Oversized Daikin 9kw
Evening all, I wonder if someone can share any thoughts on my situation?
I sent the below email to Octopus in January which was the first opportunity when I could see how my 9kw Daikin installed last June was performing at or below the design temperature. I'm now in a situation where the Octopus heat loss design estimates my heat loss at ~8.5kw and my own Heat Punk heat loss is 6.6kw with more accurate inputs and air changes (not all rooms in my house have trickle vents on windows, the kitchen doesn't have an extractor which extracts externally etc). The measured heat loss from EmonCMS is ~4-5kw to maintain 21*C at an average outdoor temperature of -4*C. I spoke to Octopus today and they are waiting on MCS to confirm whether 'measured heat loss' is a suitable substitute to the various heat loss calculation methodologies / standards that exist. Having read some of the MCS standards I believe they focus solely on designed heat loss, not measured heat loss (the latter of course being more accurate). Octopus stated today their survey doesn't allow modifying any air changes/hr for each room so they are limited to the standard assumptions (which of course can lead to inaccurate results).
I'd welcome any insights or advice from others - I'd like Octopus to swap the 9kw high capacity unit (which is a software limited 16kw unit) with the 8kw low capacity unit which can modulate down lower to prevent cycling.
Monitoring available here:
"Good evening,
My thoughts are - good luck, you seem to have a reasonable argument for the replacement. That said Im not sure you could prove the current one is unfit for purpose so they may well decline, but worth a go.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
There have been several people on the OpenEnergyMonitor forums who have persuaded Octopus to replace their 9kW or 11kW Daikin with a smaller 6kW or 8kW Daikin. Take a look at this.
@jamespa thanks, it's way off of the MCS performance estimate and I think if it ended up in Court I could construct a sound case to justify it's not fit for purpose (based on efficiency, wording on the contract etc)
@big_si As has been mentioned you are not the first with this problem. Several 🐙 clients have had Daikin 9s changed for Daikin 8s. The first was Matt Drummer who is over on OE Monitor.
The 9kw is a 16 kw restricted by software and is famously juicy although there are people running them very efficiently. The restriction means they don't have the modulation range which is a pain.
The 4/6/8 are the same - all are 8s restricted by software but for some reason it doesn't have the same impact. All 3 modulate down very nicely. I have the 6kw Daikin and I am very happy with it. I run it on pure weather compensation and the compressor never turns off and it runs low without complaining or cycling.
Key for you is building a case with evidence so do talk to the other guys over on the OEM forum. Best of luck. 🐙 are pretty good if you make a strong, logical case.
@lucia thanks for the reply, I think I've now got sufficient evidence that it needs replacing particularly OEM data when it was operating at design temperature which I did not have last year when Octopus refused to replace it at my first request. I've since raised with NAPIT and MCS as additional levers. I just want the system to perform as intended and the 9kw isn't meeting expectations in that regard and hopefully Octopus learn from this with future surveys to reduce rework and increase customer satisfaction.
9kw monster swapped with the 8kw unit today - it's whisper quiet and running a treat so far! Well worth persevering with NAPIT as Octopus were reluctant to swap out the 9kw. Had to tweak the EmonCMS flow temperature sensor to before backup heater (as the 8kw doesn't have a backup heater) and updated the details on heatpumpmonitor.org
Looking forward to seeing how it performs next winter 🙂
@big_si thanks for the update. It’s still forecast to be unseasonably chilly for a few more days so you may get some insights. But good to hear you’re happy with the new smaller unit. Keep us updated.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
-
Is Your 6kW Air Source Heat Pump Really a 6kW?
7 months ago
-
Warm weather and heat pumps.
7 months ago
-
Is your gut better than Math
8 months ago
-
Daikin COP / energy used measurement from MMI
2 years ago
-
Why does my second unit sometimes start up unexpectedly on a Daikin split system?
2 years ago
- 26 Forums
- 2,323 Topics
- 52.1 K Posts
- 256 Online
- 5,979 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
@majordennisbloodnok Thanks. Yes, no problem. Wher...
By Bash , 15 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Here's what mine typically looks like. Hence why I ...
By benson , 22 minutes ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@hcas Hello Henri, I know that we have had an exchange ...
By DavidAlgarve , 36 minutes ago
-
RE: MELcloud scheduling misbehaviour
@downfield my understanding is that you can have a maxi...
By Richard24738 , 3 hours ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
If it is combined with the BUS and they make it all goo...
By Batpred , 3 hours ago
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
Fair enough. There seem to be ways to achieve the same...
By JamesPa , 5 hours ago
-
RE: Electricity price predictions
Before I dive into the issue of a strategy which helps ...
By Transparent , 6 hours ago
-
RE: Advice on reading thermal images
@editor Thanks Mars, better price from the website and ...
By colinc , 8 hours ago
-
RE: Signenergy AI Mode - How long does it take to learn a usage pattern?
@editor apparently it helps optimise charging and disch...
By Grantmethestrength , 9 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
To be blunt, I wouldn't choose. If we were to move to...
By Majordennisbloodnok , 9 hours ago
-
RE: Diagnostic Data Needed for Repeatedly Failing Tesla Powerwall 3 System
Yes, some queries were raised on github recently: ...
By Batpred , 10 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@cold123456 Mitsubishi has failed to respond to my com...
By Ecoste , 10 hours ago
-
RE: Grant Aerona Short Cycling
@steam-powered I'm currently running 30@-7 23@15 so cur...
By damonc , 14 hours ago
-
RE: What a Bad Heat Pump Installation Looks Like
That's pretty impressively incompetent. In our develo...
By Steelbadger , 21 hours ago
-
RE: Marginal pricing and UK electricity costs
@judith I just realised he’s the guy with the ‘minimum ...
By Lucia , 22 hours ago
-
Midea ASHP Issues with Smart Home App losing connectivity with the Wall Unit
Hi, First Post - replaced out 16 year old gas boiler ...
By SteveT , 23 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: @lucia Manufacturer: Daikin Model: E...
By Lucia , 24 hours ago
-
RE: Heat Pump Training vs. Real-World Installation
@judith I looked at the control challenge of balancin...
By Lucia , 1 day ago
-
RE: Grant Aerona circulation/system pump staying on
@mikefl thank you, I've changed 4200 to 2 and now the m...
By damonc , 1 day ago