High air source heat pump running costs – Vaillant AroTherm Plus
Sounds like it might be setup with a fixed flow temp without weather compensation? Might be best to set up a new thread and post the link here so we can hop on and get into the detail of your install. There will be lots of people who are happy to help you investigate.
Posted by: @murchison2003Hi all
Just read this through this topic and looks like there are alot of yous with the same issue as i have and hopefully someone can help with the high running costs i'm experiencing.
Some basic background information, i have a timber frame kit /block bungalow, heating area 267m2 with underfloor heating, highly insulated, A rating EPC. Replaced a 14 year old ground source pump with a Vaillant Aro Therm 12 kw air source pump approx 3 months ago and haven't touched any settings that the installation team set up. I have tried various timings, on all time / timer etc to try and get this running as efficiently as possible. DHW set at 48 deg on manual to top up when water drops 5 deg. All underfloor manifolds open and inside thermostat set at 21.5 with fallback at 21 deg. I normally run this for 4 hours at night on the cheap tariff to heat the house which retains the heat for about 10 hours then it kicks in for approx 4-5 hours, this is the time it takes to increase the inside temp by .5 to 1 deg.
What i have noticed is this, no matter what the outside temperature is, i've seen it at -3 ranging to + 9 deg, the flow temperature is always 32-38 deg, i haven't seen above 38 deg no matter how long the pump has been running. When heating DHW, i've seen the flow temp up as far as 69 deg which tops up the 300 ltr water tank in about 30 mins. Another thing i've noticed too is that the pump runs at 5 kw/ hr all the time, again no matter how long the pump has been running, it ran for 7 hours solid once, all at 5 kw/hr. Is this correct as i would have thought that when it gets up to temperature it wouldn't take so much energy to sustain that temperature. Am i right or have i got this all wrong? I'm hoping a few setting adjustments will remedy this running costs but not holding out much hope. I am grateful that i have solar and battery storage to compensate for the running of this pump, if not my December bill would have been £980 which is a bit worrying. I appreciate electricity prices have risen dramatically however this pump is running way more expensive than my ground source pump did. My old system used to run at 34 deg and that kept my whole house at 22 deg where now i have cold ceramic floors at this flowrate temperature which i just can't understand.
Any input would be appreciated.
Thanks in advance.
Why didn't you replace the old GSHP with a new GSHP, since they are more efficient?
I would suggest that you read through the manual, particularly the section on weather compensation (WC), and check that your ASHP is set to operate in WC mode, and report back the actual settings of the WC curve.
Derek M
i would have if I could have but due to new regulations, all the house demand now has to come completely from the source. My old pump had an immersion back up whereas now the pumps do not come with such backup. I would have required to double the length of my ground coil which wasn’t viable hence why the air source pump is fitted.
@derek how is your COP looking for DHW when the heating is switched off in April/May? We had our Glycol levels adjusted and would like a comparitor.
Ours is 3.15 for May heating 250l to 47 degrees once per day.
I also noticed the heat pump uses 1kwh every few days for 'heating' even though heating is switched off. Does yours do similar?
Posted by: @webcmg@derek how is your COP looking for DHW when the heating is switched off in April/May? We had our Glycol levels adjusted and would like a comparitor.
Ours is 3.15 for May heating 250l to 47 degrees once per day.
I also noticed the heat pump uses 1kwh every few days for 'heating' even though heating is switched off. Does yours do similar?
We don't have an A2W heat pump we have an A2A one that cannot heat the DHW. At the moment our DHW is provided exclusively by our solar PV system via a power diverter.
-
Installing your own ASHP - DIY
18 hours ago
-
New Installation - Grant Aerona 3 + 210L Hot Water Cylinder
1 week ago
-
Volumiser placement in Vaillant Arotherm + system?
1 month ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
1 month ago
-
ASHP heating issues / error code - advice very much appreciated
2 months ago
- 24 Forums
- 1,413 Topics
- 29.7 K Posts
- 38 Online
- 1,199 Members
Join Us!
Latest Posts
-
RE: Gas Combi to ASHP - Making sense of survey results and proposal.
This has hammered home my understanding of cycling than...
By IRMartini , 2 mins ago
-
RE: Fossil Fuel Fired Heating v Heat Pump?
Another aspect was the DHW heating; the coal fire in th...
By Toodles , 5 mins ago
-
In an ideal world a heat pump unit would contain two co...
By Derek M , 13 hours ago
-
RE: ASHP Advice: High Temperature vs. Low Temperature Heat Pump For Microbore
@jamespa I fully agree with James that a HT heat pump...
By Derek M , 15 hours ago
-
RE: Installing your own ASHP - DIY
@tomasmcguinness Have you been able to perform any sani...
By IanMK13 , 18 hours ago
-
RE: Viessmann Vitocal 250-A in the UK
For reference, I have a 10 kWh Viessmann 151-A installe...
By GC61 , 21 hours ago
-
RE: Vaillant Arotherm Settings for New Installation
@drew-pa Ah thanks. Good to know I dont have a misconce...
By bontwoody , 21 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
On the whole marketing claims vs reality on performance...
By GunboatDiplomat , 21 hours ago
-
RE: Microbore Central Heating Plumbing, will it be a barrier / pain?
@mattc All the existing (designed for T50) radiators ar...
By IanMK13 , 1 day ago
-
The temporary fix has reconnected about 60% of users, a...
By Abernyte , 2 days ago
-
RE: What is Wrong with our Heat Pump Installation?
Having to run the heat pump during the summer for DHW s...
By Toodles , 2 days ago
-
Issues with Vaillant connectivity via the MyCONNECT gateway
I'm sensing a variety of issues with Vaillant connectiv...
By dr_dongle , 2 days ago
-
Interesting heat pumps installations
Thought it would be cool to share photos of interesting...
By Mars , 2 days ago
-
RE: Say hello and introduce yourself
@Toodles That's very interesting to hear, thanks. I ha...
By dr_dongle , 2 days ago
-
RE: Massive Electricity Cost for Running My Air Source Heat Pump
@allyfish In fairness installer has replied stra...
By Holts , 2 days ago
-
-
RE: Are Solar Diverters Necessary for Homes with ASHPs and Solar PV?
@zzxap19 that's a fair point. With the eddi, is it poss...
By Mars , 3 days ago
-
RE: Delivering a smart and secure electricity system: government consultation
"I don't think I'll need to refer to past iterations of...
By eggnchips , 3 days ago
-
RE: Error on Immersun – Error 8 Load Short Circuit
@julesmp8 fingers crossed. I have to say our Immersu...
By Mars , 4 days ago
-
Latest Topics
-
Interesting heat pumps installations
By Mars 2 days ago
-
What is Wrong with our Heat Pump Installation?
By Mars 3 days ago
-
Fossil Fuel Fired Heating v Heat Pump?
By Toodles 3 days ago
-
Viessmann Vitocal 250-A in the UK
By treehugger 4 days ago
-
By HUBB84 7 days ago
-
By jswhite 7 days ago