In the middle of an ASHP installation - a few questions (and issues)
Hi all,
Our ASHP installation is underway- and had a few questions. To be honest the contractors haven't been too great so far hence why I wan't to check on this forum at this juncture. Currently the first fix electrics and pipework have been done, as well as most of the radiator swaps. There was an issue with the unit itself in that it was delivered damaged so this has had to be re ordered. No issues- it happens, and another one is on order. On the first day of works the contractor said it wouldn't delay the completion date as they could do other things, including the foundations, in the meantime. I assumed this to mean the foundations for the unit.
The ASHP itself is being sited onto the gable end of the property (south facing), here:
This is an area of gravel with soil underneath. As you can see no prep work has been completed. I am assuming this is wrong if they do try and install it without some form of groundworks? The area of gravel isn't even level as it slopes downwards towards the gate.
Secondly I asked how the weather compensation will work as I assumed a probe would be fitted on another wall. The contractor said the probe is built in within the unit (Clivet Evo Edge). I'm confused how this would work though as the ambient temperature in and around the unit will surely not be the actual external temperature? It is the homely controller that they are installing.
Thanks
It is usual to prepare the groundwork and use solid blocks or slabs on top with gravel in between the blocks for drainage purposes and of course it must be levelled of adjustable feet employed for levelling on the base of the pump.
The sensor is often sited on the rear of the pump case and should sense the ambient temperature at the rear of the unit. When the pump is running, the airflow will of course be the exact temperature of the air sucked into the pump. There are external sensors available for some makes / models of pumps which are normally sited on a northernly facing wall thus not influenced greatly by sunshine. Interested to hear you are having a Homely smart controller - I am very pleased with our Homely controlled Daikin ASHP. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@toodles thanks that makes sense regarding the temp sensing, and confirms what I thought regarding the base. The fact that he mentioned it on day 1 as well- clearly part of the initial plan but now they are over running with the job I just need to keep an eye on them to make sure they don’t cut corners.
Good to hear you are pleased with the homely controller as well
Hi @benson - the outdoor temperature sensor is often within a piece of plastic tubing which hangs at the back of the ASHP.
Somewhere on the forum there's a photo of one, but I can't find it at the moment.
2: The external unit will drip condensate onto the ground.
So your gravel bed needs to allow that to run to the side and down into soil.
If the gravel layer is too thin or the soil unable to absorb the water, then your path will turn into an ice rink in winter.
You know your soil better than the installer.
Use common sense rather than any formula!
3: Heat pumps are often supported by heavy rubber 'feet'.
Here's one as sold by BES
Depending on where you live, this may be all that's required.
However, there are places where heat-pumps get stolen by 'gangs' who come equipped with a trolley jack. 😥
The ASHP itself will invariably have bolt-holes by which it can be secured...
... in which case you might want a concrete pad to bolt it onto, rather than rubber feet.
There are a number of types of 'security bolt/nut' which can be used, rather than a hex-head which could be removed with a spanner.
That means a thief would have to use an angle-grinder on the bolt-heads... which is noisy and attracts attention
Some installers might suggest fitting a couple of strong eye-bolts into the wall behind the heat-pump before it's in position.
A hefty chain can then be used to secure the unit to those eyes.
No mechanism can be completely fool-proof.
Given enough time, a gang could use bolt-cutters, angle-grinders and sledge-hammers to bag themselves a nice new £5k unit sitting outside your house.
The idea is to make your heat-pump less attractive than all the others in the neighbourhood!
Save energy... recycle electrons!
@benson it’s unusual not to have a solid base under the heat pump. Typically, a concrete base or concrete slabs are used, so I’d definitely question the lack of one.
Similar to what @transparent mentioned, the Zeus Articulated Mounted Feet have been widely accepted in the industry for providing stability: https://renewableheatinghub.co.uk/straight-steady-why-your-heat-pump-should-be-level
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Thanks all. It will be mounted on anti vibration feet- that I know. Thus, I have emailed them and asked them to ensure that this is done properly. I cannot see how anti vibration feet on their own are sufficient for a heavy unit, on sloped gravel, and that article above is really handy in terms of knowing now why it needs to be level.
First the ASHP has to sit sit level to with in the limit prescribed in the manufacturers instructions.
The important bit about the weather compensation is the probe can never see the sun. This screws up the temp registered by the heat pump. Being on the sunny side of the building makes little or no difference as the unit takes energy from air which is the same temperature where you site the unit, due to the vast quantities of air consumed.
Just make sure the morning or evening sun cannot see the temperature probe on the rear of the unit.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
To update on this, it transpired that the installers intended on using brackets to wall mount it. To be honest I’ve never seen a wall mounted ashp from scouring forums such as this, photos of installs etc and not least the companies own Facebook page which shows them all with a nice tidy base…
when I reminded them that the quote included ant vibration feet and thus assumed it would be on the ground, they said it could still be wall mounted with the anti vibration feet. Having seen the design of wall brackets I have no idea how this would work….
Long and short of it is Ive told them to prepare a concrete base and install it on the ground. There’s absolutely no practical reason to wall mount it other than save their time.
literally have to watch these people like a hawk but no different to 90% of contractors we’ve had over the years in fairness.
Wall mounted Aircon units are very common. Many ashps include instructions for wall mounting. Perfectly legit as long as the wall is strong enough and you have sufficient clearance. However perhaps more likely to transmit vibration to house so ground mount preferable imho.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@benson I think that ground mount is the better option; there is always the risk of vibration being transmitted into the building structure from the pump - so a good choice there! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@benson I’ve come across ASHPs mounted on walls before. Our neighbour has a large unit attached to the side of their house, but I’ve only seen this done when there’s limited ground space. From the photo you shared, it looks like you’ve got plenty of room, so I think you’ve made the right choice putting it on the ground. This will help minimise any risk of vibrations or reverberations being heard inside the house.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 48 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
OMG, the attached schematics (even with incorrect room ...
By BAMi , 40 minutes ago
-
RE: Setback savings - fact or fiction?
@cathoderay I see you are continuing to misquote from t...
By SUNandAIR , 1 hour ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
So I turned my thermostats down last night And w...
By Joshua , 1 hour ago
-
What is the best strategy for operating a very oversized heat pump?
As the title really. There are at least three live thr...
By JamesPa , 2 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 2 hours ago
-
Heat Pump Sizing & Installation Costs
I’m doing some research for an upcoming article and pod...
By Mars , 2 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 3 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 14 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 17 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 18 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 20 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 21 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 23 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 2 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 3 hours ago
-
SolarPV tables / online calculator
By MichelleC 10 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 22 hours ago
-
By Toodles 2 days ago