"Can you define "Short Cycling"?
Is this short Cycling , acceptable , during April , during the prime Short cycling month of April?"
Unfortunately there is no definitive answer to this but, as @derek-m says 6 times per hour, a 10 min period, is the frequently quoted rule of thumb, which probably dates from times prior to inverter driven compressors which have a slow start up reducing wear, thus I have absolutely no faith in it! It's the same problem in modelling terms as on/off operation, so at present I don't know of any actual quantitative results. John Cantor does discuss it on his YouTube videos and does a bit of quantitative work on a couple of examples.
In qualitative terms, if it's cycling when it's 7 ish or less outside, either you have a problem or your system is oversized or you should probably open up some more trvs and maybe run at a lower flow temp.
If it's cycling at 15+, then that's no surprise at all.
If it's cycling at zub zero temps you have a serious issue.
And some long cycling, due as much to load variations as the OAT changes, are perfectly fine.
As a warning, it's very easy to overthink heat pumps and become a bit obsessed with them. I should know! If you get the basics right as I and others have suggested, you will be in a much better position. So if I were you I'd concentrate on this before anything else, for the benefit of your own sanity.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Many Thanks Derek.
My Water Law settings are :
The Water Law Graph is defined by several bits in the Samsung Controller memory.
The Offsets, above and below the central Water Law graph, are set by the Samsung Front panel Thermostat.
Because the outside Temperatures are currently 23 C the Heat Pump is inactive.
As James says, I am becoming obsessed with Heat Pumps ...............
Time for a break from Heat Pumps!
Many thanks !
ian
Posted by: @fazel6 times per hour? How about "6" times per day?
https://emoncms.org/samsung5kw
-- Attachment is not available -- -- Attachment is not available --
With an OAT of 5C which is what the graphs say you have, you would indeed expect that or better. Remember that cycling occurs when the heat pump cant modulate down to match the load. At 5C it can, unless its been really badly over-sized.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @fazel6 times per hour? How about "6" times per day?
https://emoncms.org/samsung5kw
-- Attachment is not available -- -- Attachment is not available --
With an OAT of 5C which is what the graphs say you have, you would indeed expect that or better. Remember that cycling occurs when the heat pump cant modulate down to match the load. At 5C it can, unless its been really badly over-sized.
At higher outdoor temps it just runs less often.
So I assume that your heat pump is being operated in the same manner, which goes to prove that optimisation of your particular system is key to achieving best overall thermal efficiency.
Posted by: @derek-mSo I assume that your heat pump is being operated in the same manner, which goes to prove that optimisation of your particular system is key to achieving best overall thermal efficiency.
That's universally agreed, that optimisation of a system is key to achieving best overall efficiency.
Optimisation should start before the quote is accepted, not after the start up of the system.
I fully agree, if the system design is correct then optimising the operation of the system is much easier. The problem is that I suspect that most customers, either don't have the technical knowledge and information to be involved in the design, or since they are paying for a 'system designer' to do this work then why should they have to get involved.
It would appear that many installers also don't have the ability or inclination to fully optimise a system once it has been installed.
Doesn't bode well for the future.
fazel, I am green with envy.
If only I could get Six cycles per day !
I have a system that was NOT designed , but , chosen because my "installer" discovered a cheap Heat Pump in the local outlet of a large Plumbing supplies Organisation.
Unfortunately, the Heat Pump came with an Heat Exchanger which my "installer" proceeded to ignore .
Do you have an heat exchanger ?
Do you have a Buffer ?
ian
Yes Derek, I agree with you .......... I should have Designed my Heat Pump myself.
External pipe Temperature Sensors?
The Only affordable sensors appear to be K type sensors which attach to the outside of the copper pipes.
This external temperature sensing can be inaccurate if not very inaccurate with the Temperature measurement being the Temperature of the copper , not the water!
Internal pipe Temperature Sensors?
These Sensors appear to be very accurate, judging by my experience with my German "Sharky".
Excellent but completely unaffordable.
How do you measure internal water Temperatures?
ian
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 20 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Is that heat loss, or maximum output of the ASHP? Unde...
By Scalextrix , 10 hours ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan Fully agree with you. It shouldn't be the homeo...
By HCas , 12 hours ago
-
RE: Solar Thermal DHW and ASHP
@judith That makes sense to me! If I was in @alex_n '...
By HCas , 13 hours ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
Good unit. And the 10 kW is the same as the 12 kW I ...
By HCas , 13 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@judith thanks for your suggestions. Starting from col...
By GrahamF , 15 hours ago
-
RE: Inventor (Midea) Heat Pump short cycling advice
I switched to "fan coil mode" to be able to set water t...
By immunity , 18 hours ago
-
RE: DESNZ doing a survey which asks the right questions!
Without a survey their only source of data is probably ...
By JamesPa , 22 hours ago
-
RE: Can you help with our research: solar panels, EV chargers, home batteries, heat pumps?
Just done your survey!
By Judith , 1 day ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
@cleardene-ashp just thinking about your issues here. Y...
By Judith , 1 day ago
-
RE: Midea ASHP – how to set weather compensation
@cathoderay OK let's wait and see, it sounds an interes...
By Tasos , 2 days ago
-
RE: What is the Heat Geek Guarantee?
@judith, I’m with you on Heat Geek, but there really do...
By Mars , 2 days ago
-
RE: Electricity price predictions
Community energy installations are a great idea, but th...
By Scalextrix , 3 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Ooh, heat pumps in neon blue wrap 🤣 🤣 &...
By Old_Scientist , 3 days ago
-
@profzarkov Good to know in case it ever happens to me...
By bontwoody , 4 days ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
I mean, is this surprising? The local installers in my ...
By Alex , 4 days ago
-
@old_scientist sorry, I should have made it clear that ...
By GrahamF , 4 days ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 4 days ago
Members Online
No online members at the moment