Heat Pump sizing - Further adventures of a boiler owner
A couple of weeks ago I posted a graph of the gas consumption of my boiler versus heating degree day (HDD) that I created over eighteen months ago (here). Since I’ve learned quite a bit in the period since I originally created the graph, I decided to repeat the process for intervening years. I changed my approach this time, creating a separate plot covering the whole of each heating season rather than for a calendar year. I used weather data from my weather station to calculate local HDD data using the method detailed at degreeday.net using a base temperature of 15.5°C as derived by degreeday.net’s regression tool (which use my local airport’s HDD data). To validate my newly-calculated data and methods, I repeated my earlier plot. The trend lines were almost identical - y=12.784x+13.485 and R2=0.9237 this time against y=12.822x+13.658 and R2=0.9236 previously. My other new plots are as follows
It can be seen that 2021-22 was a relatively mild winter with the daily average temperature barely clipping 0°C on a couple of occasions. This was not the case in 2022-23; the second week of December and the third week of January being particularly cold (several degrees below zero). 2023-24 also had its share of cold days, although not quite as bad as the previous year. The boiler struggled this year as I had downrated the boiler and reduced the flow temperature at the beginning of the heating season. I was also playing with pump speeds and monitoring flow temperatures but was unable to come to any conclusions; I suspect the TRVs were affecting the situation. I also experimented with having no overnight setbacks last year.
My interpretation of the plots and trendline equations:
- It looks like I may have turned-down my DHW thermostat in 2022.
- There was quite a cold spell when I was away on holiday in October last year (Heating and DHW turned off). On checking, daily average temperatures dipped into single figures during my time away.
- It’s not clear that my experiments at turning-down the boiler have been successful in monetary terms. Comparing the trendlines for 2021-22 and 2023-24 (cf y=mx + c), m is greater for the later year but I don’t believe it is fully offset by the reduced value of c.
- It appears as though I need a 10-11kW heat source - but only for 2-3 weeks per year. A 7kW source would suffice at other times
Bearing in mind the disadvantages of a 10-1kW ASHP (in particular, the size), are there other viable options that merit consideration? Two smaller ASHPs? A gas hybrid heating system? How would radiator requirements be determined for a hybrid system?
I have seen suggestions of using auxiliary electric heaters when it is only a matter of perhaps 10 - 15 days during a full winter season. Might this cover your needs?
Thanks to failures of British Gas to orchestrate prompt repairs when we were still heating with gas, we have two very compact 1 or 2 kW fan heaters plus a convection heater we bought years back. These all stand by in readiness for such occasions - though the Daikin 8 kW keeps us cosy at -7 or -8 degrees as we experienced last Nov/Dec for a few days. Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@ianmk13 Perhaps have a word with @davidalgarve 😉 Perhaps he could put you up! Though I should avoid Valencia area at the moment - they seem to have some flow problems.Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@toodles Are you going into competition with Booking.com? What are your commission rates?
I am rather occupied at the moment, with a big Birthday, a hip replacement operation and a cataract operation due. Otherwise OK!
@davidalgarve I’ve done several ‘big birthdays’ had cataract surgery (and much more too!) but still have my original hips! My commission rates are (behind hand in front of mouth - mumble mumble.)😉 Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Posted by: @toodlesI have seen suggestions of using auxiliary electric heaters when it is only a matter of perhaps 10 - 15 days during a full winter season. Might this cover your needs?
There is sometimes quite a good argument for this and many heat pumps do have the capability to drive electric heaters inline. Check actual specs at design temp & FT, eg Vaillant 7kW is actually 8.6 at -2 and 45, but quite a few heat pumps only give their rated output at a rather restricted range of conditions.
That said the Mitsi 11.2kW R32 unit (and the R290 when they release it doubtless) or the Samsung 12kW unit arent much bigger than eg a Vaillant 7kW so consider these (or other manufacturers ) if they fit in space/noise envelope. Ideal also do single fan higher capacity pumps, sourced I think from Midea (the R290 ones anyway).
Remember the BUS requires that the unit can cover the entire heat load, but it seems that 'the unit' includes (at least according to the interpretation of some installers) any linked backup heater.
Finally how are you estimating your boiler efficiency. It could be more than 100% (up to 110%) if its actually condensing (most don't because FT is set too high) or 75% if its very old. This makes quite a difference to the conclusion.
2xheat pumps is of course possible, but you wont get it in under permitted development and it will cost a lot in ancillary kit which installers will want to put in, and there will be installers that wont touch it. Personally I wouldn't go there at 10-12kW, there are some perfectly good reasonably sized (ie single fan) solutions in this range.
Put these into the mix and you should be able to find a comfort spot. Feel free to ask more particularly as you move towards a conclusion. Then of course you have to persuade an installer to take notice of real measurements, which many wont (but some will).
As a word of warning - there are those (perhaps the majority if you include installers) who dismiss the 'what does my boiler use' method due to the uncertainties in boiler efficiency and how the boiler is used. MCS only formally recognises the fabric spreadsheet (although I do somewhere have an email from MCS recognising that it has limitations for retrofits). So you are a bit out on a limb relying on boiler measurements. That said its what I am doing for my install (which, following 2 years of hassle with planning, is now hopefully going to happen in the next couple of months).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
-
Surface mount or bury primaries for heat pump installation?
1 month ago
-
Air Changes per Hour - ACH and the MCS requirement
2 months ago
-
UFH and ASHPs
3 months ago
-
Installing your own ASHP - DIY
4 months ago
-
ASHP install contract and BUS grant money
5 months ago
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 10 Online
- 5,655 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: ASHP heat output monitoring
@tim441 Thanks, PM received and appreciated, I can't ev...
By Carlo , 3 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
I am keen to see how this unfolds and changes the lands...
By ASHP-BOBBA , 5 hours ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 8 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist I have never cleaned the mag filter myse...
By Toodles , 9 hours ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 9 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 9 hours ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 9 hours ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 2 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 2 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 3 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 3 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 3 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@sandy, I'll send Vaillant an email tomorrow and see if...
By Mars , 4 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 4 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 4 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 6 days ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 7 days ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 1 week ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 1 week ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@dgclimatecontrol I don't know, but they were not happy...
By DavidAlgarve , 1 week ago