Mitsubishi Ecodan System Pressure Changes - An Issue or Expected ?
Hi all
I've noticed that my 8.5kw Mitsubishi Ecodan PUHZ-W85VA2 heat pump w pre-plumbed 250L DHW cylinder EHPT25X-UKHCW system pressure changes depending on the mode of operation.
- Heating on AutoAdaptation flow temp circa 40C = system pressure 1.5bar
- Antifreeze mode flow temp circa 20C = system pressure 0.5bar
- System off = system pressure 0bar
Is this normal/expected ?
If not, what could be the cause and how would you go about fixing it ?
I've had this system 7 years and first noticed this about a month ago.
Photo/screenshots from MelCloud attached.
No obvious performance issue noted.
THANKS !
Hello, this sound like expansion and low on water pressure, assuming you have a 2 story house you should have a static pressure of around 1 bar, running pressure of around 1.2 bar and antifreeze mode of between 1 bar and 1.2 bar, the vessel should balance and absorb expansion.
To check this you will need to switch of the system and safely electrically isolate, isolate the expansion vessel and drain it, then using a pump with a gauge pump this vessel through the valve usually at the top to 1.5 bar, place this back into position and refill the system to 1 bar. then fire the unit back up.
If the vessel will not hold its pressure its likely that the bladder is broken and this will need replacing. there are some rules in the UK:
2. Servicing Requirements for Expansion Vessels
A. Regular Maintenance Checks
-
Annual servicing is recommended, often carried out alongside a boiler service.
-
A service should include:
-
Checking pre-charge pressure of the expansion vessel (usually between 0.75 - 1.5 bar).
-
Re-pressurizing if necessary using a foot pump or nitrogen (as per manufacturer’s instructions).
-
Inspecting for leaks, corrosion, or diaphragm failure.
-
B. Signs of a Failing Expansion Vessel
-
Frequent pressure drops in the heating system.
-
Water leaking from the pressure relief valve (PRV).
-
Boiler pressure gauge rising too high when heating is on.
C. Replacement and Repair
-
If an expansion vessel fails (e.g., diaphragm rupture), it must be replaced.
-
Some vessels have external Schrader valves for easy re-pressurization, while others may need complete replacement.
3. Who Can Service an Expansion Vessel?
-
For sealed heating systems, a qualified heating engineer or plumber can service the vessel.
-
For unvented hot water cylinders, only a G3-qualified engineer can work on the expansion vessel.
4. Compliance & Best Practices
-
Always follow the manufacturer's servicing guidelines.
-
Ensure servicing records are kept, especially for landlords (required under the Landlord and Tenant Act 1985).
-
Commercial systems may have additional requirements under The Pressure Systems Safety Regulations (PSSR) 2000.
Expansion is important for the system to run correctly so it may be worth getting a qualified engineer if you are not sure.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba thanks ! Ok so it's likely the expansion vessel. It's been replaced twice already. Last time about 2yrs ago. Will get in touch with a local heating engineer (again).
@alsocold123456 I would have thought it would last a bit longer than that. Its worth checking out, it may have just lost some air pressure, this is something your service engineer would have checked on the last service.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
-
Mitsubishi Ecodan 11kw Defrosting Issue.
2 months ago
-
Ecodan consuming 100kwh per day in new build!!!
4 months ago
-
Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
6 months ago
-
Ecodan 11.2kw Wireless thermostat drop outs
7 months ago
-
Transforming a Derbyshire Property into an Energy-Efficient Haven
8 months ago
- 26 Forums
- 2,242 Topics
- 49.9 K Posts
- 517 Online
- 5,903 Members
Join Us!
Podcast Picks
Latest Posts
-
Apologies as my post clearly interrupted this flow. Whe...
By Batpred , 5 minutes ago
-
RE: One room is colder than the rest of the house
I would personally be sceptical about reaching any conc...
By JamesPa , 15 minutes ago
-
@davidalgarve So Air-to-Air talks a different version o...
By F1p , 24 minutes ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
If you paid for any of the assessments try asking for t...
By JamesPa , 2 hours ago
-
@drei Thats a nice designer radiator which it would ...
By JamesPa , 2 hours ago
-
I've created a separate post here, wondering about radi...
By DREI , 3 hours ago
-
Mitsubishi Ecodan R290 10kW performance
I have just had a Mitsubishi Ecodan R290 10 kW heat pum...
By Ecoste , 4 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@ecoste, @walnut-tree-cottage these are both great piec...
By JamesPa , 4 hours ago
-
RE: New build installation query
That suggests to me that you have loss of heat in the p...
By Transparent , 6 hours ago
-
RE: Solar inverters - where does the energy go when clipping?
You will, of course, check the dimensions and weight be...
By Transparent , 8 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - there may be other ways you can improve t...
By cathodeRay , 9 hours ago
-
RE: What should we do with our Aga?
@annahickson We had a similar dilemma with our oil-fire...
By Morgan , 10 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
17l/min is enough for only 6kW at 5C DT, not surprising...
By JamesPa , 11 hours ago
-
@bontwoody The extra battery capacity is the solution f...
By Toodles , 12 hours ago
-
RE: End of Summer Time Reminder to Ecodan owners
As I understand it....ha....Melcoud will over ride any ...
By Abernyte , 12 hours ago
-
Finding flow temp data from Samsung 16kw HP
Hello, I have a Samsung MIM-E03 16kwh heat pump, and ...
By martingale , 21 hours ago
-
RE: Faulty Clivet heat pump out of the box
We would never win these projects as we spend 1 whole d...
By ASHP-BOBBA , 23 hours ago
-
RE: Ecodan Melcloud Temperature Change
@gruff2001 - if set on WC, the app is only communicatin...
By ASHP-BOBBA , 23 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@toodles indeed. the question of proof will only get ...
By Tim441 , 1 day ago