Mitsubishi Ecodan System Pressure Changes - An Issue or Expected ?
Hi all
I've noticed that my 8.5kw Mitsubishi Ecodan PUHZ-W85VA2 heat pump w pre-plumbed 250L DHW cylinder EHPT25X-UKHCW system pressure changes depending on the mode of operation.
- Heating on AutoAdaptation flow temp circa 40C = system pressure 1.5bar
- Antifreeze mode flow temp circa 20C = system pressure 0.5bar
- System off = system pressure 0bar
Is this normal/expected ?
If not, what could be the cause and how would you go about fixing it ?
I've had this system 7 years and first noticed this about a month ago.
Photo/screenshots from MelCloud attached.
No obvious performance issue noted.
THANKS !
Hello, this sound like expansion and low on water pressure, assuming you have a 2 story house you should have a static pressure of around 1 bar, running pressure of around 1.2 bar and antifreeze mode of between 1 bar and 1.2 bar, the vessel should balance and absorb expansion.
To check this you will need to switch of the system and safely electrically isolate, isolate the expansion vessel and drain it, then using a pump with a gauge pump this vessel through the valve usually at the top to 1.5 bar, place this back into position and refill the system to 1 bar. then fire the unit back up.
If the vessel will not hold its pressure its likely that the bladder is broken and this will need replacing. there are some rules in the UK:
2. Servicing Requirements for Expansion Vessels
A. Regular Maintenance Checks
-
Annual servicing is recommended, often carried out alongside a boiler service.
-
A service should include:
-
Checking pre-charge pressure of the expansion vessel (usually between 0.75 - 1.5 bar).
-
Re-pressurizing if necessary using a foot pump or nitrogen (as per manufacturer’s instructions).
-
Inspecting for leaks, corrosion, or diaphragm failure.
-
B. Signs of a Failing Expansion Vessel
-
Frequent pressure drops in the heating system.
-
Water leaking from the pressure relief valve (PRV).
-
Boiler pressure gauge rising too high when heating is on.
C. Replacement and Repair
-
If an expansion vessel fails (e.g., diaphragm rupture), it must be replaced.
-
Some vessels have external Schrader valves for easy re-pressurization, while others may need complete replacement.
3. Who Can Service an Expansion Vessel?
-
For sealed heating systems, a qualified heating engineer or plumber can service the vessel.
-
For unvented hot water cylinders, only a G3-qualified engineer can work on the expansion vessel.
4. Compliance & Best Practices
-
Always follow the manufacturer's servicing guidelines.
-
Ensure servicing records are kept, especially for landlords (required under the Landlord and Tenant Act 1985).
-
Commercial systems may have additional requirements under The Pressure Systems Safety Regulations (PSSR) 2000.
Expansion is important for the system to run correctly so it may be worth getting a qualified engineer if you are not sure.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba thanks ! Ok so it's likely the expansion vessel. It's been replaced twice already. Last time about 2yrs ago. Will get in touch with a local heating engineer (again).
@alsocold123456 I would have thought it would last a bit longer than that. Its worth checking out, it may have just lost some air pressure, this is something your service engineer would have checked on the last service.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
-
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
6 hours ago
-
Ecodan Zone 2 Mitshibishi thermostat Auto Adapt
3 weeks ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
1 month ago
-
New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
1 month ago
-
Ecodan with FTC7 - True Weather Compensation
1 month ago
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 298 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Electricity price predictions
@skd I think your guess might well be right - unfortuna...
By Toodles , 2 minutes ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
@majordennisbloodnok I’m glad I posted this. There see...
By AndrewJ , 13 minutes ago
-
RE: What determines the SOC of a battery?
@batpred I didn't write the Seplos BMS software, I a...
By Bash , 1 hour ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@tasos and @cathoderay thanks. I have some history grap...
By benson , 2 hours ago
-
I am having my existing heat pump changed to a Vaillant...
By trebor12345 , 3 hours ago
-
Our Experience installing a heat pump into a Grade 2 Listed stone house
First want to thank everybody who has contributed to th...
By Travellingwave , 3 hours ago
-
RE: Setback savings - fact or fiction?
@cathoderay The input power is largely determined by...
By RobS , 4 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 6 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 6 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 7 hours ago
-
@painter26 — as @jamespa says, it's for filling and re-...
By cathodeRay , 11 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 22 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 24 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 1 day ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 1 day ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago