Posted by: @scrchngwslPosted by: @william1066
in theory, the emitters won't be emitting any more heat, and the heat pump won't be using any more power.
The above is not entirely correct, since an increase in LWT will actually cause the heat emitters to 'emit' more heat energy.
Consider the following:-
If the outside air temperature is 10C, with the indoor air temperature at 20C, a fixed LWT of 35C and a water flow rate of 15 litres per minute.
The outside air temperature falls to 5C, which increases the heat loss of the building, since the DeltaT between inside and outside is now 15C. The inner fabric of the building starts to cool, which in turn has a cooling effect upon the air within the rooms. As the cooler air circulates around the rooms it comes into contact with the heat emitters, and creates an increased DeltaT between the room air and the outer surface of the heat emitters, and hence has a cooling effect. The fall in temperature at the outer surface of the heat emitters is reflected at the inner surface, which in turn has a cooling effect upon the water flowing through the heat emitters.
Because the LWT and the water flow rate are in this case being held constant, the heat energy produced by the heat pump will initially still be the same. The heat emitters, on the other hand, are absorbing more heat energy from the water, which has the net effect of causing the RWT to reduce slightly. This slight reduction in RWT will increase the DeltaT between LWT and RWT, causing the heat energy output of the heat pump to increase slightly.
Without any further changes in operating parameters, the system should achieve equilibrium with a reduced indoor temperature of say 19C or even 18C.
To keep the indoor temperature more constant during the above scenario, most heat pump controllers sense the increase in DeltaT between LWT and RWT, and have the capability to increase the water flow rate by increasing the water pump speed. Although the LWT remains constant, the increase in water flow rate transfers more heat energy from the heat pump to the heat emitters, thereby supplying the additional heat loss of the building.
If the heat pump is operating in WC mode during the above scenario, the falling outside air temperature would automatically cause an increase in the required LWT produced by the heat pump. Any change to the specified DeltaT between LWT and RWT being corrected by varying the water pump speed.
A correctly optimised heat pump controller should therefore be capable of keeping indoor temperatures reasonably constant under normal operating conditions.
@derek-m Exactly, I had this formula for UFH, though not sure it is correct but seems to give results in a reasonable ball park. In any case the results illustrate your point.
G7 is room and H7 floor temp
@william1066 I think the bellimo valves that @heacol recommends are back in stock at JTM, I'm tempted to grab one for my build before he gets them all again 😉
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@heacol so if I'm going to replumb in a couple of weeks will you be selling by that point, or just get a bellimo from JTM?
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @william1066That is my current choice for replacement of existing one. At 45 lpm is 1 mh2o.
-- Attachment is not available --
doing some component research over the weekend. spirotech 1 1/4 "
https://www.spirotech.co.uk/products/spirotrap/spirotrap-mb3mbl--brass--magnet--uni-118/?variant=948
pressure loss spec took some hunting down but its 2.2kpa (0.22 mh2o) at 3.6m3/h, which is way better than the typical 28mm ones that are sold.
pricings not too bad, available in the usual places. There's even a 1 1/2" one if you wanted even more headroom.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank You need the chart, because given a big enough pump you can probably get a pretty high flow rate. I would ideally like less than .5 mh20 lost through a filter.
Posted by: @iancalderbankpressure loss spec took some hunting down but its 2.2kpa (0.22 mh2o) at 3.6m3/h, which is way better than the typical 28mm ones that are sold.
This is definitely acceptable, do you have a link to the pressure loss chart?
@william1066 3.6m3/h with a DP of 0.22mh20 means its not relying on a monster pump. the chart is here
I was comparing to some of the usual suspect 28mm versions on offer (including the spirotech one) its a substantial difference.
there's also a a caleffi one https://buyplumbingonline.co.uk/altecnic-dirtmag-brass-dirt-separator-1-1-4-546307-caleffi.html
DP is better again, down to 0.5kpa = 50mm h20 , at 60l/m for the 1 1/4"
spec sheet
I'm about to order one.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Thanks for that. I quite like the ESBE diverters, but can't seem to get the one I need here in UK. Also trying to connect 28mm to 1 1/4 will be a pain. I am not a plumber by trade, just a diy plumber, and like the simpler options 😀
@william1066 I'm exactly same as you. keen DIYer' . I'd prefer it if the filters came with 28mm connections, but those are all too small bore inside. I don't want to go with just a strainer. 28 comp to 1 1/4" is simple. https://www.monsterplumb.co.uk/compression-male-straight-coupling-28mm-x-1-1-4
diverter there is the the bellimo R3025-S2-LR230A that @heacol recommends (unless he gets his new ones imminently) I'm intending to do that part of the plumbing v soon. anything particular for the ESBE versus that one?
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
- 26 Forums
- 2,282 Topics
- 51 K Posts
- 520 Online
- 5,943 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Bosch CS5800i 5kW - Experience So Far
I’ve been reading to find out about the Bosch and you’r...
By Judith , 18 minutes ago
-
I signed up for this, I think it will be a good one. Al...
By ASHP-BOBBA , 4 hours ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@mairia - if you want to try following the discussion a...
By Transparent , 4 hours ago
-
RE: Heat Loss v Outside Air Temperature
Ideal conditions to collect the data! Although the left...
By cathodeRay , 5 hours ago
-
RE: My DIY Heat Pump installation
@majordennisbloodnok The 'more' button takes me to ...
By Polar bear , 5 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
@vsmith1 If you have access to Home Assistant then you ...
By Gmuzz , 6 hours ago
-
RE: Daikin Wireless Thermostat
If you do go for pure WC you may need to adjust the WC ...
By JamesPa , 7 hours ago
-
Aira Intelligence: integrated home energy system
Aira has just announced a new integrated home energy sy...
By Mars , 7 hours ago
-
RE: Low COP and unevenly heated rooms with 12kW Samsung AE120MXTPEH / AE260TNWTEH
i cant trace it. Near the pumps in the basement it seem...
By bonobo , 9 hours ago
-
Daikin Altherma Heating Controls using Onecta Integration via Home Assistant
Ok so likely not setting the world on fire here for rev...
By phil bell , 12 hours ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
@grahamf I don't believe there's any issue with the war...
By TreeWizard , 12 hours ago
-
@ashp-bobba That would explain it thank you, I'll take ...
By TreeWizard , 13 hours ago
-
Trying to understand my Nibe F1245
I would like to ask if anyone has any experience using ...
By Chris12 , 14 hours ago
-
RE: Who's your electricity provider and what's your tariff?
So I’m still with E.ON Next, and I received a pretty sn...
By Mars , 1 day ago
-
RE: First time wall mounting an ASHP
what you need to do is everything you can to remove the...
By ASHP-BOBBA , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Aira 12kW - @gmuzz
By Gmuzz , 1 day ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
ASHP switched off per specialists guidance. Seems the b...
By Crimson , 1 day ago
-
RE: Faulty Clivet heat pump out of the box
@steveimpey that is disappointing. I am inclined to agr...
By benson , 1 day ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@andrewj Bear with me, this is my first post on this fo...
By KevH , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
Is the ZD is a bit of a marketing ploy? has the it bee...
By BWood , 1 day ago