Heat Pump, DHW, UFH and Radiator Install
Ive just been over to help a friend with her ASHP which was tripping the consumer unit. Im pretty sure the problem is a leak which has shorted the pump. However the real issue is what she said to me was happening with the heating.
She informed me that the cylinder was heated every day to 50+C but that the same temperature water was being pumped around her UFH. When the room thermostat hit 20C the heat pump turned off. The upstairs radiators do not get hot.
I was gobsmacked but Im not a plumber so took her at her word and also took a picture of her setup.
Im not altogether sure how a system like this should be plumbed. It seems to me the optimum solution requires water at 3 different temperatures. Is the usual solution to heat the DHW as usual, but then use a lower temp for the radiators and perhaps use a mixing valve to lower the temperature again for the UFH?
Thanks in advance
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Could it be that the valve has stuck open so that the higher temperature water intended for the DHW circuit is also flowing through the UFH manifold? Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@toodles I suppose anything is possible. I wish I had took a better photo of the cylinder so I could perhaps look it up and see its connections. Perhaps its a thermal store? The UFH and Rad circuits each seem to have one two-way valve
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody My eyesight is not good enough to follow the pipework to those two valves so I cannot tell which from what however… another thing I cannot see is any insulation - I think most of those pipes need lagging! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@bontwoody I can see 3 motorized valves but cant quite work out how one of them (which is on the pipework to the cylinder) is connected. I also dont know how it is controlled although it looks like its linked directly to the cylinder stat.
Posted by: @bontwoodyIm not altogether sure how a system like this should be plumbed. It seems to me the optimum solution requires water at 3 different temperatures. Is the usual solution to heat the DHW as usual, but then use a lower temp for the radiators and perhaps use a mixing valve to lower the temperature again for the UFH?
yes, exactly that.
But maybe the plumber has 'designed' the whole system to operate at a single FT of 50C without weather compensation, in which case it could be operated just like a boiler, with (or even without) mix-down for the UFH. What I presume to be the feed to the rads also appears to feed the UFH manifold directly. Stupid but possible and if there is no mix-down for the UFH risk of burned feet or spoiled floor covering.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespa@bontwoody I can see 3 motorized valves but cant quite work out how one of them (which is on the pipework to the cylinder) is connected. I also dont know how it is controlled although it looks like its linked directly to the cylinder stat.
Posted by: @bontwoodyIm not altogether sure how a system like this should be plumbed. It seems to me the optimum solution requires water at 3 different temperatures. Is the usual solution to heat the DHW as usual, but then use a lower temp for the radiators and perhaps use a mixing valve to lower the temperature again for the UFH?
yes, exactly that.
But maybe the plumber has 'designed' the whole system to operate at a single FT of 50C without weather compensation, in which case it could be operated just like a boiler, with (or even without) mix-down for the UFH. What I presume to be the feed to the rads also appears to feed the UFH manifold directly. Stupid but possible and if there is no mix-down for the UFH risk of burned feet or spoiled floor covering.
Looking again I think the slightly hidden motorized valve has 3 ports, one directing water to the middle of the cylinder the other to the bottom. The flow to the CH and UFH (which does appear to be common without mixing) appears to come from the bottom. So perhaps this is a combined cylinder/butter tank, with the buffer tank below and the cylinder above. The bottom bit has an immersion, which may just be a backup.
Does that help?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@toodles LOL, I did point that out to her 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@jamespa Its a lot more than I had managed to work out James, so thanks yes. Ive offered to switch the pump for her as a belated wedding present, so when I go back I will take some more extensive pictures and trace some pipes. She said she was spending £180 per month on electricity bills so Im hoping that can be reduced substantially.
The heat pump looks on the big size for the house, but was also tipped forwards about 15 degrees so Ive done my best to level it as a temporary measure. Long term its position will be changed.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@jamespa I think you are spot on about the integrated buffer vessel, she has sent me her documentation. It was designed for a 50C flow temperature with UFH! There is no thermostatic mixer valve on it.
Im going to try and find out how to access the control unit and see whats going on once I change the pump. It a modern one similar to the Samsung unit from the outside.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
So I have changed the pump (all working again) and had a better look around. There appear to be 2 x two way valves one on the upstairs rads and the other on the downstairs UFH.
There is a 3 way valve switching between heating and DHW as normal. Ive been into the installer settings to have a look but need some advice on the LG way of doing things so I will start a new thread.
Thanks for all your help.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody You are most welcome - not that I contributed much, but if it helped, I’m happy! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
That doesn't look like a thermal store to me.
I think it's a combined DHW cylinder (top) and 50-litre buffer tank (below).
Have a look at this diagram from the manufacturer's product literature.
At least that graphic has the ports labelled, which gives you a fighting chance of working out what each pipe is meant to do.
Save energy... recycle electrons!
-
ASHP install contract and BUS grant money
6 days ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
1 week ago
-
Savings - using Weather Compensation & Time of Use Tariffs
2 weeks ago
-
Heat Pump starting current
1 month ago
-
Running my new Nibe ASHP efficiently
1 month ago
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 66 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Setback savings - fact or fiction?
And here in case any one wants it is the code I used in...
By cathodeRay , 2 minutes ago
-
RE: What is the best strategy for operating a very oversized heat pump?
@jamespa Samsung has it 'Quiet mode' and I use it a ...
By IRMartini , 6 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
No need for apologies, just cautioning about getting to...
By JamesPa , 19 minutes ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 21 minutes ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 2 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 4 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 6 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 7 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 18 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 21 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 22 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 6 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 7 hours ago
-
SolarPV tables / online calculator
By MichelleC 14 hours ago
-
By Toodles 2 days ago