Mitsubishi Ecodan System Pressure Changes - An Issue or Expected ?
Hi all
I've noticed that my 8.5kw Mitsubishi Ecodan PUHZ-W85VA2 heat pump w pre-plumbed 250L DHW cylinder EHPT25X-UKHCW system pressure changes depending on the mode of operation.
- Heating on AutoAdaptation flow temp circa 40C = system pressure 1.5bar
- Antifreeze mode flow temp circa 20C = system pressure 0.5bar
- System off = system pressure 0bar
Is this normal/expected ?
If not, what could be the cause and how would you go about fixing it ?
I've had this system 7 years and first noticed this about a month ago.
Photo/screenshots from MelCloud attached.
No obvious performance issue noted.
THANKS !
Hello, this sound like expansion and low on water pressure, assuming you have a 2 story house you should have a static pressure of around 1 bar, running pressure of around 1.2 bar and antifreeze mode of between 1 bar and 1.2 bar, the vessel should balance and absorb expansion.
To check this you will need to switch of the system and safely electrically isolate, isolate the expansion vessel and drain it, then using a pump with a gauge pump this vessel through the valve usually at the top to 1.5 bar, place this back into position and refill the system to 1 bar. then fire the unit back up.
If the vessel will not hold its pressure its likely that the bladder is broken and this will need replacing. there are some rules in the UK:
2. Servicing Requirements for Expansion Vessels
A. Regular Maintenance Checks
-
Annual servicing is recommended, often carried out alongside a boiler service.
-
A service should include:
-
Checking pre-charge pressure of the expansion vessel (usually between 0.75 - 1.5 bar).
-
Re-pressurizing if necessary using a foot pump or nitrogen (as per manufacturer’s instructions).
-
Inspecting for leaks, corrosion, or diaphragm failure.
-
B. Signs of a Failing Expansion Vessel
-
Frequent pressure drops in the heating system.
-
Water leaking from the pressure relief valve (PRV).
-
Boiler pressure gauge rising too high when heating is on.
C. Replacement and Repair
-
If an expansion vessel fails (e.g., diaphragm rupture), it must be replaced.
-
Some vessels have external Schrader valves for easy re-pressurization, while others may need complete replacement.
3. Who Can Service an Expansion Vessel?
-
For sealed heating systems, a qualified heating engineer or plumber can service the vessel.
-
For unvented hot water cylinders, only a G3-qualified engineer can work on the expansion vessel.
4. Compliance & Best Practices
-
Always follow the manufacturer's servicing guidelines.
-
Ensure servicing records are kept, especially for landlords (required under the Landlord and Tenant Act 1985).
-
Commercial systems may have additional requirements under The Pressure Systems Safety Regulations (PSSR) 2000.
Expansion is important for the system to run correctly so it may be worth getting a qualified engineer if you are not sure.
@ashp-bobba thanks ! Ok so it's likely the expansion vessel. It's been replaced twice already. Last time about 2yrs ago. Will get in touch with a local heating engineer (again).
@alsocold123456 I would have thought it would last a bit longer than that. Its worth checking out, it may have just lost some air pressure, this is something your service engineer would have checked on the last service.
-
Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
1 week ago
-
Ecodan 11.2kw Wireless thermostat drop outs
2 weeks ago
-
Ecodan consuming 100kwh per day in new build!!!
2 weeks ago
-
Transforming a Derbyshire Property into an Energy-Efficient Haven
1 month ago
-
Ecodan ASHP - How to optimise my set up?
2 months ago
- 22 Forums
- 2,043 Topics
- 44.5 K Posts
- 47 Online
- 3,264 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Help me understand my Mitsubishi Ecodan system
@robs Sorry to ask silly questions, but how do I access...
By Carpenterstation , 10 minutes ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
Cynically I would suggest its there to protect the inst...
By JamesPa , 4 hours ago
-
RE: Ecodan Legionella cycle - immersion heater problem
Thanks for letting us know @clockworks I admire your ...
By Transparent , 21 hours ago
-
@fillib what a wonderful result, both for you personall...
By Judith , 1 day ago
-
RE: Revised version of MCS-020 (noise standards for heat pumps)
As you say this is no change, which I personally think ...
By JamesPa , 1 day ago
-
RE: What happens when the outside temperature exceeds the upper WC point?
@editor not via the WC curve but as @old_scientist ment...
By bontwoody , 1 day ago
-
RE: MHHS and Heat Pump compatibility
@toodles to be clear I don't know if there will be a re...
By Scalextrix , 2 days ago
-
I did not know this concept, although others might. I...
By Morgan , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk it's probably filtering different providers in t...
By Mars , 2 days ago
-
RE: why solar diverters for HW instead of the heat pump?
I should probably add to my comments above that, whilst...
By JamesPa , 3 days ago
-
RE: Commencing on an ASHP Installation Process
Lots of reading and questioning which the background ma...
By JamesPa , 3 days ago
-
RE: The Great British Heat Pump Quiz
Not sure how that happened 🤣 I suspect that it ...
By Mars , 3 days ago
-
RE: Help with understanding my Mitsubishi Ecodan air source heat pump
@patch I think @ashp-bobba gave you some great pointers...
By SUNandAIR , 4 days ago
-
RE: Installing your own ASHP - DIY
Hi @tomasmcguinness, how are you progressing with this?...
By Ashfp , 4 days ago
-
RE: Say hello and introduce yourself
Welcome to the forum. If you are new to ASHPs I sug...
By JamesPa , 4 days ago
-
RE: The Rise and Fall of Europe’s Most Generous Green Subsidy
This is where the cold water storage tank was situated;...
By Dwynwen , 5 days ago
-
RE: Air Source Heat Pump - Side Alley Suitability
Thats probably fair enough. The degree-days calculatio...
By JamesPa , 5 days ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
That’s interesting, but obviously concerning also…. Do ...
By SUNandAIR , 6 days ago
-
RE: In the middle of an ASHP installation - a few questions (and issues)
Thank you @robs - that very useful data. The issue wa...
By Transparent , 6 days ago