Hi all, Jordan here, hope you're all well.
I've read some great topics and advice so far here so thought I would share my dilemma!
I currently have an oil boiler which has served us well but is nearing its life expectancy. So its either a new oil boiler for £6k approx or a new funded air source heat pump? Only problem is I hear dreadful things about the running costs!
I have just been granted funding based on an assessment from from Energy Savings Trust and also had heat loss calculations from the MSC installers. Based on this information they have suggested a Valiant AroTherm Plus 7kw with all new radiators.
- Its a 3 bed house, 89m2 2 bedroom at top of stairs, all other rooms and bathroom down stairs.
- I currently have a 1951 timber frame house and I have installed 70-80mm PIR to all walls that have an external surface albeit with some 25mm on a couple of walls for specific reasons.
- 70-80mm PIR underfloor insulation.
- Have 200mm in loft which I will be adding too.
- Double glazing circa 2010
- Current heating situation, will lose approx 0.5oC every 1 hours
I have done a fair biut of research already I know there are possible ways to setup all configurations to get the most out of ones system (thanks to Heat Geeks) My question is, is this actually possible? I am currently on oil and fear there will be steep increase in my electricity bills. If you could indulge me, could any of you offer any advise generally and as to whether the Valliant will provide a decent COP/SCOP and provide a decent return given all the above factors and should I be worried about it not providing enough heat or a moderate spend or enough but at an extortionate increase in electricity usage/cost?
I would love to hear more from you all and get your take on it.
Thanks in advance.
Hi Jordan, welcome to the forum.
You sound like you have done a lot of research already and that your house is well suited to low temperature heating.
You may already know that in terms of SCOP, if you can get to about 3.6 then you have reached parity with mains gas heating. Oil is a bit more difficult to judge because its price is so volatile, but in my opinion a well performing heat pump will beat it on a like for like basis.
The crucial point here is well performing. You should be able to get an SCOP of well above 4 with a good installation (see heat geek COP guarantee) which will rival or beat oil. Notice that I also said like for like. That doesnt have to be true. The price of oil is set at current market rates and you cant drill for you own in your back yard. There are many heat pump/time of use tariffs that you can use to your advantage to get the average unit price of electricity lower. If you can run to it, solar panels will lower your bills too and a home battery even more so. If you intend to get an Electric vehicle in the future, then the average price you pay per unit will plummet. I think im paying about 12-15p per kWh on average.
Its also worth thinking ahead, the new government looks keen on bringing more renewables on line and its possible the stupid pricing system we have at the moment may be looked at (fingers crossed), so electricity prices could fall.
If a new oil boiler will cost you £6000 and you can get the £7500 grant then that should get you a good install with perhaps some left over.
I would get the heat loss estimate checked just to be sure as MCS can over estimate quite a bit. There are various ways you can sanity check their estimate if you dont mind a little maths. You also want to be looking for a quote with the lowest flow temperature you can get as that will increase your COP.
If you do decide to go down the heat pump route then you will find lots of help on here as to what to look for to get a good install. Vaillant make good heat pumps but they are plenty of other good makes around too.
Its worth pointing out too that your electricity bills would vary wildly over the year so you have to be prepared to take an average.
good luck!
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @jmlValliant will provide a decent COP/SCOP
Don't get to hung up on makes, they nearly all can provide around the same same cop in like for like conditions. It's the system they are connected to that makes the real difference in performance and how they are operated.
If changing all radiators aim for as low a flow temperature as possible, to get most benefit.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
This site is one of the most comprehensive for what size heat pump you might need, as you may have read too big a pump can’t be less efficient
https://energy-stats.uk/what-size-heat-pump/
There are several regular posters on the forum who have successfully moved from oil and might reassure you. Or search the site for ‘oil boiler’ if you get impatient.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
Posted by: @judithThis site is one of the most comprehensive for what size heat pump you might need, as you may have read too big a pump can’t be less efficient
https://energy-stats.uk/what-size-heat-pump/
There are several regular posters on the forum who have successfully moved from oil and might reassure you. Or search the site for ‘oil boiler’ if you get impatient.
A few misleading facts in the attached.
Cylinder reheat time is from 10 degs, you will do that once, then after you are raising the cylinder 5 to 10 degs only depending on your heating strategy. My 6kW unit does a reheat twice per day currently at 30 to 40 mins at a time up to 50 degs.
No allowance seems to be made at the lowest design temperature to actually have enough over capacity in the heat pump to reheat the cylinder and to heat the house. Which is an omission.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Hi guys!
Thanks for getting back to me so quickly.
@johnmo Aye, thank you. I am not too concerned about the brands but rather thought it an idea just to inform of the system i may be getting. I understand all brands these days offer close to what the others do. Also, thank you for info regarding hot water cylinder heating. I was worried i would have the extra cost of boosting with the immersion element but good to know it can be done via the heat pump heat process too. (I hope i am reading that right hence you 'does a reheat'.
@judith - Thanks for that. I have had a good look on Valliant and at their spec sheets.
@bontwoody I would get the heat loss estimate checked just to be sure as MCS can over estimate quite a bit. There are various ways you can sanity check their estimate if you dont mind a little maths. You also want to be looking for a quote with the lowest flow temperature you can get as that will increase your COP.
@bontwoody Thanks bontwoody! I did try doing the Math, and have tried to set myself up for worse case scenario regarding costings based on Heat Geeks W/m2 hierarchy.
Basically I started with worse off state to my current situation ie. Victorian property with no insulation, 50-75mm loft insulation, single glazed windows compared to my current house which is obviously far better insulation wise than that.
So, Victorian proeprty on heqt Geeks States 65-85 W/m2 I chose 75 W/m2
75W/m2 x my house area 93m2 = 6975W = 7Kw (as it happens I have been quoted a 7Kw heat pump)
As per H Geeks 7Kw x 1500 for heating = 10500Kwh
+
7Kw x 500 for Hot water = 3000Kwh
= Total 14000Kwh Demand
(Now my installer gave me HP combined performance of 2.91 SCOP at 45oC flow rate and a total demand of 14600kwh)
I have pushed those boundaries further a little further and given myself a SCOP of 2.5 (not a great deal difference but I guess a worse case is better than an unrealistic expectation, and I can play further with these figures to project different potential spendings)
So 14000Kwh Demand / 2.5 SCOP = 5600Kwh x Elec Unit 0.22p = £1232 Costings to power heat pump through the year.
(This of course could/well be reduced in the summer months with minimal/low usage, improving the SCOP and efficiency, not to mention the other hacks and tweaking of controls with weather compensation etc and given the fact I have already set my conditions to an old Vict property not my current one that is moderately well insulated.)
Does this make sense and look right to you based on the math you are referring too??
Of course I have to factor in appliances but that is minimal given my usage of low wattage devices.
I also agree with you, this place seems amazing for all one needs to know, you are all so knowledgeable which makes things clear and understandable.
If you or anyone has more info regarding the hot water cylinder that would be great? I fear I would need to fire the immersion element which would use more electricity (right?) and so if there are ways to override that so the heat pump heats house and water that would be great to know. 👍
Again, I thank you in advance.
It seems you both have a nice system setup!
if only i had a decent solar array then this whole ASHP would be a no brainer!! 👍
Posted by: @jmlmore info regarding the hot water cylinder that would be great?
Basically you store water between 45 and 50. I store at 50 and heat twice a day (210L) the cylinder volume is bigger than an oil system hot water cylinder as the energy storage volume is related to the stored temperature and volume. At 50 degs there is zero risk of legionella, as at 50 degs 90% plus of legionella dies in 2 hrs.
The other issue is heat transfer when heating the cylinder. You want the lowest flow temperature from the heat pump and this achieved with a large heating coil in the cylinder. The bigger the better, ideally 3m² plus.
The CoP of 2.9 is closer to what you would get at -3 and 45 flow temp. Most the time it's nearer 7 degs and your flow temp came down to 35 the CoP would be closer to 4.5, if you have an open system.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Posted by: @jmlI have pushed those boundaries further a little further and given myself a SCOP of 2.5 (not a great deal difference but I guess a worse case is better than an unrealistic expectation, and I can play further with these figures to project different potential spendings)
So 14000Kwh Demand / 2.5 SCOP = 5600Kwh x Elec Unit 0.22p = £1232 Costings to power heat pump through the year.
(This of course could/well be reduced in the summer months with minimal/low usage, improving the SCOP and efficiency, not to mention the other hacks and tweaking of controls with weather compensation etc and given the fact I have already set my conditions to an old Vict property not my current one that is moderately well insulated.)
Does this make sense and look right to you based on the math you are referring too??
Of course I have to factor in appliances but that is minimal given my usage of low wattage devices.
I also agree with you, this place seems amazing for all one needs to know, you are all so knowledgeable which makes things clear and understandable.
If you or anyone has more info regarding the hot water cylinder that would be great? I fear I would need to fire the immersion element which would use more electricity (right?) and so if there are ways to override that so the heat pump heats house and water that would be great to know. 👍
Hi Jordan
So given all the insulation upgrades you have done, I think you might be being too pessimistic. Perhaps 50 W/m2 might be a better guide. Also the heat geek sheet is there to give you an idea, you should look at the methods described by Michael Podesta in the link and use any historical oil usage figures you might have to give you a more accurate guide.
The combined SCOP figure you have been given doesnt look very impressive and I would be getting other installers to have a look.Have a look on https://heatpumpmonitor.org/ to see other systems performance.
As mentioned, system design is key to getting a good SCOP and you dont want to be saddled with a system that is expensive to run. As well as low flow temperatures, you will be looking to avoid the use of buffer vessels (which some installers insist on putting in and which lower COP). It is also beneficial if the installer will use anti frost valves rather than antifreeze fluid. The latter reduces the capability of water to transfer heat.
Modern high temperature heat pumps negate the need for an immersion top up for legionella protection. Although there will still be an immersion in your tank for emergencies 🙂 The heat pump will either be set to heat the house or the water tank and not both at the same time as different flow temperatures are required. When you heat your DHW is largely a matter of personal choice. At night will have less impact on heating (and perhaps cheaper electricity), by day will have better COP as the outside temperature is usually higher.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Morning guys! Thanks so much for this. Very interesting.
Here are the complete stats given to me. (see attached)
Regarding the pessimism of my calculation I thought that better to give me a worst case scenario.
I guess the problem I have is given my busy schedule I have actually been granted the funding and have a small window to accept the offer from energy savings trust based on the current quote I have been given from install. As the offers are in granted in conjunction with the quote I fear I would have to start the whole process again.
Based on quote they are fitting a 28mm anti freeze value and also a 25L CB Heating Expansion Vessel Is this the same as a additional heating chamber that should be avoided? I'm guessing this is similar to the normal expansion vessels we get on out oil boilers?
The CoP of 2.9 is closer to what you would get at -3 and 45 flow temp. Most the time it's nearer 7 degs and your flow temp came down to 35 the CoP would be closer to 4.5, if you have an open system
So based on my attached docs are these the sort of figures I would be looking at @johnmo, so only really low performance and scop in the expected colder months?
Not sure I entirely understand all the figures, so a little more help there would be great. When it says renewable 9000+ kWh I'm guessing that is what I a drawing receiving back in energy from the usage the HP is using?
Look forward to reading your take on the above 👍🏼
Thanks guys
@jml Hi Jordan
I cant see an attachment? The expansion vessel is as you suppose normal and not a buffer vessel. Good that they propose anti frost valves and not antifreeze solution 🙂
Do you have any previous oil usage data?
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 21 Forums
- 1,960 Topics
- 42.5 K Posts
- 48 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
Curtains and the loss through the window is what I was ...
By JohnR , 3 minutes ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 29 minutes ago
-
RE: SolarPV tables / online calculator
By Gary , 1 hour ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Yes, that sounds correct. I would say try both options...
By Old_Scientist , 10 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 11 hours ago
-
RE: Setback savings - fact or fiction?
The great thing about science is that it doesn't care o...
By JamesPa , 12 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 14 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 16 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 18 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 19 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 20 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 23 hours ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
-
RE: Baxi Air Source Heat Pump tips and tricks please
@cathyem1 - thanks for the update. Let us know how it g...
By cathodeRay , 2 days ago
-
RE: Low COP and unevenly heated rooms with 12kW Samsung AE120MXTPEH / AE260TNWTEH
@editor But do you wear your peaked cap the right way r...
By Toodles , 2 days ago
Latest Topics
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 29 minutes ago
-
SolarPV tables / online calculator
By MichelleC 7 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 19 hours ago
-
Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
By BAMi 22 hours ago
-
By Toodles 2 days ago
-
Solid manhole cover within r290 exclusion zone
By dbrb2 2 days ago
-
Towel rails. An unexpected final hurdle
By Davesoa 2 days ago