Posted by: @s_gatoratorHi @cathodeRay , aren't all of the cycles in your chart defrost cycles? The clue I'm seeing is in the OAT graph, which has a small spike just after the compressor stops, presumably due to your outside temperature sensor being near the external unit and it getting some heat from the warm air at the end of the defrost cycle when the fan restarts. I have the same think on ours.
Of the charts that I posted on 17/01/2025 at 8:46 am, the first two are normal cycling, the second two are defrost cycles. The way I identify defrost cycles is the LWT falls below the RWT.
The OAT spikes are indeed down to the sensor being, in my (Midea) case, inside the main case, meaning it is really the AIT (air intake temperature) rather than the true OAT. In normal cycling, when running, the unit exhausts cooler air, which lowers the OAT/AIT, when it is off the OAT/AIT recovers a bit with a small spike visible. In defrost cycles, this spike is more marked as the unit, as you say, exhausts warmer air. We've had quite a lot of discussion about the problems of using AIT rather than OAT on other threads, because of course it is the OAT which is actually the IAT that the weather compensation curve uses. The OAT being actually the AIT also complicates assessments of heat loss, because the rest of the house is sitting in the true OAT rather than the AIT, and finally, the local slightly cooler air around the heat pump has at least some detrimental effect on performance. My heat pump by the way isn't in a so called cold well, but it is 1ft in front of a wall, and inevitably some of the air drawn in at the rear comes from the cooler air in front of the unit. Some heat pump brands do have true OAT sensors, placed away from the unit, but many don't.
If the temperatures are lower, as in Europe, the moisture freezes out of the air and it looks like frosting does not occur below -7C or above 5C (quick internet search). Otherwise, here, I agree, it's a problem.
This is indeed what one hears. One wonders whether there is a sort of tinkling of breaking ice as the moisture drops out of the air at -7 degrees. More seriously, -7 to +5 degrees is really quite a large range, there must be places in Europe where the OAT is within that range for some if not much of the time. I wonder what happens there?
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayOf the charts that I posted on 17/01/2025 at 8:46 am, the first two are normal cycling, the second two are defrost cycles. The way I identify defrost cycles is the LWT falls below the RWT.
Ah! OK, that's interesting, thanks @cathodeRay, I stand corrected. NIBE have a separate OAT sensor. I now know about Air Intake temperature sensors!
Another way I can see defrost cycles is the evaporator temperature, which goes positive.
Posted by: @cathoderayMore seriously, -7 to +5 degrees is really quite a large range, there must be places in Europe where the OAT is within that range for some if not much of the time. I wonder what happens there?
That's a very good question. I wonder if anyone on the forum has an idea, an interested contact, or experience of living the ASHP in such temperatures
End 1980's terrace in Southern England
NIBE 12kW air source heat pump
2 solar water panels
1 x Ohme ePod
1 x VW ID Buzz
Posted by: @s_gatoratorI now know about Air Intake temperature sensors!
That is indeed what they are, though Midea calls readings from it the Outdoor ambient temperature. As ambient is in practice rather vague (does it mean immediate surroundings, or just surroundings? And surrounding what? The heat pump? The building?), and on top of that given ambient temperature is often used interchangeably with outside air temperature, there is a recipe for confusion. As a result, someone on this forum, maybe @jamespa, used the unambiguous term Air Intake Temperature to name the variable.
Posted by: @s_gatoratorI wonder if anyone on the forum has an idea, an interested contact, or experience of living the ASHP in such temperatures
I echo this!
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @s_gatoratorI wonder if anyone on the forum has an idea, an interested contact, or experience of living the ASHP in such temperatures
We need to be on the lookout for a person with a name that sounds vaguely Eastern European or Scandinavian.
@editor might know someone.
Save energy... recycle electrons!
@transparent I'm actually working on a podcast episode along these lines and will start looking for homeowners in the next couple of weeks with surnames ending in "wicz" and "ski" 🤣
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Great! 😆
I'd also been keen to attract here some people who might later play a part in rebuilding Ukraine.
There's a lot of content on the Forum which would allow them to provide heat and light in locations which may only have intermittent power for years to come.
They don't need to replicate the energy supply system as it was before,
nor in the style we have here in UK.
It would a lot cheaper/quicker to create community clusters which can use multiple sources of energy when they are available, including micro-hydro which is more abundant in winter.
That would provide them with systems that are more resilient to outages.
Save energy... recycle electrons!
Vaillant's comment about de-icing is:
It is hard to say how often a de-icing cycle will take place as it depends on several things…
• The humidity of the air
• The amount of energy being taken out
• The period of time the energy is being taken.
The de-icing cycle will happen more often when the outside air temperature is around 2.5°C but will happen less often when the air temperature is below 0°C, as there is less water in the air.
From page 4 of
Posted by: @johnrbut will happen less often when the air temperature is below 0°C, as there is less water in the air.
Of course, that should be a key thing, warmer air can hold more water than cooler air. But in practice my heat pump seems to do much the same defrost activity (duration and frequency) at -4 degrees (0600-0900) as it does at 0 degrees (1800-0000):
Do any Vaillant owners have similar charts for their heat pumps?
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay Ditto my Grant ASHP, During last week's cold spell it spent much of each day frosting then clearing, even down to -6C which was the lowest temperature we reached in West Oxfordshire. But then I know my overall installation was done far from optimally in terms of the kWh used at any OAT.
Mike
Grant Aerona HPID10 10kWh ASHP
@cathoderay & @transparent I have attempted to measure start up current spikes but don’t have high speed monitor devices. The monitor on our battery system monitors at once per 5mins which isn’t a fast rise but that’s not an adequate resolution. The octopus mini samples at one per min and shows a steady rise, so for me there is no fast switch on issue.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
@judith - thanks. Can you get leaving and returning water temperature at one minute intervals? That would let us see frequency and duration of defrosts on a Vaillant if you can get a chart covering a defrost period.
Midea 14kW (for now...) ASHP heating both building and DHW
-
Surface mount or bury primaries for heat pump installation?
1 month ago
-
UFH and ASHPs
3 months ago
-
Installing your own ASHP - DIY
4 months ago
-
ASHP install contract and BUS grant money
5 months ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
6 months ago
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 35 Online
- 5,655 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: ASHP heat output monitoring
@tim441 Thanks, PM received and appreciated, I can't ev...
By Carlo , 7 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
I am keen to see how this unfolds and changes the lands...
By ASHP-BOBBA , 9 hours ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 13 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist I have never cleaned the mag filter myse...
By Toodles , 13 hours ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 13 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 13 hours ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 13 hours ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 2 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 3 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 3 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 3 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@sandy, I'll send Vaillant an email tomorrow and see if...
By Mars , 4 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 4 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 5 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 7 days ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 7 days ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 1 week ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 1 week ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@dgclimatecontrol I don't know, but they were not happy...
By DavidAlgarve , 1 week ago