Posted by: @scrchngwslPosted by: @william1066
in theory, the emitters won't be emitting any more heat, and the heat pump won't be using any more power.
The above is not entirely correct, since an increase in LWT will actually cause the heat emitters to 'emit' more heat energy.
Consider the following:-
If the outside air temperature is 10C, with the indoor air temperature at 20C, a fixed LWT of 35C and a water flow rate of 15 litres per minute.
The outside air temperature falls to 5C, which increases the heat loss of the building, since the DeltaT between inside and outside is now 15C. The inner fabric of the building starts to cool, which in turn has a cooling effect upon the air within the rooms. As the cooler air circulates around the rooms it comes into contact with the heat emitters, and creates an increased DeltaT between the room air and the outer surface of the heat emitters, and hence has a cooling effect. The fall in temperature at the outer surface of the heat emitters is reflected at the inner surface, which in turn has a cooling effect upon the water flowing through the heat emitters.
Because the LWT and the water flow rate are in this case being held constant, the heat energy produced by the heat pump will initially still be the same. The heat emitters, on the other hand, are absorbing more heat energy from the water, which has the net effect of causing the RWT to reduce slightly. This slight reduction in RWT will increase the DeltaT between LWT and RWT, causing the heat energy output of the heat pump to increase slightly.
Without any further changes in operating parameters, the system should achieve equilibrium with a reduced indoor temperature of say 19C or even 18C.
To keep the indoor temperature more constant during the above scenario, most heat pump controllers sense the increase in DeltaT between LWT and RWT, and have the capability to increase the water flow rate by increasing the water pump speed. Although the LWT remains constant, the increase in water flow rate transfers more heat energy from the heat pump to the heat emitters, thereby supplying the additional heat loss of the building.
If the heat pump is operating in WC mode during the above scenario, the falling outside air temperature would automatically cause an increase in the required LWT produced by the heat pump. Any change to the specified DeltaT between LWT and RWT being corrected by varying the water pump speed.
A correctly optimised heat pump controller should therefore be capable of keeping indoor temperatures reasonably constant under normal operating conditions.
@derek-m Exactly, I had this formula for UFH, though not sure it is correct but seems to give results in a reasonable ball park. In any case the results illustrate your point.
G7 is room and H7 floor temp
@william1066 I think the bellimo valves that @heacol recommends are back in stock at JTM, I'm tempted to grab one for my build before he gets them all again 😉
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@heacol so if I'm going to replumb in a couple of weeks will you be selling by that point, or just get a bellimo from JTM?
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @william1066That is my current choice for replacement of existing one. At 45 lpm is 1 mh2o.
-- Attachment is not available --
doing some component research over the weekend. spirotech 1 1/4 "
https://www.spirotech.co.uk/products/spirotrap/spirotrap-mb3mbl--brass--magnet--uni-118/?variant=948
pressure loss spec took some hunting down but its 2.2kpa (0.22 mh2o) at 3.6m3/h, which is way better than the typical 28mm ones that are sold.
pricings not too bad, available in the usual places. There's even a 1 1/2" one if you wanted even more headroom.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank You need the chart, because given a big enough pump you can probably get a pretty high flow rate. I would ideally like less than .5 mh20 lost through a filter.
Posted by: @iancalderbankpressure loss spec took some hunting down but its 2.2kpa (0.22 mh2o) at 3.6m3/h, which is way better than the typical 28mm ones that are sold.
This is definitely acceptable, do you have a link to the pressure loss chart?
@william1066 3.6m3/h with a DP of 0.22mh20 means its not relying on a monster pump. the chart is here
I was comparing to some of the usual suspect 28mm versions on offer (including the spirotech one) its a substantial difference.
there's also a a caleffi one https://buyplumbingonline.co.uk/altecnic-dirtmag-brass-dirt-separator-1-1-4-546307-caleffi.html
DP is better again, down to 0.5kpa = 50mm h20 , at 60l/m for the 1 1/4"
spec sheet
I'm about to order one.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Thanks for that. I quite like the ESBE diverters, but can't seem to get the one I need here in UK. Also trying to connect 28mm to 1 1/4 will be a pain. I am not a plumber by trade, just a diy plumber, and like the simpler options 😀
@william1066 I'm exactly same as you. keen DIYer' . I'd prefer it if the filters came with 28mm connections, but those are all too small bore inside. I don't want to go with just a strainer. 28 comp to 1 1/4" is simple. https://www.monsterplumb.co.uk/compression-male-straight-coupling-28mm-x-1-1-4
diverter there is the the bellimo R3025-S2-LR230A that @heacol recommends (unless he gets his new ones imminently) I'm intending to do that part of the plumbing v soon. anything particular for the ESBE versus that one?
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 385 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
@batpred I reckon Andy might know a thing or 2 about...
By Bash , 3 minutes ago
-
RE: What determines the SOC of a battery?
@batpred Ironically you didn't have anything good to...
By Bash , 60 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Here’s a current graph showing a bit more info. The set...
By benson , 1 hour ago
-
RE: Setback savings - fact or fiction?
True there is a variation but importantly it's understa...
By RobS , 1 hour ago
-
Below is a better quality image. Does that contain all ...
By trebor12345 , 2 hours ago
-
Sorry to bounce your thread. To put to bed some concern...
By L8Again , 2 hours ago
-
@painter26 — they (the analogue gauges) are subtly diff...
By cathodeRay , 2 hours ago
-
RE: Electricity price predictions
I am always impressed with how you keep abreast of so m...
By Batpred , 3 hours ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
@majordennisbloodnok I’m glad I posted this. There see...
By AndrewJ , 3 hours ago
-
Our Experience installing a heat pump into a Grade 2 Listed stone house
First want to thank everybody who has contributed to th...
By Travellingwave , 6 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 9 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 10 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 1 day ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 1 day ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 1 day ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 1 day ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago