New ASHP system - choices
Posted by: @harriupAll heat pumps will hit the point where their minimum output exceeds the heat being taken out by the heating circuit, not oversizing too much means that happens at a higher outside temperature. How the pumps handle the lower demand is really hard to pin down. I know my system when using the weather compensation curve worked just at its minimum power but cycled up to 6 times per hour. Switching to the room adaptive mode slowed the cycle to once per hour or so but with a more complex power consumption as it it often puts a burst of energy in before a pause. But overall this a more efficient mode - better COP. Looking at some similar systems on heatpumpmonitor, though, displays such dissimilar working patterns that it is hard to differentiate what elements are created by the way the house heating system is responding or is programmed.
In an ideal world a heat pump unit would contain two compressors, a nominal 12kW capacity heat pump having one compressor rated at 8kW and one compressor rated at 4kW. The 8kW compressor providing heating during most of the Winter period, with the 8kW plus 4kW meeting demand during particularly cold spells.
As milder weather conditions are encountered the system would changeover from the 8kW compressor to the 4kW one, thereby allowing a much lower thermal energy output without the possibility of cycling, and probably providing an increase in overall efficiency.
Unfortunately we don't yet live in an ideal world.
I believe that most, if not all, heat pumps control the stopping and starting of the compressor based upon the temperature of the LWT and RWT, such that when either of these temperatures reaches a defined limit, the compressor is started or stopped. This of course is more likely to happen during milder weather conditions.
The 'on' period and the 'off' period is therefore dependent upon the limits set within the controller and the actual temperature measurements produced by the LWT and RWT temperature sensors. One of the major determining factors affecting the frequency of cycling could be the location of the LWT and RWT sensors within the system. If the sensors are located within the outdoor unit they are likely to cool at a more rapid rate than if they were located within the home's thermal envelope, and therefore increase the cycling frequency.
- 26 Forums
- 2,123 Topics
- 46.7 K Posts
- 27 Online
- 4,531 Members
Join Us!
Podcast Picks
Latest Posts
-
Fast DHW setting on Midea (Clivet) heat pump
Hello everyone, We have a Clivet ASHP and smarthome a...
By benson , 11 hours ago
-
RE: Who has a V2G EV installation
I agree, but a word of caution. V2X is also sometimes u...
By Majordennisbloodnok , 12 hours ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 13 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
No idea, but bear in mind if you have a BUS grant I thi...
By Scalextrix , 20 hours ago
-
RE: Is your heat pump insured?
My home insurance renewal is due soon meaning I am doin...
By cathodeRay , 2 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 3 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Ive called most of them over the years. By far the best...
By dgclimatecontrol , 3 days ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 3 days ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
I've certainly seen that on their Ts & Cs page but ...
By Majordennisbloodnok , 3 days ago
-
RE: ASHP heat output monitoring
@carlo - not much better, is it. It looks more like a u...
By cathodeRay , 4 days ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 4 days ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 5 days ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@dgclimatecontrol I don't know, but they were not happy...
By DavidAlgarve , 5 days ago
-
RE: Why do we need pressurised systems?
A good question @toodles. My old open thermal store and...
By AllyFish , 5 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
Cross references for @martingale Background discussi...
By Transparent , 5 days ago
-
@ecobaker May I ask a question of you please. I too hav...
By Papahuhu , 5 days ago
-
It's unclear to me how the Smart Control project work b...
By Transparent , 6 days ago
-
RE: Have Consumers Been Lied to About the Efficiency of Heat Pumps Made in China?
@pavel, this isn't about discrediting Chinese products....
By Mars , 6 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
We had an excellent four months (11/3 to 15/7) generati...
By JulianC , 1 week ago
-
RE: Is this just haze or something more?
I think the present somewhat cooler hazy days show the ...
By Judith , 1 week ago