Is my Ecodan well installed and setup?
@trbob I realise that this thread is a bit old but I have a similar problem with the Legionnaires cycle taking too long. In particular, it is the initial immersion bit which takes 1 hour to get from 50c to 54.5c.
Did you every resolve your issue with the legionnaire Cycle?
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Octopus Fixed Rate
Hi Richard, what I do now (I'm on Octopus Cosy) is to have my Hot Water come on at 12:45pm (heated by the ASHP, the load isn't too bad in the first 15 minutes) and my Legionella Cycle is set to come on at 1pm and lasts for 2 hours. It will let the ASHP get to 51.5 before switching to the immersion element. This seems to be the best way I could find of doing it. I noticed a few weeks ago that it got up to temperature on the Legionella cycle relatively quickly as it was a fairly mild(ish) day, it's a shame that it doesn't end the cycle itself as we could have banked some heating before 4pm.
Mitsubishi Ecodan 8.5kWh
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
@trbob Thanks. Does that mean your system reached the 60c within the 2 hours?
Not sure if I understand your last comment concerning ending the cycle.
According to my Ecodan Legionnaire settings, it's supposed to reach 60c and the stay there for 5 minutes. After 5 minutes it should end the cycle. Unfortunatley, in my case it never reaches the 60c before tiiming out at 2 hours.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Octopus Fixed Rate
@richard24738 Yes it's usually 59 or 60 thereabouts (or sits at 59.5 for ages, not drawing any power), yes mine is set for 5 minutes as well I think, but it has never to my knowledge ended the cycle, it just times out in the end at 3pm.
Mitsubishi Ecodan 8.5kWh
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
@trbob Sounds like the software is switching off the immersion at 59.5c and as it's not reaching the desired 60c, it continues with the cycle waiting to reach 60c, which never comes, and times out after the 2 hours.
I wonder if we are the only Ecodans with this problem?
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Octopus Fixed Rate
@richard24738 My next L cycle is tomorrow conveniently, I'll try to keep an eye on it to see what it does.
Mitsubishi Ecodan 8.5kWh
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
I lowered the temp to 60 (the lowest it will go) for today's cycle. It got to 58 in the expected amount of time, then the element went off and came on after a while, did a bit more and went off again and again it hit the end of the 2 hour window.
I called Mitsubishi and the tech logged in to have a look at it. He seems to think that it may be either the immersion element or some faulty wiring causing the problem. He recommended getting an accredited installer out to look at it rather than Mitsubishi (wait times and £292 fee).
He also said that they normally set it to come on in the early morning, which I might as well do now that the Sun (significant PV power) is gone until Spring. Probably the 10pm to midnight Cosy slot as we don't have the heating on then.
Speaking of which, I asked why we can't have the heating on when the ASHP switches to the immersion element in the L cycle and he said that it's just how their systems are set up unfortunately.
I'll tag @transparent too as there is some cross over with the other thread we've been using.
Mitsubishi Ecodan 8.5kWh
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
@trbob I went down the Mitsi Engineer route unfortunately with the fee.
Report has just come in to say that the immersion had "irregular figures when carrying out Ohm check" so essentially saying faulty immersion heater.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Octopus Fixed Rate
Posted by: @richard24738"irregular figures when carrying out Ohm check" so essentially saying faulty immersion heater.
Eh?
It's just a coil of wire.
How the heck do you get 'irregular figures"?
Check what I said here about Richard's heater being rated by the manufacturer at 3000watts at 240v and 2700watts at 230v
I realise it's actually being driven by an AC waveform, but a quick rule of thumb indicates:
3000 watts of power divided by 240v gives us 12½ Amps [Power in watts = volts x amps]
240v divided by 12½ Amps gives us a (DC) resistance of 19.2 Ω [R=V/I]
So if I disconnected the immersion heater from the mains, and put a meter across the Live & Neutral terminals I'd expect to see a reading around 20-ohms-ish.
Bear in mind that this test is being done on a heater whilst it's cold, and that the resistance is likely to be lower when hot.
The two other possible readings are:
Zero ohms if it's a short-circuit, in which case the fuse/trip should've blown
100,000 Ω or more which is typical of an open circuit when the wire coil is broken
Does 'irregular' mean that none of those three options was encountered?
If so, then why can't a £300 engineer's inspection provide you with the figure? 🤔
Save energy... recycle electrons!
-
Oversized Ecodan
1 week ago
-
Ecodan consuming 100kwh per day in new build!!!
2 weeks ago
-
Ecodan ASHP - How to optimise my set up?
4 weeks ago
-
Mitsubishi Ecodan 11kw Defrosting Issue.
2 months ago
-
Running ASHP efficiently, general thought process. (Low and slow)
2 months ago
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 47 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 44 minutes ago
-
RE: What is the best strategy for operating a very oversized heat pump?
Something else... that works for some people... LG ha...
By Tim441 , 50 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
OMG, the attached schematics (even with incorrect room ...
By BAMi , 2 hours ago
-
RE: Setback savings - fact or fiction?
@cathoderay I see you are continuing to misquote from t...
By SUNandAIR , 2 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
So I turned my thermostats down last night And w...
By Joshua , 2 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 3 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 4 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 15 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 18 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 19 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 21 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 22 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 24 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 3 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 4 hours ago
-
SolarPV tables / online calculator
By MichelleC 11 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 23 hours ago
-
By Toodles 2 days ago