Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Mitsubishi Ecodan stuck on immersion symbol
That’s definitely cycling do you have UFH or rads regardless of which it would suggest you have only a very small proportion of the heating system calling g for heat. Do you have a lot of zoning in the house?
That will be the cause then, with only 1 thermostat calling for heat the water volume is too small it heats quickly and the heat pump has to turn off then back on again when it cools. Ideally you want all circuits calling at the same time. What make of thermostats are the UFH zones on? Do they connect to a wiring centre that turns the actuators on for each circuit? If so you can unscrew the actuators for the UFH loops that will mean they are all open all the time so when one zone calls for heat water will flow round them all. This will mean you have more water volume for the heat pump to react to giving it more chance to find the correct input power before the water over heats
I have 1 of each of the right Mitsubishi controller, one on the ground floor and one on the 1st floor. The EPH controllers control the actuators. I have a EPH controller in every room, around 5, on the ground floor for the UFH. The Mitsubishi is wireless and the EPH is hardwired.
So presumably the EPH thermostats are wired back to a controller near to the UFH manifold? Do you have a picture of that?
@gary That's in an awkward place, hard to get to. The EPH do control the actuators, but the underfloor heating won't come on until the Mitsubishi controller temperate is set above the current room temperature..
Yep that all makes sense the easiest solution is to remove all the actuators from the UFH manifold they should just unscrew them all loops will be open when thermostats call for heat.
Or as you need the mitsi thermostat to be calling for heat for the heat pump to fire up. Then just increase the temp on all the 5 zone stats to a high level then the UFH will only come on when the mitsi thermostat calls for heat. Depending how it’s wired then downside of that may be that there is an extra circulation pump for the UFH that will run constantly once you set the zone thermostats to constantly call for heat
Ideally you want it all to come on at the same time. When my hall thermostat calls for heat all of the UFH loops downstairs come on and all the rads upstairs come on. Upstairs can be kept cooler than downstairs by turning down the lock shield valves to reduce flow. If you have more water volume you can run at lower flow temps without cycling
- 27 Forums
- 2,778 Topics
- 65.5 K Posts
- 1,670 Online
- 7,185 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Say hello and introduce yourself
@olivierm welcome to the forums and finding the right i...
By Mars , 58 minutes ago
-
RE: Estimating true heat loss from twelve months of consumption data
Finally, after what seems like an eternity, we paid a d...
By ian33a , 5 hours ago
-
RE: Replacing Storage Heaters with a Heat Pump in a Stone Cottage
@paul1098 — as we are getting down to the nitty gritty,...
By cathodeRay , 16 hours ago
-
RE: Tesla Powerwall (2) Calibration Cycles
I’ve had two calibration cycles in the last three month...
By Davesoa , 21 hours ago
-
RE: Is This Initial Free Quote From Octopus Trusted Partner Reasonable?
@editor That's a pity, but thank you for checking. I'l...
By ltron2 , 1 day ago
-
My fifth heat pump book, Heat Pumps Explained, is out n...
By Mars , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
Just furkled Into the parameter menu. Found the master ...
By AgentGeorge , 2 days ago
-
RE: Analysis of the economics of switching to an A2W ASHP compared to other heat sources
It's interesting that Norway with a much colder climate...
By Rob of York , 2 days ago
-
RE: Review your electricity provider
Happy to add Scottish Power and the review 'dont touch ...
By JamesPa , 2 days ago
-
RE: Is it just me, or does tradesperson timekeeping and communication drive you absolutely mad?
Yes, and I would suggest likely to get worse with more ...
By Batpred , 4 days ago
-
RE: Electricity price predictions
This topic seems more suitable for this thread... I a...
By Batpred , 4 days ago
-
RE: Why are ASHP installs so expensive?
It is clearly difficult to say, there must be cases whe...
By Batpred , 4 days ago
-
RE: Panasonic Free Multi Z and Etherea Internal units.
@dgclimatecontrol Thank you for that information and re...
By Toodles , 4 days ago
-
RE: My Kronoterm Adapt 0312 ASHP is finally installed!
@editor It was serendipitous really. Both my wife and I...
By tomasmcguinness , 4 days ago