[Solved] Low shower pressure after ASHP retrofit
Posted by: @jacs@derek-m not sure on the cylinder pressure but the flow drops massively when I open multiple taps, almost to a stop.
When you say that the flow drops massively, I assume this is at the shower head. It would appear that you have some form of restriction that is limiting the flow from or to the hot water cylinder, such that opening more taps will mean that this limited flow is being shared over more 'openings'. Because the shower head is higher than the taps it is more likely that this will lose flow first.
Try turning the shower 'cold' and open some cold taps. If the flow through the shower head remains constant then the problem is not with the shower, but is some form of restriction in the 'hot' pipework.
I would suggest that you check the pipework from the shower head back to the hot water cylinder for partially closed valves or thinner pipework. Also check the pipework from the mains supply to the hot water cylinder.
If, as Johnmo suggests, the problem is due to a pressure imbalance at the shower unit, you should ask your installer to fit a pressure reducing valve on the cold water feed to the shower unit. It should then be possible to set both the hot and cold feed to 3 bar.
@johnmo Hi, please can you confirm what balance flow is?
I turned the shower to cold and opened the cold taps and the shower flow didn't change.
Most mixers uses a balanced flow i.e. the flow pressure from hot and cold is the same. This is how it is normally achieved via the combined valve at the UVC
If you don't have this setup, you really need a check valve on the hot outlet of the cylinder to prevent reverse flow.
The alternative to the balanced flow connection on the combi valve is a prv at the cold water entry to the house set at 3bar or less. Mine is after stop cock, and strainer, then prv then to the rest of the house.
Your cold water test shows it's not a cold issue. So all that is left is the hot water supply. Testing hot on its own isn't really possible because there may always be a mix of cold going into the hot side of the mixer.
Problem resolved - there was a reducing valve under the bathtub restricting flow.
@jacs brilliant. Thanks for letting us know, and glad you’ve resolved it.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Our newly fitted shower system was regularly running to cold if paused. The excellent plumber fitting the ashp solved it by fitting a pressure control valve on the inlet cold feed.
Different symptoms but same root cause the mixer shower needed balanced pressure feeds. Why the original plumber didn’t fit one is a good question.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
-
Yes, the "zoning with ASHP" topic again...
2 months ago
-
My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
5 months ago
-
Has anyone seen this problem before? Huge anticycling times
8 months ago
-
My British Gas – Heat Force ASHP Installation: A Frustrating Experience
9 months ago
-
Advice needed on inefficient Samsung ASHP installation
10 months ago
- 22 Forums
- 2,096 Topics
- 46.2 K Posts
- 42 Online
- 3,383 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness, I think your best bet would be using ...
By Aventus Eco , 6 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles all depends on asking the right questions! And...
By Tim441 , 8 hours ago
-
RE: Mitsubishi cycling while on chilled water output
I absolutely wouldn't remove the buffer altogether, I'd...
By JamesPa , 14 hours ago
-
RE: Commencing on an ASHP Installation Process
I received confirmation this morning that my Greener Ho...
By Sheriff Fatman , 17 hours ago
-
@jamespa Thanks for the advice - very helpful. I had al...
By abam48 , 2 days ago
-
RE: Weather compensated secondary circuits with Biomass
Hi @andycoo we do an LK 110 standalone weather compensa...
By Sune , 2 days ago
-
RE: Adding battery storage to SolarEdge PV system
@chandykris No need to apologise at all! I forgot to ad...
By Toodles , 3 days ago
-
RE: Say hello and introduce yourself
Yes please do Suggesting a loss in the region...
By JamesPa , 3 days ago
-
As I have reported elsewhere we turned on the cooling o...
By downfield , 3 days ago
-
-
@el3b Hi, sorry to hear that, it is advisable to instal...
By ASHP-BOBBA , 4 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn Out of intrigue, the thread reads as though Ai...
By Sheriff Fatman , 5 days ago
-
RE: Mitsubishi Ecodan Fails to Heat Water despite temperature drop
@m1kegibson If you are able to access the service me...
By HarriUp , 5 days ago