So plumbers have sent over adjusted calcs………
This puts all rooms basically bar my office, the main bathroom and downstairs toilet at watt deficits with current rads even at delta 20 (which might explain a lot!).
I've looked at delta 20, the MCS correction factor of 0.2325 (think that's basically 16.5 as Derek pointed out).
Doubling the eskimo heights should fix downstairs (including doubling the width of the hall rad), but MCS calc would still put the Living 2 down by 400W if ignored Eskimo's correction factor. I'll have to have a think about that, I suspect the Eskimos are actually quite good, but they've got such a deficit atm due to poor calcs in first place. For context Living 2 is down by 382W if delta 210 atm, 1286W at delta 16 and 2520W using MCS factor.
Upstairs is down other than my office as per above (explains why it's 21C in here quite easily). The deficits at delta 20 look around 300-370W between bedrooms, going up to 920W using the MCS factor (Basically 4.3x oversize).
They could be fixed with K2 up sizing, but the landing would suffer still according to the calcs.
I wonder if upstairs would just get away with it with the heat rising.
Problem I have is it's hard to judge the system as it is in mild weather etc.
@crimson With our system being commissioned on 19th. February last year - with a very mild spell for some days, I had to approximate the balancing work until the winter arrived. November of last year cooled down so I commenced the rounds of tweaking and all is well now. (I even query over 0.5 degrees C. between rooms now!) This difference is nearly always due to solar gain on the south side of the house and the ‘node’ that senses being in the living room that faces north east. Regards, Toodles.
Toodles, 76 years young and hoping to see 100 and make some ROI on my renewable energy investment!
Posted by: @toodles@crimson With our system being commissioned on 19th. February last year - with a very mild spell for some days, I had to approximate the balancing work until the winter arrived. November of last year cooled down so I commenced the rounds of tweaking and all is well now. (I even query over 0.5 degrees C. between rooms now!) This difference is nearly always due to solar gain on the south side of the house and the ‘node’ that senses being in the living room that faces north east. Regards, Toodles.
Thanks Toodles, hopefully I can get there.
Does look like a lot of rad changes incoming however due to a complete mess up by the plumbers but will see. Glad that calcs show even using delta 20 everything is off. I didn't things were so badly off, but maybe explains why the ASHP cycles like crazy.
4 days later, with guests over the weekend I left things mostly alone. I did end up changing the secondary pump speed to 1/3 as lock shields became a bit noisy in the living room. Temps seemed to have stabilised around 19.5-20C downstairs. 20.5C upstairs mostly (with lockshields right down). TRVs essential upstairs as rooms get too warm (19.5C is ideal really) unless windows open a crack. What's clear is the office is the most performant room and that I guess reflects the updated calcs that imply it's the only correctly sized one currently rad-wise.
I'm still awaiting confirmation when radiators will be swapped out. I'll have a bit of time next week to try the method of using a heater timed off and on to broadly see how many watts down we are.
All looks a bit of a mess, where's the lagging.
I was working on a Grant this week and I’m ripping out all those valves, extra pumps and low loss header.
Installing a new 3 port making the system open loop.
Technical Manager & Professional Installer: Ultimate Renewables
Posted by: @kenboneAll looks a bit of a mess, where's the lagging.
I was working on a Grant this week and I’m ripping out all those valves, extra pumps and low loss header.
Installing a new 3 port making the system open loop.
Hi Ken, lagging is done just used an old photo for the detail of pipes. I’m hoping for rad upsize replacement then will look later in the year for removal of unnecessary parts. What areas do you work in?
I've ripped all these pumps and low Loss Header out the last few days. Just a spoiler, the system still works.
Technical Manager & Professional Installer: Ultimate Renewables
that’s ideally what I’d like to have done to (once current plumbers sort the rad sizing under the contract, I don’t want them touching anything else). Its clear temps drop across the plant room alone across all this mess. Hopefully I can find someone locally to do this later in the year ahead of next winter!
@kenbone bloody hell. That would have freed up a lot space in the utility/plant room 😂
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
Follow our sustainability journey at My Home Farm: https://myhomefarm.co.uk
Posted by: @editorbloody hell. That would have freed up a lot space in the utility/plant room 😂
probably about a grand's worth as well. which could have been not spend during the original install.
its not just for laughs that we keep banging on about single loop....simpler, cheaper, more efficient
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
- 25 Forums
- 1,442 Topics
- 30.2 K Posts
- 24 Online
- 1,225 Members
Join Us!
Latest Posts
-
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
Yes, it is one of those two who first alerted me to the...
By IvanOpinion , 4 hours ago
-
RE: EV charger installation question – I don't want to bury the cable
The fact that the MCB is rated 16A tells us what we nee...
By Transparent , 4 hours ago
-
RE: Are You Getting the Most Out of Your Renewable Energy?
Thanks, @editor. Ideally it’d be someone who would li...
By Majordennisbloodnok , 6 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Unless adequately controlled it could devour your bank ...
By Derek M , 7 hours ago
-
RE: Effect of buffer tank or volumiser on heat pump system
I think that you will find that the best location for a...
By Derek M , 7 hours ago
-
RE: ASHP Commissioning: What Questions Should I Ask the Installer?
@derek-m thanks - will look out for the point regarding...
By Declan90 , 24 hours ago
-
RE: Noise problems with newly installed Samsung 8kW ASHP
@editor @kenbone Thanks, I would be very interested ...
By Elton , 1 day ago
-
RE: No-code, plug-and-play monitoring for your heat pump
This is all a bit too frequentist for my liking. The pr...
By scrchngwsl , 1 day ago
-
Relax with 4K drone footage of lawn mowing to a smooth Motown tune
Sending out some chilled weekend vibes to everyone. Lis...
By Mars , 1 day ago
-
RE: Incorrect Billing of Customers with a Smart Meter
The starting point of that discussion on Camelot-Forum ...
By Transparent , 2 days ago
-
Share Your Experiences with Heat Pump Manufacturer Support
Have you ever reached out to your air source heat pump ...
By Mars , 2 days ago
-
RE: Is this a bad installation and is there something wrong with my Samsung heat pump?
@ant87 thanks for that.
By David999 , 2 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
I might change my mind again, but I'm currently unlikel...
By IvanOpinion , 3 days ago
-
RE: Samsung ASHP scheduling help
@elgreco69 worth reading the GitHub here as that will a...
By morh , 3 days ago
-
RE: ASHP sizing - value of Heat Transfer Coefficient
@toodles Thanks for the explanation I get it now as I h...
By Jancold , 3 days ago
-
RE: Questions about yearly heat pump maintenance
For the installer, I believe servicing and maintenance ...
By Majordennisbloodnok , 3 days ago
-
RE: Rate the quality of your heat pump design and installation
@retrorich It is very worrying that any of this should ...
By Toodles , 3 days ago
-
RE: Spacing for roof fixing bolts ?
There is another consideration...but alas this doesn't ...
By Transparent , 3 days ago
-
RE: Air source heat pumps and noise
Yes, but when they go wrong things get really sticky. D...
By Majordennisbloodnok , 3 days ago
Heat Pump Humour
Latest Topics
-
By David999 3 hours ago
-
Spacing for roof fixing bolts ?
By heat-pump-newbie 6 days ago
-
ASHP sizing - value of Heat Transfer Coefficient
By jamesw 6 days ago
-
Incorrect Billing of Customers with a Smart Meter
By KoRWraith 1 week ago
-
Home energy storage & battery register
By Mars 1 week ago