"Can you define "Short Cycling"?
Is this short Cycling , acceptable , during April , during the prime Short cycling month of April?"
Unfortunately there is no definitive answer to this but, as @derek-m says 6 times per hour, a 10 min period, is the frequently quoted rule of thumb, which probably dates from times prior to inverter driven compressors which have a slow start up reducing wear, thus I have absolutely no faith in it! It's the same problem in modelling terms as on/off operation, so at present I don't know of any actual quantitative results. John Cantor does discuss it on his YouTube videos and does a bit of quantitative work on a couple of examples.
In qualitative terms, if it's cycling when it's 7 ish or less outside, either you have a problem or your system is oversized or you should probably open up some more trvs and maybe run at a lower flow temp.
If it's cycling at 15+, then that's no surprise at all.
If it's cycling at zub zero temps you have a serious issue.
And some long cycling, due as much to load variations as the OAT changes, are perfectly fine.
As a warning, it's very easy to overthink heat pumps and become a bit obsessed with them. I should know! If you get the basics right as I and others have suggested, you will be in a much better position. So if I were you I'd concentrate on this before anything else, for the benefit of your own sanity.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Many Thanks Derek.
My Water Law settings are :
The Water Law Graph is defined by several bits in the Samsung Controller memory.
The Offsets, above and below the central Water Law graph, are set by the Samsung Front panel Thermostat.
Because the outside Temperatures are currently 23 C the Heat Pump is inactive.
As James says, I am becoming obsessed with Heat Pumps ...............
Time for a break from Heat Pumps!
Many thanks !
ian
Posted by: @fazel6 times per hour? How about "6" times per day?
https://emoncms.org/samsung5kw
-- Attachment is not available -- -- Attachment is not available --
With an OAT of 5C which is what the graphs say you have, you would indeed expect that or better. Remember that cycling occurs when the heat pump cant modulate down to match the load. At 5C it can, unless its been really badly over-sized.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @fazel6 times per hour? How about "6" times per day?
https://emoncms.org/samsung5kw
-- Attachment is not available -- -- Attachment is not available --
With an OAT of 5C which is what the graphs say you have, you would indeed expect that or better. Remember that cycling occurs when the heat pump cant modulate down to match the load. At 5C it can, unless its been really badly over-sized.
At higher outdoor temps it just runs less often.
So I assume that your heat pump is being operated in the same manner, which goes to prove that optimisation of your particular system is key to achieving best overall thermal efficiency.
Posted by: @derek-mSo I assume that your heat pump is being operated in the same manner, which goes to prove that optimisation of your particular system is key to achieving best overall thermal efficiency.
That's universally agreed, that optimisation of a system is key to achieving best overall efficiency.
Optimisation should start before the quote is accepted, not after the start up of the system.
I fully agree, if the system design is correct then optimising the operation of the system is much easier. The problem is that I suspect that most customers, either don't have the technical knowledge and information to be involved in the design, or since they are paying for a 'system designer' to do this work then why should they have to get involved.
It would appear that many installers also don't have the ability or inclination to fully optimise a system once it has been installed.
Doesn't bode well for the future.
fazel, I am green with envy.
If only I could get Six cycles per day !
I have a system that was NOT designed , but , chosen because my "installer" discovered a cheap Heat Pump in the local outlet of a large Plumbing supplies Organisation.
Unfortunately, the Heat Pump came with an Heat Exchanger which my "installer" proceeded to ignore .
Do you have an heat exchanger ?
Do you have a Buffer ?
ian
Yes Derek, I agree with you .......... I should have Designed my Heat Pump myself.
External pipe Temperature Sensors?
The Only affordable sensors appear to be K type sensors which attach to the outside of the copper pipes.
This external temperature sensing can be inaccurate if not very inaccurate with the Temperature measurement being the Temperature of the copper , not the water!
Internal pipe Temperature Sensors?
These Sensors appear to be very accurate, judging by my experience with my German "Sharky".
Excellent but completely unaffordable.
How do you measure internal water Temperatures?
ian
- 26 Forums
- 2,283 Topics
- 51.1 K Posts
- 238 Online
- 5,944 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Heat Pumps Without Grants: Would You Have Installed One & Will You Now?
I was discussing the same with the family and a friend ...
By ChandyKris , 25 minutes ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
... which is usually how to run almost any heat pump BT...
By JamesPa , 2 hours ago
-
RE: Renewables & Heat Pumps in the News
If the installer is a regular plumber or someone who is...
By JamesPa , 4 hours ago
-
RE: Electricity price predictions
Erm... obtaining planning consent is rarely a problem f...
By Transparent , 4 hours ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
Ian Rippin, CEO of MCS, gave oral evidence to the Selec...
By Transparent , 4 hours ago
-
RE: UFH downstairs and radiators upstairs balancing question
I wonder what the logic of this was, that will be the c...
By JamesPa , 7 hours ago
-
RE: New Fogstar 15.5kWh upright solution
@batpred Well you must be one of the very f...
By Bash , 19 hours ago
-
@judith I haven't noticed any noise myself yet, nor my ...
By Eliuccio , 22 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Latest situation:Installer attended, couldn't get it wo...
By Crimson , 1 day ago
-
RE: Ecodan ASHP Low COP and Unstable Compressor Frequency
Thanks for the reply and the welcome ! Locat...
By lukewarmbath , 1 day ago
-
RE: Bosch CS5800i 5kW - Experience So Far
@ectoplasmosis Buderus is a subsidiary of the Bosch Gro...
By Steelbadger , 1 day ago
-
RE: Confusion over Octopus Tariffs
@agentgeorge I can’t recall when and the details but Co...
By Toodles , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@technogeek Yep, the same here. Toodles.
By Toodles , 1 day ago
-
RE: Maximising Home Automation: Integrating Octopus Energy & More
Thank you and I agree most people can stay clear of net...
By Batpred , 1 day ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
@jamespa Yes that post.
By dgclimatecontrol , 1 day ago
-
RE: Faulty Clivet heat pump out of the box
@steveimpey glad you got it sorted and agreed- being ig...
By benson , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
@agentgeorge it has got 2, the other bleed screw is the...
By AdamK , 2 days ago
-
I too felt the podcast was useful but think it could do...
By AndrewJ , 2 days ago
-
Putting a 30 cm. radio controlled wall clock on Freegle...
By Toodles , 2 days ago