HOT TIP - DHW Cylinder Thermostat
Whilst running some tests on the disinfection cycle of my Daikin Mono 16kw I observed that the temperature of the booster heater was only getting up to 59.9C and not reaching the 60c mark. I had set it to reach 60C for 5 mins to satisfy the legionella cycle but it had been running for 30 mins and could not get pass that magic 60c number.
I had a read through the cylinder book and it said "make sure the thermostat is FULLY insterted", so i unscrewed the thermostat gland and found that i could push in the probe another 2-3 inches. Immediately the reported temperature of the DHW went to 62.9C! So just by pushing in the probe right to the end of the pocket the 60c was satisfied and the disinfection cycle completed for the first time ever!
By my calculations that will save 0.5kw of additional heating every time the DHW is run, so that will be a saving of over 180KW per year just by pushing in the probe where it should be.
This is because the water would be heating an extra 3c above the setpoints for my Eco and Confort settings.
see also
Correction, it should say saving of over 540KW per year just by pushing in the probe - as i have HW heat 3 x per day
-
Warm weather and heat pumps.
2 months ago
-
Oversized Daikin 9kw
2 months ago
-
Daikin COP / energy used measurement from MMI
1 year ago
-
Why does my second unit sometimes start up unexpectedly on a Daikin split system?
1 year ago
-
Legionella cycle: Heat Pump or Immersion Heater?
2 years ago
Currently viewing this topic 2 guests.
- 22 Forums
- 2,084 Topics
- 46 K Posts
- 28 Online
- 3,377 Members
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
@ashp-bobba thank you, and equally so, thank you for ta...
By Mars , 54 minutes ago
-
@judith good to know… I’ll continue to feed Wattson, an...
By Mars , 11 hours ago
-
RE: Vaillant AroTherm Plus 7kW
@jamespa I have a hydronic baseboard heater in the kitc...
By Scalextrix , 17 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
I think that QR code is to download the app SmartHome o...
By cathodeRay , 23 hours ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
@editor great article re accreditation. I note ISO/IEC ...
By Bart , 1 day ago
-
RE: Renewables & Heat Pumps in the News
Here’s a little more technical detail/p>
By Judith , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
I don't (yet), but my PW3 is due to be installed shortl...
By Old_Scientist , 2 days ago
-
RE: MCS and NAPIT complaints process
@chrislay, is your heat pump complaint still unresolved...
By Mars , 2 days ago
-
RE: ASHP Install from hell - help please
@saf1973 I’ve been going through old cases on the forum...
By Mars , 2 days ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron There's the rub, the database does not list my ...
By AF1 , 3 days ago
-
RE: Commencing on an ASHP Installation Process
Yes, it's "doable" if everything goes to plan, they arr...
By Old_Scientist , 4 days ago
-
RE: How not to install a heat pump
You are right. Thinking on this has evolved over the p...
By JamesPa , 5 days ago
-
RE: DHW SET UP with Samsung gen 5
Thats good news indeed, you are very likely almost ther...
By JamesPa , 5 days ago
-
RE: Plate heat exchanger considerations
As far as I can tell my vented system would have a peak...
By Scalextrix , 5 days ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
There have been a few discussions dotted around (e.g. I...
By Declan90 , 5 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having made some enquiries locally I have found a compa...
By Morgan , 5 days ago