@jamespa Ah, really?  Maybe we’re not as well insulated as we thought.

I am definitely going to follow the more logical approach you outlined. Current setup is just me dropping the flow temp after being alarmed at the amount of electricity we’re using.

I tried changing the flow temp to 36 initially and found the thermostats reporting that the temperature was dropping in some rooms so I’ve upped it to 38.  


   
ReplyQuote
(@davidnolan22)
Trusted Member Member
240 kWhs
Joined: 2 months ago
Posts: 38
 

@sandman1600 if your house is 130m2 and you have a 14kw mitshi machine....... I would be staggered if it wasn't oversized. that's 107w/m2. that's a really really poorly insulated house with holes in the windows 


   
ReplyQuote
(@sandman1600)
Eminent Member Member
80 kWhs
Joined: 1 day ago
Posts: 17
Topic starter  

Posted by: @davidnolan22

@sandman1600 

Your problem will be the minimum output of the 14kw heat pump might be not far from your heat loss in cold weather,

I'm sorry to sound thick but what does this mean? 

As for the rest of your advice, thank you. Definitely makes sense that it may take time to warm up the fabric of the house. I’d kind of considered that the concrete floor would take time to heat but yeah, I’d not really considered the whole property absorbing that heat. Thanks. 

 


   
ReplyQuote
(@sandman1600)
Eminent Member Member
80 kWhs
Joined: 1 day ago
Posts: 17
Topic starter  

@davidnolan22 Oh wow. Starting to sweat that we have been sold an inappropriate heat pump.


   
ReplyQuote
(@jamespa)
Famed Member Moderator
10956 kWhs
Veteran
Joined: 2 years ago
Posts: 2077
 

Posted by: @sandman1600

@davidnolan22 Oh wow. Starting to sweat that we have been sold an inappropriate heat pump.

Based on the numbers I think its likely its oversized.  Not a disaster but it means it will probably cycle on and off a lot.  If does prove to be oversized (difficult to tell until you have it working without influence from external controls and also some monitoring) and you have a big enough slab you may find you can cost effectively batch heat the slab during cheap rate periods (much like storage heaters).  It may take some experimentation but for sure you are going to save money relative to operating at 55C flow temperature!

 

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
Page 4 / 4
Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security