Evening all, I wonder if someone can share any thoughts on my situation?
I sent the below email to Octopus in January which was the first opportunity when I could see how my 9kw Daikin installed last June was performing at or below the design temperature. I'm now in a situation where the Octopus heat loss design estimates my heat loss at ~8.5kw and my own Heat Punk heat loss is 6.6kw with more accurate inputs and air changes (not all rooms in my house have trickle vents on windows, the kitchen doesn't have an extractor which extracts externally etc). The measured heat loss from EmonCMS is ~4-5kw to maintain 21*C at an average outdoor temperature of -4*C. I spoke to Octopus today and they are waiting on MCS to confirm whether 'measured heat loss' is a suitable substitute to the various heat loss calculation methodologies / standards that exist. Having read some of the MCS standards I believe they focus solely on designed heat loss, not measured heat loss (the latter of course being more accurate). Octopus stated today their survey doesn't allow modifying any air changes/hr for each room so they are limited to the standard assumptions (which of course can lead to inaccurate results).
I'd welcome any insights or advice from others - I'd like Octopus to swap the 9kw high capacity unit (which is a software limited 16kw unit) with the 8kw low capacity unit which can modulate down lower to prevent cycling.
Monitoring available here:
"Good evening,
My thoughts are - good luck, you seem to have a reasonable argument for the replacement. That said Im not sure you could prove the current one is unfit for purpose so they may well decline, but worth a go.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
There have been several people on the OpenEnergyMonitor forums who have persuaded Octopus to replace their 9kW or 11kW Daikin with a smaller 6kW or 8kW Daikin. Take a look at this.
@jamespa thanks, it's way off of the MCS performance estimate and I think if it ended up in Court I could construct a sound case to justify it's not fit for purpose (based on efficiency, wording on the contract etc)
@big_si As has been mentioned you are not the first with this problem. Several 🐙 clients have had Daikin 9s changed for Daikin 8s. The first was Matt Drummer who is over on OE Monitor.
The 9kw is a 16 kw restricted by software and is famously juicy although there are people running them very efficiently. The restriction means they don't have the modulation range which is a pain.
The 4/6/8 are the same - all are 8s restricted by software but for some reason it doesn't have the same impact. All 3 modulate down very nicely. I have the 6kw Daikin and I am very happy with it. I run it on pure weather compensation and the compressor never turns off and it runs low without complaining or cycling.
Key for you is building a case with evidence so do talk to the other guys over on the OEM forum. Best of luck. 🐙 are pretty good if you make a strong, logical case.
@lucia thanks for the reply, I think I've now got sufficient evidence that it needs replacing particularly OEM data when it was operating at design temperature which I did not have last year when Octopus refused to replace it at my first request. I've since raised with NAPIT and MCS as additional levers. I just want the system to perform as intended and the 9kw isn't meeting expectations in that regard and hopefully Octopus learn from this with future surveys to reduce rework and increase customer satisfaction.
9kw monster swapped with the 8kw unit today - it's whisper quiet and running a treat so far! Well worth persevering with NAPIT as Octopus were reluctant to swap out the 9kw. Had to tweak the EmonCMS flow temperature sensor to before backup heater (as the 8kw doesn't have a backup heater) and updated the details on heatpumpmonitor.org
Looking forward to seeing how it performs next winter 🙂
@big_si thanks for the update. It’s still forecast to be unseasonably chilly for a few more days so you may get some insights. But good to hear you’re happy with the new smaller unit. Keep us updated.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
-
Is Your 6kW Air Source Heat Pump Really a 6kW?
6 months ago
-
Warm weather and heat pumps.
6 months ago
-
Is your gut better than Math
7 months ago
-
Daikin COP / energy used measurement from MMI
2 years ago
-
Why does my second unit sometimes start up unexpectedly on a Daikin split system?
2 years ago
- 26 Forums
- 2,233 Topics
- 49.7 K Posts
- 145 Online
- 5,898 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Replacing knackered oil boiler with Samsung ASHP - Perthshire
@dgclimatecontrol thanks for the reply. subesequent rep...
By DowallyDrifter , 11 minutes ago
-
RE: Effect of Mitsu PAR WT60 Wireless Controller
Hi Rob. Thanks for your comments and I am relieved th...
By DavidAlgarve , 23 minutes ago
-
Nothing broad about what I’ve posted. My original post ...
By Majordennisbloodnok , 29 minutes ago
-
RE: Daikin Octopus installation update - I saw my first defrost. 😍😂
I don't seem to have a mixer valve. Just pressure regul...
By Jancold , 60 minutes ago
-
RE: New Fogstar 15.5kWh upright solution
😁Yes, the 90Amps capacity in total in an 8k inv...
By Batpred , 1 hour ago
-
RE: Master & Slave Zones/Setback
Have you yet adjusted the WC settings, it sounds like n...
By JamesPa , 2 hours ago
-
RE: Say hello and introduce yourself
This discussion has gone quite deep for our Hello &...
By Transparent , 16 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - it sounds as though you are close to havi...
By cathodeRay , 17 hours ago
-
Let's see if we can tempt @glyn-h to give his insights....
By Mars , 18 hours ago
-
RE: Question about Heating Pump Operation mode – Ecodan FTC6 v20.06
This isn't an exact reply to your question, as I don't ...
By rhh2348 , 19 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
Let's first note what those parameters are. They are ...
By Transparent , 21 hours ago
-
I’ve met the Flexi-Orb team, and they come across as ge...
By Mars , 21 hours ago
-
Webinar on "Heat Pumps for Home Owners" Thursday 20...
By Mars , 23 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@grantmethestrength also i need to check the other stra...
By AdamK , 24 hours ago
-
@jamespa @old_scientist @iaack Hi, thanks for the inp...
By bontwoody , 1 day ago
-
RE: Should Our Water Circulation Pump Be Configured to Run All The Time?
This is how Daikin run their heat pumps. Weather Comp...
By RadWhisperer , 1 day ago
-
Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
I ended up with a Solis S6-EH1P8K-L-PLUS (8 kW) hybrid ...
By Batpred , 2 days ago
-
RE: Options on flushing my system
@grantmethestrength with your pragmatic approach and &#...
By SUNandAIR , 2 days ago
-
RE: Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
@batpred For the moment I'm sticking with what I have, ...
By bubuontheweb , 2 days ago