Mitsubishi Ecodan System Pressure Changes - An Issue or Expected ?
Hi all
I've noticed that my 8.5kw Mitsubishi Ecodan PUHZ-W85VA2 heat pump w pre-plumbed 250L DHW cylinder EHPT25X-UKHCW system pressure changes depending on the mode of operation.
- Heating on AutoAdaptation flow temp circa 40C = system pressure 1.5bar
- Antifreeze mode flow temp circa 20C = system pressure 0.5bar
- System off = system pressure 0bar
Is this normal/expected ?
If not, what could be the cause and how would you go about fixing it ?
I've had this system 7 years and first noticed this about a month ago.
Photo/screenshots from MelCloud attached.
No obvious performance issue noted.
THANKS !
Hello, this sound like expansion and low on water pressure, assuming you have a 2 story house you should have a static pressure of around 1 bar, running pressure of around 1.2 bar and antifreeze mode of between 1 bar and 1.2 bar, the vessel should balance and absorb expansion.
To check this you will need to switch of the system and safely electrically isolate, isolate the expansion vessel and drain it, then using a pump with a gauge pump this vessel through the valve usually at the top to 1.5 bar, place this back into position and refill the system to 1 bar. then fire the unit back up.
If the vessel will not hold its pressure its likely that the bladder is broken and this will need replacing. there are some rules in the UK:
2. Servicing Requirements for Expansion Vessels
A. Regular Maintenance Checks
-
Annual servicing is recommended, often carried out alongside a boiler service.
-
A service should include:
-
Checking pre-charge pressure of the expansion vessel (usually between 0.75 - 1.5 bar).
-
Re-pressurizing if necessary using a foot pump or nitrogen (as per manufacturer’s instructions).
-
Inspecting for leaks, corrosion, or diaphragm failure.
-
B. Signs of a Failing Expansion Vessel
-
Frequent pressure drops in the heating system.
-
Water leaking from the pressure relief valve (PRV).
-
Boiler pressure gauge rising too high when heating is on.
C. Replacement and Repair
-
If an expansion vessel fails (e.g., diaphragm rupture), it must be replaced.
-
Some vessels have external Schrader valves for easy re-pressurization, while others may need complete replacement.
3. Who Can Service an Expansion Vessel?
-
For sealed heating systems, a qualified heating engineer or plumber can service the vessel.
-
For unvented hot water cylinders, only a G3-qualified engineer can work on the expansion vessel.
4. Compliance & Best Practices
-
Always follow the manufacturer's servicing guidelines.
-
Ensure servicing records are kept, especially for landlords (required under the Landlord and Tenant Act 1985).
-
Commercial systems may have additional requirements under The Pressure Systems Safety Regulations (PSSR) 2000.
Expansion is important for the system to run correctly so it may be worth getting a qualified engineer if you are not sure.
@ashp-bobba thanks ! Ok so it's likely the expansion vessel. It's been replaced twice already. Last time about 2yrs ago. Will get in touch with a local heating engineer (again).
@alsocold123456 I would have thought it would last a bit longer than that. Its worth checking out, it may have just lost some air pressure, this is something your service engineer would have checked on the last service.
-
Transforming a Derbyshire Property into an Energy-Efficient Haven
3 weeks ago
-
Ecodan ASHP - How to optimise my set up?
3 weeks ago
-
Oversized Ecodan
1 month ago
-
Ecodan consuming 100kwh per day in new build!!!
1 month ago
-
Mitsubishi Ecodan 11kw Defrosting Issue.
3 months ago
Recently viewed by users: Judith 35 minutes ago.
- 22 Forums
- 2,010 Topics
- 43.9 K Posts
- 49 Online
- 3,182 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: What happens when the outside temperature exceeds the upper WC point?
@editor Thanks Mars, thats very helpful
By bontwoody , 3 minutes ago
-
RE: A question about battery life
Here's my take on this with some rough maths that might...
By Mars , 16 minutes ago
-
RE: Is it KISS or constant – weather compensation vs. set flow temperature?
I had to laugh at this as I do exactly the same thing, ...
By Grantmethestrength , 21 minutes ago
-
Would You Find Value in a Premium Installer-Supported Forum?
We’re exploring the idea of introducing a premium forum...
By Mars , 27 minutes ago
-
@eliuccio there are some very high level arguments in t...
By Judith , 37 minutes ago
-
RE: Is my Samsung heat pump working too well?
@pooneil Apparently you can set up a different water la...
By bontwoody , 1 hour ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
That's fine @irmartini and @editorbut let's keep this i...
By Transparent , 2 hours ago
-
RE: Battery sizing - How low can you go!
So just for completeness here is may last update on thi...
By bontwoody , 2 hours ago
-
RE: Grant Aerona fine tuning advice needed
To be honest our figures are all over the place as we o...
By Grantmethestrength , 2 hours ago
-
RE: Mitsubishi Ecodan System Pressure Changes - An Issue or Expected ?
@alsocold123456 I would have thought it would last a bi...
By ASHP-BOBBA , 17 hours ago
-
RE: Are Homeowners Being Silenced Over Faulty Heat Pumps?
This is sad to hear and should not happen, to give you ...
By ASHP-BOBBA , 17 hours ago
-
@editor Thank you for the information,do you have any i...
By Potatoman , 21 hours ago
-
@cathoderay Years ago (40+) I enquired about moving our...
By Toodles , 24 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
I didn't realise that Samsung even had customer support...
By JamesPa , 1 day ago
-
RE: New Heat Pump - mixer shower pressure
Just a little update, I eventually decided to put a pre...
By Spanners , 1 day ago
-
RE: Setback savings - fact or fiction?
I'm not a statistician, but I have had to use statistic...
By cathodeRay , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@matthew_w It's a complex area and every case is diff...
By JamesPa , 3 days ago
-
RE: Multiple simultaneous connections to Samsung R290 heat pump via Modbus
Thanks for the various replies. I've tried to summari...
By Angus , 3 days ago
-
RE: Help me keep the faith with my installation
@adamk Yes, it's a good way and an alternative to (o...
By JamesPa , 3 days ago
Most Active This Week
# | Name | kWhs |
---|---|---|
1 | Mars | 396 |
2 | JamesPa | 169 |
3 | bontwoody | 160 |
4 | Pooneil | 158 |
5 | Majordennisbloodnok | 120 |
6 | Heatgeek | 111 |
7 | Toodles | 108 |
8 | Transparent | 105 |
9 | cathodeRay | 94 |
10 | IRMartini | 72 |