New to world of ASHPs: Ideal Logic Air Monobloc heat pump 8kW questions
Our new tariff with eon cheaper rates at night. Found out our hallway radiator is a buffer radiator
OK.
To minimise costs and maximise efficiency you are going to need to get your 'weather compensation' curve as low as possible so you are running with the flow temperature (the temperature of thee water produced by the heat pump) as low as it can be consistent with heating your house. If you haven't already, I suggest you read this introduction to heat pumps which explains some of the features of heat pumps including this one.
In essence the process to optimise is this:
1. Set your heat pump to operate 24*7
2. Because you have a Halo (at least I think you do) disable the 'room influence' setting. If you dont have a halo then turn any thermostat up to maximum
3. Turn all TRVs to maximum or remove the heads
This will result in a house that is too hot - so now:
4. Slowly adjust the weather compensation down until the house is just below the required temperature, then turn it up one notch. By slowly I mean no more than one step at a time no more than twice a day, reducing to once per day as you get close.
5. If rooms are settling at different temperatures (or more precisely if the temperature differential between rooms is not what you want - eg you may want bedrooms cooler than living rooms), you will need to 'balance' the radiators using the lockshield valves (the valves opposite the TRVs). We can provide separate instructions for this
The process takes a couple of weeks (which is why installers rarely complete it).
Once this is done, you have the system operating at its most efficient point and should provide a high degree of stability throughout the season. If there are a couple of rooms that, for example, suffer from excess solar gain, you can reinstate TRVs in those rooms but by and large the majority of TRVs should be at maximum or the heads removed.
Ultimately its you choice if you wish to do this. It may, depending on how you are currently set up, save in the region of 10-20% running costs and result in a higher level of comfort. However it does require patience and a level of trust in the theory. It also requires that you 'see it through', stopping halfway may make things worse.
If you do wish to do it please say so and I or another can talk ou through in a bit more detail.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I would worry about the heat loss from the cylinder and pipework in the loft. My cylinder and associated pipework have turned what was the coldest room in my house into the warmest room but at least that heat loss is in the house.
Posted by: @johnrI would worry about the heat loss from the cylinder and pipework in the loft. My cylinder and associated pipework have turned what was the coldest room in my house into the warmest room but at least that heat loss is in the house.
In fairness sometimes it's the only viable location. So long as gge pipes and tank are well insulated it may be the best that an be done.
My cylinder is in a small airing cupboard which, unlike with the previous cylinder, now barely gets warm. We actually instructed the plumber to omit the pipe insulation in this cupboard so we would get some heat for airing! If yours has as much effect as you say something is wrong.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa similar for us.
Our ashp cylinder is in the airing cupboard where very few pipes were insulated.
So after I insulated them the other half complained the airing cupboard was cold so I removed all insulation.
Now, at least the heat loss is still going into the house so what does it matter?
Posted by: @westkentNow, at least the heat loss is still going into the house so what does it matter?
Only to the extent that the heat has been produced at a lower COP than your space heating. But as you are probably talking 1-2kWh max per day, who cares?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,153 Topics
- 47.3 K Posts
- 21 Online
- 5,673 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Failing heat pump system - seeking thoughts on a rebuild
@jamespa I think that's a good interim solution James. ...
By bontwoody , 1 hour ago
-
RE: Electricity price predictions
Community energy installations are a great idea, but th...
By Scalextrix , 5 hours ago
-
RE: Can you help with our research: solar panels, EV chargers, home batteries, heat pumps?
I have signed up as well. @belsnugg could you outline ...
By JamesPa , 13 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Ooh, heat pumps in neon blue wrap 🤣 🤣 &...
By Old_Scientist , 13 hours ago
-
@profzarkov Good to know in case it ever happens to me...
By bontwoody , 1 day ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
I mean, is this surprising? The local installers in my ...
By Alex , 1 day ago
-
@old_scientist sorry, I should have made it clear that ...
By GrahamF , 1 day ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@thundermink can you provide photos to illustrate your ...
By Morgan , 1 day ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 2 days ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
After our rather lengthy meander off piste, I thought I...
By GrahamF , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - to collect the IAT/OAT data, can I sugges...
By cathodeRay , 2 days ago
-
RE: Ecodan software update. Real or scam?
@vinz86 Contact Mitsubishi and an engineer attends and ...
By ASHP-BOBBA , 2 days ago
-
@drei When I was in local government we were of cours...
By JamesPa , 2 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Sufficient system volume is also essential for ensuring...
By Old_Scientist , 3 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 3 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 3 days ago
-
RE: Octopus tariffs - a quick comparison
@tim441 I’d agree wholeheartedly with that, with 2 x Po...
By Toodles , 3 days ago