Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Mitsubishi Ecodan stuck on immersion symbol
They could be defrosts but unlikely at that Frequency.
do you have the MELCloud app that can show the flow and retune temps for those times?
There is an hourly chart that is useful
That’s definitely cycling do you have UFH or rads regardless of which it would suggest you have only a very small proportion of the heating system calling g for heat. Do you have a lot of zoning in the house?
I have UFH on ground floor and rads on 1st floor. 2 Zones have been setup, ground floor and 1st floor. There are also individual thermostats for UFH in each room.
That will be the cause then, with only 1 thermostat calling for heat the water volume is too small it heats quickly and the heat pump has to turn off then back on again when it cools. Ideally you want all circuits calling at the same time. What make of thermostats are the UFH zones on? Do they connect to a wiring centre that turns the actuators on for each circuit? If so you can unscrew the actuators for the UFH loops that will mean they are all open all the time so when one zone calls for heat water will flow round them all. This will mean you have more water volume for the heat pump to react to giving it more chance to find the correct input power before the water over heats
I have 1 of each of the right Mitsubishi controller, one on the ground floor and one on the 1st floor. The EPH controllers control the actuators. I have a EPH controller in every room, around 5, on the ground floor for the UFH. The Mitsubishi is wireless and the EPH is hardwired.
So presumably the EPH thermostats are wired back to a controller near to the UFH manifold? Do you have a picture of that?
@gary That's in an awkward place, hard to get to. The EPH do control the actuators, but the underfloor heating won't come on until the Mitsubishi controller temperate is set above the current room temperature..
Yep that all makes sense the easiest solution is to remove all the actuators from the UFH manifold they should just unscrew them all loops will be open when thermostats call for heat.
Or as you need the mitsi thermostat to be calling for heat for the heat pump to fire up. Then just increase the temp on all the 5 zone stats to a high level then the UFH will only come on when the mitsi thermostat calls for heat. Depending how it’s wired then downside of that may be that there is an extra circulation pump for the UFH that will run constantly once you set the zone thermostats to constantly call for heat
Ideally you want it all to come on at the same time. When my hall thermostat calls for heat all of the UFH loops downstairs come on and all the rads upstairs come on. Upstairs can be kept cooler than downstairs by turning down the lock shield valves to reduce flow. If you have more water volume you can run at lower flow temps without cycling
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 1,047 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 4 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 8 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 10 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 10 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 13 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 19 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 19 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 1 day ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 2 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 3 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago