Heat Pump, DHW, UFH and Radiator Install
Ive just been over to help a friend with her ASHP which was tripping the consumer unit. Im pretty sure the problem is a leak which has shorted the pump. However the real issue is what she said to me was happening with the heating.
She informed me that the cylinder was heated every day to 50+C but that the same temperature water was being pumped around her UFH. When the room thermostat hit 20C the heat pump turned off. The upstairs radiators do not get hot.
I was gobsmacked but Im not a plumber so took her at her word and also took a picture of her setup.
Im not altogether sure how a system like this should be plumbed. It seems to me the optimum solution requires water at 3 different temperatures. Is the usual solution to heat the DHW as usual, but then use a lower temp for the radiators and perhaps use a mixing valve to lower the temperature again for the UFH?
Thanks in advance
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Could it be that the valve has stuck open so that the higher temperature water intended for the DHW circuit is also flowing through the UFH manifold? Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@toodles I suppose anything is possible. I wish I had took a better photo of the cylinder so I could perhaps look it up and see its connections. Perhaps its a thermal store? The UFH and Rad circuits each seem to have one two-way valve
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody My eyesight is not good enough to follow the pipework to those two valves so I cannot tell which from what however… another thing I cannot see is any insulation - I think most of those pipes need lagging! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@bontwoody I can see 3 motorized valves but cant quite work out how one of them (which is on the pipework to the cylinder) is connected. I also dont know how it is controlled although it looks like its linked directly to the cylinder stat.
Posted by: @bontwoodyIm not altogether sure how a system like this should be plumbed. It seems to me the optimum solution requires water at 3 different temperatures. Is the usual solution to heat the DHW as usual, but then use a lower temp for the radiators and perhaps use a mixing valve to lower the temperature again for the UFH?
yes, exactly that.
But maybe the plumber has 'designed' the whole system to operate at a single FT of 50C without weather compensation, in which case it could be operated just like a boiler, with (or even without) mix-down for the UFH. What I presume to be the feed to the rads also appears to feed the UFH manifold directly. Stupid but possible and if there is no mix-down for the UFH risk of burned feet or spoiled floor covering.
Posted by: @jamespa@bontwoody I can see 3 motorized valves but cant quite work out how one of them (which is on the pipework to the cylinder) is connected. I also dont know how it is controlled although it looks like its linked directly to the cylinder stat.
Posted by: @bontwoodyIm not altogether sure how a system like this should be plumbed. It seems to me the optimum solution requires water at 3 different temperatures. Is the usual solution to heat the DHW as usual, but then use a lower temp for the radiators and perhaps use a mixing valve to lower the temperature again for the UFH?
yes, exactly that.
But maybe the plumber has 'designed' the whole system to operate at a single FT of 50C without weather compensation, in which case it could be operated just like a boiler, with (or even without) mix-down for the UFH. What I presume to be the feed to the rads also appears to feed the UFH manifold directly. Stupid but possible and if there is no mix-down for the UFH risk of burned feet or spoiled floor covering.
Looking again I think the slightly hidden motorized valve has 3 ports, one directing water to the middle of the cylinder the other to the bottom. The flow to the CH and UFH (which does appear to be common without mixing) appears to come from the bottom. So perhaps this is a combined cylinder/butter tank, with the buffer tank below and the cylinder above. The bottom bit has an immersion, which may just be a backup.
Does that help?
@toodles LOL, I did point that out to her 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@jamespa Its a lot more than I had managed to work out James, so thanks yes. Ive offered to switch the pump for her as a belated wedding present, so when I go back I will take some more extensive pictures and trace some pipes. She said she was spending £180 per month on electricity bills so Im hoping that can be reduced substantially.
The heat pump looks on the big size for the house, but was also tipped forwards about 15 degrees so Ive done my best to level it as a temporary measure. Long term its position will be changed.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@jamespa I think you are spot on about the integrated buffer vessel, she has sent me her documentation. It was designed for a 50C flow temperature with UFH! There is no thermostatic mixer valve on it.
Im going to try and find out how to access the control unit and see whats going on once I change the pump. It a modern one similar to the Samsung unit from the outside.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
So I have changed the pump (all working again) and had a better look around. There appear to be 2 x two way valves one on the upstairs rads and the other on the downstairs UFH.
There is a 3 way valve switching between heating and DHW as normal. Ive been into the installer settings to have a look but need some advice on the LG way of doing things so I will start a new thread.
Thanks for all your help.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody You are most welcome - not that I contributed much, but if it helped, I’m happy! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
That doesn't look like a thermal store to me.
I think it's a combined DHW cylinder (top) and 50-litre buffer tank (below).
Have a look at this diagram from the manufacturer's product literature.
At least that graphic has the ports labelled, which gives you a fighting chance of working out what each pipe is meant to do.
Save energy... recycle electrons!
-
Mitsubishi EcoDan ASHP Settings not saving.
4 days ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
2 weeks ago
-
Heat Pump sizing - Further adventures of a boiler owner
1 month ago
-
If the supplier won't commission my Heliotherm heat pump what should I do next?
2 months ago
-
Simulation of ASHP with Gas boiler as part of decision process
2 months ago
- 21 Forums
- 1,741 Topics
- 37.2 K Posts
- 60 Online
- 2,033 Members
Join Us!
Latest Posts
-
@raiph I apologise for my incorrect assumption. A PWM p...
By Mike H , 45 minutes ago
-
RE: New Samsung 12KW Heat Pump Help
@mike-h so 2091/2092 were set to 'Use(Signal only ON/OF...
By dinhp , 51 minutes ago
-
RE: Baffled by heat pump size/ choice!
another is to fit waste water heat recovery
By JamesPa , 1 hour ago
-
RE: Should We Rethink the Name “Heat Pump” for Homeowners?
Not sure you need the "re". Caleferator sounds fine to...
By downfield , 2 hours ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
Thanks for this Mars. I've actually found out the issue...
By dnagre , 22 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@transparent it doesn't sound good 🤔
By Andris , 23 hours ago
-
RE: 6 Red Flags to Avoid When Considering a Heat Pump Installation
The ASHP, just like a boiler, can supply water at only ...
By JamesPa , 1 day ago
-
RE: Excessive performance/system issues with GSHP
Is the buffer tank in the house? If so, any heat loss s...
By JohnR , 1 day ago
-
RE: The good, the bad and the not that great – my heat pump installation
@transparent - here's the page with more details and im...
By cathodeRay , 1 day ago
-
RE: Vaillant ASHP Weather Compensation with Octopus Cosy
In the Vaillant app go to Settings (the cog wheel icon)...
By JohnR , 2 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Thanks for your reply. I love Octopus Energy and are a ...
By Trevor , 2 days ago
-
RE: Watch Where Your Installer Fits Motorised Valves
The 2000W Karcher will be out shortly!
By Mars , 2 days ago
-
We had a Daikin 8kW ASHP installed two weeks ago. We h...
By R0y124 , 2 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
I did not have the time to check the thermistors Yester...
By ThunderMink , 3 days ago
-
Evening all. Thanks for the replies. Great info....
By TheHolyHeatPump , 3 days ago
-
RE: Incorrect Billing of Customers with a Smart Meter
It would be nice if there being lower existing demand o...
By Transparent , 3 days ago
-
RE: Mitsubishi Ecodon stuck on immersion symbol
This how my system is running : Top graph is the am...
By ak2024 , 3 days ago
-
RE: Ecodan help - flow temperature spikes when operating in weather compensation mode
@eleusis it can do it but not in 4 hours, you will need...
By Gary , 3 days ago
-
RE: Most treasured kitchen gadget.
@toodles With the machine its as many as I want or s...
By IRMartini , 3 days ago
-
RE: Mitsubishi Ecodan ASHP general set-up and efficiency
@gary The heating bill often looks like we live in a ma...
By ngillam , 3 days ago
Latest Topics
-
Baffled by heat pump size/ choice!
By zuluwarrior 1 day ago
-
Vaillant ASHP Weather Compensation with Octopus Cosy
By tom58l 2 days ago
-
By R0y124 2 days ago
-
Mitsubishi Ecodan 11kw Defrosting Issue.
By ThunderMink 3 days ago
-
By TheHolyHeatPump 4 days ago
-
Flow temperature- At what point?
By Westkent 4 days ago
-
Excessive performance/system issues with GSHP
By didjerama_uk 4 days ago
-
Thermostat setting...still learning
By Profzarkov 4 days ago
-
Watch Where Your Installer Fits Motorised Valves
By Mars 5 days ago
-
Mitsubishi EcoDan ASHP Settings not saving.
By Fez96 5 days ago