK , 2 days ago
-
RE: MELcloud scheduling misbehaviour
No, it gets to set temperature easily even during perio...
By Abernyte , 2 days ago
-
RE: Free Ecoheat Heat Pump Install
Sorry hit 'add reply' too early, this forum layout will...
By Deltona , 2 days ago
-
And arguably even more important, sodium will be hopefu...
By Batpred , 2 days ago
-
RE: A Smarter Smart Controller from Homely?
I've been thinking of emailing Homely to ask for a few ...
By JohnnyB , 3 days ago
-
Max output of Heat pump (Daikin 4Kw EDLA04)
Hello, I am a bit puzzled that according to pcdb tes...
By GeorgeA , 3 days ago