Help with heat pump sizing
I’m looking to install a heat pump but confused on how to size it and what units work best.
My calculated heat loss is 14kw (8kw fabric and 6kw ventilation based on 0.7 air changes). It’s an Edwardian house that we are refurbishing and extending and will end up around 380sqm. Design temp is -3 based on being in London.
I’ve been looking at mixture of units but I am confused by the heating output figures. Do I look at A7W35? Surely that doesn’t work at design temps of -3 where defrost is likely to bite? Also it seems as though A7W35 doesn’t match the quoted kw rating of the unit. I assume I’m looking at the wrong thing?
The units I’m considering/recommended by installers:
Steibel Eltron WCL AC25 has A7W35 of~8kw
Vailant arotherm 12kw has A7W35 of~8kw
Samsung EHS 16kw has A7W35 16
Grant Arona 15.5kw A7W35 16.6kw
Would appreciate a bit of help - thanks!
Posted by: @aminI’m looking to install a heat pump but confused on how to size it and what units work best.
My calculated heat loss is 14kw (8kw fabric and 6kw ventilation based on 0.7 air changes). It’s an Edwardian house that we are refurbishing and extending and will end up around 380sqm. Design temp is -3 based on being in London.
I’ve been looking at mixture of units but I am confused by the heating output figures. Do I look at A7W35? Surely that doesn’t work at design temps of -3 where defrost is likely to bite? Also it seems as though A7W35 doesn’t match the quoted kw rating of the unit. I assume I’m looking at the wrong thing?
The units I’m considering/recommended by installers:
Steibel Eltron WCL AC25 has A7W35 of~8kw
Vailant arotherm 12kw has A7W35 of~8kw
Samsung EHS 16kw has A7W35 16
Grant Arona 15.5kw A7W35 16.6kwWould appreciate a bit of help - thanks!
Unfortunately you will almost certainly need to go a layer deeper and look at the detailed specs (which are not always easy to find) to work out what the heat pump will do at your design flow temp and design air temp. Some of your figures are odd though eg Vaillant Arotherm 12kw has A7W35 of~8kw is incorrect see attached (but beware that Vaillant are allegedly not good at accounting for defrost so you may have to derate a bit around OAT0, particularly in the parts of London where its damp.
Sorry but there is no short circuit to this other than relying on the installer. Personally in your situation I would do the latter to give you cover, but check their workings
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
For the Vailant I’ve been looking at the values from pg49 of the operation manual attached and the page here
This seems different to the table in the doc you shared so I assume each is measuring something different?
I’m okay to rely on an installer but I also want to be able to verify and making sure I get something up to the task.
I dont think materially relative to this (I assume 'nominal' means the output at which they measure all the other various parameters)
But I agree its different to the page here, although the latter does also say 12.2kW at A-7W35. Not sure what the figures for A7/W35 or A2W35 are meant to signify, its the first time I had seen this table (Vaillant do keep changing exactly what they publish!). I cant see how they could possibly be max outputs because thats not how the thermodynamics works. Maybe they are trying to give representative figures for COP. A 12kW heat pump sized for -2C wont be running at anything like 12kW when its 7C, roughly half is about right but it sure is confusing. That however wouldnt explain the numbers at +2. Perhaps they are coming clean about the effects of deftost.
If you find out perhaps you could post here the answer, Im tempted to ask Vaillant myself!
PS I was tempted and I have. There is also a planning guide here
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,342 Topics
- 53 K Posts
- 327 Online
- 6,000 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Commencing on an ASHP Installation Process
I've got a bit of time to draft something today, so the...
By Sheriff Fatman , 45 minutes ago
-
RE: Setback savings - fact or fiction?
The predicted values are based on assumptions and it is...
By RobS , 1 hour ago
-
RE: Help with heat pump sizing
@amin I dont think materially relative to t...
By JamesPa , 3 hours ago
-
Totally agree. The problem lies with what I was once ...
By Majordennisbloodnok , 3 hours ago
-
@majordennisbloodnok I have decided to take the plunge....
By TechnoGeek , 4 hours ago
-
RE: LiFePO4 lithium battery fires and explosions
I too had spotted the Na-ion battery and matching inver...
By Transparent , 5 hours ago
-
RE: Poll for Time of Use, tariffs, technology
You are absolutely right. I think another common fac...
By JamesPa , 8 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
Let' start with first thing first, HG is a startup, the...
By ksim , 9 hours ago
-
RE: Configuring third party dongle for Ecodan local control
@sheriff-fatman might be interested in this, f...
By F1p , 10 hours ago
-
RE: Different dT on each radiator?
I cant sorry. Its based on some calculations I did fro...
By JamesPa , 22 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@simonf thats interesting as I’ve noticed my flow and r...
By AdamK , 1 day ago
-
RE: MELcloud scheduling misbehaviour
No, it gets to set temperature easily even during perio...
By Abernyte , 1 day ago
-
RE: Free Ecoheat Heat Pump Install
Sorry hit 'add reply' too early, this forum layout will...
By Deltona , 1 day ago
-
And arguably even more important, sodium will be hopefu...
By Batpred , 2 days ago
-
RE: A Smarter Smart Controller from Homely?
I've been thinking of emailing Homely to ask for a few ...
By JohnnyB , 2 days ago
-
Max output of Heat pump (Daikin 4Kw EDLA04)
Hello, I am a bit puzzled that according to pcdb tes...
By GeorgeA , 2 days ago
-
RE: Has Anyone Else Noticed a Decline in Tradesmanship?
@cathoderay Hence my rider about ‘all else being equal’...
By Toodles , 2 days ago
-
RE: Heat Pump Performance Analysis Web App using Modbus Data
@redzer_irl — all my heat pump data is in csv files, me...
By cathodeRay , 2 days ago