Mitsubishi Ecodan System Pressure Changes - An Issue or Expected ?
Hi all
I've noticed that my 8.5kw Mitsubishi Ecodan PUHZ-W85VA2 heat pump w pre-plumbed 250L DHW cylinder EHPT25X-UKHCW system pressure changes depending on the mode of operation.
- Heating on AutoAdaptation flow temp circa 40C = system pressure 1.5bar
- Antifreeze mode flow temp circa 20C = system pressure 0.5bar
- System off = system pressure 0bar
Is this normal/expected ?
If not, what could be the cause and how would you go about fixing it ?
I've had this system 7 years and first noticed this about a month ago.
Photo/screenshots from MelCloud attached.
No obvious performance issue noted.
THANKS !
Hello, this sound like expansion and low on water pressure, assuming you have a 2 story house you should have a static pressure of around 1 bar, running pressure of around 1.2 bar and antifreeze mode of between 1 bar and 1.2 bar, the vessel should balance and absorb expansion.
To check this you will need to switch of the system and safely electrically isolate, isolate the expansion vessel and drain it, then using a pump with a gauge pump this vessel through the valve usually at the top to 1.5 bar, place this back into position and refill the system to 1 bar. then fire the unit back up.
If the vessel will not hold its pressure its likely that the bladder is broken and this will need replacing. there are some rules in the UK:
2. Servicing Requirements for Expansion Vessels
A. Regular Maintenance Checks
-
Annual servicing is recommended, often carried out alongside a boiler service.
-
A service should include:
-
Checking pre-charge pressure of the expansion vessel (usually between 0.75 - 1.5 bar).
-
Re-pressurizing if necessary using a foot pump or nitrogen (as per manufacturer’s instructions).
-
Inspecting for leaks, corrosion, or diaphragm failure.
-
B. Signs of a Failing Expansion Vessel
-
Frequent pressure drops in the heating system.
-
Water leaking from the pressure relief valve (PRV).
-
Boiler pressure gauge rising too high when heating is on.
C. Replacement and Repair
-
If an expansion vessel fails (e.g., diaphragm rupture), it must be replaced.
-
Some vessels have external Schrader valves for easy re-pressurization, while others may need complete replacement.
3. Who Can Service an Expansion Vessel?
-
For sealed heating systems, a qualified heating engineer or plumber can service the vessel.
-
For unvented hot water cylinders, only a G3-qualified engineer can work on the expansion vessel.
4. Compliance & Best Practices
-
Always follow the manufacturer's servicing guidelines.
-
Ensure servicing records are kept, especially for landlords (required under the Landlord and Tenant Act 1985).
-
Commercial systems may have additional requirements under The Pressure Systems Safety Regulations (PSSR) 2000.
Expansion is important for the system to run correctly so it may be worth getting a qualified engineer if you are not sure.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
@ashp-bobba thanks ! Ok so it's likely the expansion vessel. It's been replaced twice already. Last time about 2yrs ago. Will get in touch with a local heating engineer (again).
@alsocold123456 I would have thought it would last a bit longer than that. Its worth checking out, it may have just lost some air pressure, this is something your service engineer would have checked on the last service.
Professional installer. Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
-
Mitsubishi Ecodan 11kw Defrosting Issue.
6 days ago
-
Ecodan consuming 100kwh per day in new build!!!
2 months ago
-
Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
5 months ago
-
Ecodan 11.2kw Wireless thermostat drop outs
5 months ago
-
Transforming a Derbyshire Property into an Energy-Efficient Haven
6 months ago
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 52 Online
- 5,744 Members
Join Us!
Podcast Picks
Latest Posts
-
What brand is the stat? We had a similar issue and w...
By Mars , 1 second ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
That has always been my most likely explanation, in whi...
By cathodeRay , 6 minutes ago
-
@bontwoody, I’ve made contact with @mixergy on your beh...
By Mars , 7 minutes ago
-
@jamespa Ours is a Daikin EDLA03 8 kW and the Delta T =...
By Toodles , 19 minutes ago
-
RE: Big Changes Coming to Our Heat Pump System
Day one is done. The system’s been fully flushed and ...
By Mars , 15 hours ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 17 hours ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 17 hours ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 17 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 20 hours ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 2 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 2 days ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I hear you on the locality issue @transparent, and I ag...
By Scalextrix , 2 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 2 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 4 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 4 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 5 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 5 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 5 days ago