[Solved] Low shower pressure after ASHP retrofit
Posted by: @jacs@derek-m not sure on the cylinder pressure but the flow drops massively when I open multiple taps, almost to a stop.
When you say that the flow drops massively, I assume this is at the shower head. It would appear that you have some form of restriction that is limiting the flow from or to the hot water cylinder, such that opening more taps will mean that this limited flow is being shared over more 'openings'. Because the shower head is higher than the taps it is more likely that this will lose flow first.
Try turning the shower 'cold' and open some cold taps. If the flow through the shower head remains constant then the problem is not with the shower, but is some form of restriction in the 'hot' pipework.
I would suggest that you check the pipework from the shower head back to the hot water cylinder for partially closed valves or thinner pipework. Also check the pipework from the mains supply to the hot water cylinder.
If, as Johnmo suggests, the problem is due to a pressure imbalance at the shower unit, you should ask your installer to fit a pressure reducing valve on the cold water feed to the shower unit. It should then be possible to set both the hot and cold feed to 3 bar.
@johnmo Hi, please can you confirm what balance flow is?
I turned the shower to cold and opened the cold taps and the shower flow didn't change.
Most mixers uses a balanced flow i.e. the flow pressure from hot and cold is the same. This is how it is normally achieved via the combined valve at the UVC
If you don't have this setup, you really need a check valve on the hot outlet of the cylinder to prevent reverse flow.
The alternative to the balanced flow connection on the combi valve is a prv at the cold water entry to the house set at 3bar or less. Mine is after stop cock, and strainer, then prv then to the rest of the house.
Your cold water test shows it's not a cold issue. So all that is left is the hot water supply. Testing hot on its own isn't really possible because there may always be a mix of cold going into the hot side of the mixer.
Problem resolved - there was a reducing valve under the bathtub restricting flow.
@jacs brilliant. Thanks for letting us know, and glad you’ve resolved it.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Our newly fitted shower system was regularly running to cold if paused. The excellent plumber fitting the ashp solved it by fitting a pressure control valve on the inlet cold feed.
Different symptoms but same root cause the mixer shower needed balanced pressure feeds. Why the original plumber didn’t fit one is a good question.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
-
Yes, the "zoning with ASHP" topic again...
4 months ago
-
My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
8 months ago
-
Has anyone seen this problem before? Huge anticycling times
10 months ago
-
My British Gas – Heat Force ASHP Installation: A Frustrating Experience
11 months ago
-
Advice needed on inefficient Samsung ASHP installation
12 months ago
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 73 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
@editor thanks Mars. I've managed to find a phone numbe...
By bontwoody , 6 hours ago
-
@rhh1, I’ll contact Daikin’s brand manager tomorrow and...
By Mars , 6 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
In a way I would like to agree with the final conclusio...
By JamesPa , 9 hours ago
-
RE: Big Changes Coming to Our Heat Pump System
Day one is done. The system’s been fully flushed and ...
By Mars , 10 hours ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 12 hours ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 12 hours ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 12 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 15 hours ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 1 day ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 1 day ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I hear you on the locality issue @transparent, and I ag...
By Scalextrix , 2 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 2 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 3 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 3 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 4 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 4 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 4 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 5 days ago