Pipe Work Question?
I'm in that common situation where after having a heat pump installed and the performance isn't great, I've dived into youtube and forums like this only to realise that maybe my installer didn't design/install/set up the system particularly well.
I'm in a good situation that I still owe them over £600 for some of the work, which means I can hold that over them. The question I have is about the main pipe work for the flow and return from the HP unit. I have a 3.5m section in my loft that is plastic 22mm pipe, not copper like all the other pipe work. I understand that this will have reduced internal diameter and thus flow, maybe costing me efficiency. Should I hold back final payment and insist this is changed (along with a few other niggles I've found) or is it minor enough not to worry about?
(should add Samsung Gen6 8kw, on two bedroom victorian mid terrace)
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
I think the 22mm plastic pipe might be a bit small for 8kw. 22mm copper is considered ok for 5kW I think. This link gives more detail. https://www.heatgeek.com/does-my-pipework-need-upgrading-for-a-heat-pump-with-cheat-sheet/
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
The issue with the 22mm plastic piping in your loft could potentially impact the efficiency of your heat pump system, especially if it differs from the rest of your installation in terms of diameter. We have this issue where the previous owners “narrowed” the pipework when they extended the heating to the north end of the house, creating a bottleneck which I think is the major issue that the rads at the far end of the house struggle.
Did your installers run all the pipework for your system - copper and the 3.5m run in the loft?
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor Yes so the pipe work from the HP that runs externally to the loft is copper, then the pipe work runs length of loft to the other end where the DHW tank is, that section inside the loft is plastic. I need to measure accurately to check diameters, but im fairly certain that it’s the same as the copper pipes.
Thinking about it now, all l the pipe work externally from the HP is insulated, I’ve assumed it copper, but don’t know for sure, I might have to check that.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
There is a good video explaining the pipe sizing issue here
https://renewableheatinghub.co.uk/forums/postid/29119
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @ecobakerI'm in that common situation where after having a heat pump installed and the performance isn't great, I've dived into youtube and forums like this only to realise that maybe my installer didn't design/install/set up the system particularly well.
I'm in a good situation that I still owe them over £600 for some of the work, which means I can hold that over them. The question I have is about the main pipe work for the flow and return from the HP unit. I have a 3.5m section in my loft that is plastic 22mm pipe, not copper like all the other pipe work. I understand that this will have reduced internal diameter and thus flow, maybe costing me efficiency. Should I hold back final payment and insist this is changed (along with a few other niggles I've found) or is it minor enough not to worry about?
(should add Samsung Gen6 8kw, on two bedroom victorian mid terrace)
That's too tight IMO, we would use 28mm copper, or 32mm MLCP
Technical Manager & Professional Installer: Ultimate Renewables
- 21 Forums
- 1,977 Topics
- 43.1 K Posts
- 44 Online
- 2,305 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
@sandman1600 how many loops on that one?
By davidnolan22 , 18 minutes ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@abernyte no, it doesn’t turn the pumps off on mine.
By davidnolan22 , 38 minutes ago
-
RE: Confused about Samsung Gen6 Hot Water Controller
Do you have the DHW on timed periods or on continuous w...
By DerekDeLeon , 10 hours ago
-
RE: What is the best strategy for operating a very oversized heat pump?
I think we are currently operating a weird mix of 2 and...
By guthrie , 12 hours ago
-
We’ve had our heat pump (EBAC) since October, with a fe...
By Simon and Zoe , 13 hours ago
-
RE: DHW temp Samsung AE120RXYDEG 12kw ASHP with Gen 6 controller
@Bami Ive had a look for the specs of your cylinder o...
By bontwoody , 14 hours ago
-
RE: best approach for primaries?
Personally I would want them inside the heated envelope...
By JamesPa , 17 hours ago
-
RE: help with new bathroom and towel radiator
I persuaded my installer that heat loss from the adjace...
By JamesPa , 17 hours ago
-
RE: Grant Aerona fine tuning advice needed
Thank you pretty sure it's solar gain causing the incre...
By Stopbar , 18 hours ago
-
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
I fitted a Samsung 8kw myself on a new build with under...
By DerekDeLeon , 21 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@adrian it does look like they’ve updated their outgoin...
By Arundalep , 2 days ago
-
RE: Heat Pump Sizing & Installation Costs
1970s 4-bed detached house approx 168 sq.m internal are...
By JohnR , 2 days ago
-
RE: Is it KISS or constant – weather compensation vs. set flow temperature?
Away at present. Hence the delay. Will get back asap. ...
By cliffhanger , 2 days ago
-
RE: Setback savings - fact or fiction?
The lower the DT the higher the flow rate. The lower ...
By BobTSkutter , 3 days ago
-
RE: New kitchen with no walls – will fan coil units work?
Thanks. That explains the strangely-shaped 'feet' (loo...
By IanMK13 , 3 days ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
I’ve updated Bodge Buster for 2025 to empower homeowner...
By Mars , 3 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Aira, the Swedish, end to end manufacturer, system desi...
By KevinPotts , 3 days ago
-
Unfortunately for your argument the best performing Dai...
By RobS , 3 days ago
-
RE: Grant ASHP not reaching target temperatures
@mikefl Thank you. I’m not sure how to do these checks ...
By Hillswick , 4 days ago
Latest Topics
-
Confused about Samsung Gen6 Hot Water Controller
By ntruby 10 hours ago
-
help with new bathroom and towel radiator
By AdamK 21 hours ago
-
Grant Aerona fine tuning advice needed
By Stopbar 1 day ago
-
Adjusting 6kW Daikin's Weather Compensation Curve
By Ubert767 5 days ago
-
Should I make my radiators smaller?
By Scalextrix 6 days ago