MIDEA MHC-V16W/D2RN8-Β Power Input Limitation
Hello, I would like to ask a question.
I have installed a MIDEA MHC-V16W/D2RN8-Β heat pump with MIDEA fan coils and when the weather is hot outside (>15oC) it cycles a lot at the heat mode...
There is an option "Power Input Limitation" on the service menu. Does this reduce the capacity of the heat pump in order to have less cycling?
I have made some tests but I cannot figure what exactly happens with that option.
Thank you very much!
(I'm sorry for my bad English)
I performed some more tests...
With power input limitation set to 8, the lowest output that I get from the ASHP is around 3kW with 10oC external temperature at 38oC water temperature (with WC).
With this setup I have now 2 cycles / hour ... I think it is better now...
There is no option to measure the COP but I consume 12kWh/24h for heating (140 sq.m. - fancoil thermsotats set at 23-24oC)
Have you managed to make it work lower?
Thank you very much!
- 26 Forums
- 2,406 Topics
- 54.6 K Posts
- 397 Online
- 6,092 Members
Join Us!
Worth Watching
Latest Posts
-
RE: New Daikin 11kW Altherma 3M install - is it working as it should?
I forgot to mention: Octopus measured our heat loss at ...
By Toodles , 3 minutes ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
When the grid is off, there it could be that the neutra...
By Batpred , 11 minutes ago
-
RE: Considering MLCP (Multi-Layer Composite Pipe) for ASHP
Thanks Mars and thank you for reaching out to so many p...
By iotum , 24 minutes ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: @davec Manufacturer: Peak Energy Mode...
By DaveC , 25 minutes ago
-
RE: Rate the quality of your heat pump design and installation
@radwhispererdwhisperereorourkeditor Well, the guy came...
By razz , 29 minutes ago
-
RE: Setback savings - fact or fiction?
Given the weather has been relatively stable, the empir...
By Batpred , 1 hour ago
-
RE: Post-Traumatic Heat Pump Stress Disorder
@jamespa Hi James - thanks so much! That sounds like ut...
By johnbroome , 2 hours ago
-
RE: Heat pump not reaching flow temperature
@jamespa system design was for 40 degrees FT at -2 degr...
By DaveC , 2 hours ago
-
RE: GSHP WOES! Midland based engineer recommendations?
@editor That is very kind! Thank you so much.
By johnbroome , 2 hours ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@wally Hi I am not sure how large your house is b...
By TechnoGeek , 4 hours ago
-
Please help with the settings ecodan
I have a 160 square meter house, first floor 6 radiator...
By nose1972 , 4 hours ago
-
RE: Predicted Heat Loss & Needs from MCS calcs vs EPC vs actual
I've been thinking along similar lines to @tim441 from ...
By Sheriff Fatman , 4 hours ago
-
Thanks, @technogeek. Good to hear about the accuracy. ...
By Majordennisbloodnok , 4 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
In my case it was a very specific pattern of behaviour ...
By Sheriff Fatman , 5 hours ago
-
RE: Vaillant aroTherm not heating with many faults
@ashp-bobba Yeah I'll give it a go, will check filter...
By Anon67 , 5 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@transparent Perhaps the names at the end of the docume...
By Toodles , 5 hours ago
-
RE: Heatpunk Floor plan issues
@jamiejones85 A2A they will design on dynamic heat loss...
By ASHP-BOBBA , 6 hours ago
-
RE: Fan unit Making terrible noise HELP!!
can you post a video looking inside, at and through the...
By ASHP-BOBBA , 6 hours ago
-
RE: Power outages and storms: A surprisingly good DNO experience
Agreed, which is no more nor less than a customer shoul...
By Majordennisbloodnok , 23 hours ago