Posted by: @harriupAll heat pumps will hit the point where their minimum output exceeds the heat being taken out by the heating circuit, not oversizing too much means that happens at a higher outside temperature. How the pumps handle the lower demand is really hard to pin down. I know my system when using the weather compensation curve worked just at its minimum power but cycled up to 6 times per hour. Switching to the room adaptive mode slowed the cycle to once per hour or so but with a more complex power consumption as it it often puts a burst of energy in before a pause. But overall this a more efficient mode - better COP. Looking at some similar systems on heatpumpmonitor, though, displays such dissimilar working patterns that it is hard to differentiate what elements are created by the way the house heating system is responding or is programmed.
In an ideal world a heat pump unit would contain two compressors, a nominal 12kW capacity heat pump having one compressor rated at 8kW and one compressor rated at 4kW. The 8kW compressor providing heating during most of the Winter period, with the 8kW plus 4kW meeting demand during particularly cold spells.
As milder weather conditions are encountered the system would changeover from the 8kW compressor to the 4kW one, thereby allowing a much lower thermal energy output without the possibility of cycling, and probably providing an increase in overall efficiency.
Unfortunately we don't yet live in an ideal world.
I believe that most, if not all, heat pumps control the stopping and starting of the compressor based upon the temperature of the LWT and RWT, such that when either of these temperatures reaches a defined limit, the compressor is started or stopped. This of course is more likely to happen during milder weather conditions.
The 'on' period and the 'off' period is therefore dependent upon the limits set within the controller and the actual temperature measurements produced by the LWT and RWT temperature sensors. One of the major determining factors affecting the frequency of cycling could be the location of the LWT and RWT sensors within the system. If the sensors are located within the outdoor unit they are likely to cool at a more rapid rate than if they were located within the home's thermal envelope, and therefore increase the cycling frequency.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 255 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Setback savings - fact or fiction?
@cathoderay The input power is largely determined by...
By RobS , 14 minutes ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
@editor, this is now an example of greenwashing in the ...
By Majordennisbloodnok , 25 minutes ago
-
RE: Electricity price predictions
@transparent Im impressed by all your work on this. ...
By JamesPa , 2 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 2 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 2 hours ago
-
RE: What determines the SOC of a battery?
I agree. Fogstar confirmed that the Seplos BMS does ...
By Batpred , 3 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 4 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson — as @tasos suggests, plotting multiple variabl...
By cathodeRay , 6 hours ago
-
@painter26 — as @jamespa says, it's for filling and re-...
By cathodeRay , 8 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 18 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 20 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 23 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 24 hours ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 24 hours ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@majordennisbloodnok Daikin, take note! (In fact, I hav...
By Toodles , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
@mk4 — good work! First, I agree, no evidence of cycl...
By cathodeRay , 2 days ago