Flow temperature up and down like a yo-yo
Hello all, I have started having an issue with my Mitsubishi Ecodan ASHP, whereby every few minutes it gives up trying to run even though the thermostats are asking for heat the entire time. You can see this in the attached 3 hours worth of flow temperature data from unit. You can see the temperature climb and then after a few minutes it gives up, lowers, and tries again. Periodic enough.. there is a pattern there.
Mitsubishi noted that the flow rate is lower (16l/min) than it needs to be (20-32l/min) (pump is running at max, external unit only behind the adjacent wall, so waiting for a new pump - they already sent the wrong item out once).
However, I would expect a lower flow rate to affect efficiency of the unit, not necessarily result in the heat pump giving up every few minutes.
Does anybody have any thoughts? Thanks
Mitsubishi Ecodan 11.2kW ASHP
Posted by: @greekgoddjHello all, I have started having an issue with my Mitsubishi Ecodan ASHP, whereby every few minutes it gives up trying to run even though the thermostats are asking for heat the entire time. You can see this in the attached 3 hours worth of flow temperature data from unit. You can see the temperature climb and then after a few minutes it gives up, lowers, and tries again. Periodic enough.. there is a pattern there.
Mitsubishi noted that the flow rate is lower (16l/min) than it needs to be (20-32l/min) (pump is running at max, external unit only behind the adjacent wall, so waiting for a new pump - they already sent the wrong item out once).
However, I would expect a lower flow rate to affect efficiency of the unit, not necessarily result in the heat pump giving up every few minutes.
Does anybody have any thoughts? Thanks
It would appear that your heat pump is cycling.
Is your heat set for a fixed Leaving Water Temperature (LWT), in Weather Compensation (WC) mode, or Auto Adaptation (AA) mode?
Do you have any room thermostats?
Hi, it is in weather compensation. Water heater is not turned on, so it isn’t the cause of the interruption. I have also checked that it isn’t defrosting that is the interruption. There is a thermostat for each UFH zone/room, and one for upstairs radiators. But again the interruptions to the heat pump are not a matter of a lack of thermostat asking for heat.
So, can the lower than ideal flow rate be causing the heat pump to cycle?
Mitsubishi Ecodan 11.2kW ASHP
Posted by: @greekgoddjHi, it is in weather compensation. Water heater is not turned on, so it isn’t the cause of the interruption. I have also checked that it isn’t defrosting that is the interruption. There is a thermostat for each UFH zone/room, and one for upstairs radiators. But again the interruptions to the heat pump are not a matter of a lack of thermostat asking for heat.
So, can the lower than ideal flow rate be causing the heat pump to cycle?
What are the settings for the Weather Compensation (WC)? What is the water flowrate? What is the Leaving Water Temperature (LWT) and Return Water Temperature (RWT)? Do you have a buffer tank or Low Loss Header (LLH)?
43C @ 0C to 25C @ 12C.
Flow rate is 16l/min (it should be 20-32l/min, waiting for new pump)
LWT and RWT, are those not the same values showed in the graphs (flow temperature & return temperature)?
I am afraid I don’t know the answer to the last question 🙂 What should I be looking for to answer this one?
THanks!
Mitsubishi Ecodan 11.2kW ASHP
Posted by: @greekgoddj43C @ 0C to 25C @ 12C.
Flow rate is 16l/min (it should be 20-32l/min, waiting for new pump)
LWT and RWT, are those not the same values showed in the graphs (flow temperature & return temperature)?
I am afraid I don’t know the answer to the last question 🙂 What should I be looking for to answer this one?
THanks!
Increasing the water flowrate should reduce the DT (the temperature difference between LWT and RWT), but may not stop the cycling. Cycling is normally caused by the thermal energy demand, being lower than the minimum continuous output of the heat pump, which can occur during milder weather conditions. What is the Outside Air Temperature (OAT) at the moment?
Cycling can also be caused if the thermal energy demand is reduced because not all the heat emitters are being utilised. What heat emitters do you have and are they all being used?
If you have room thermostats I would suggest that you set them all at 1C or 2C above the desired temperature.
A further cause of cycling is requesting a low Indoor Air Temperature (IAT), which also causes thermal energy demand to be reduced.
From the point of view of low water flowrate, have you check that the filter is clean?
Does anybody have any thoughts? ThanksPosted by: @greekgoddj
Hi Greekgod
I thought you might have known…. All heat pumps are made by the Greek goddess of Mischief, Delusion and Folly. Have you or your installer upset her? Goddess Ate’ is her name.
As Derek is suggesting there are quite a few possible causes. But the first thing is to ensure your flow rate can reach the upper part of the range quoted by “Mischiefbishi”. Once you can achieve that range you may then be able to identify other causes.
Im a bit surprised you’re not getting a flow rate error message tbh.
@derek-m Outside temperature was 0 🙂 thermostats inside were already 1-2 degrees higher than normal to rule out the system not calling for heat in the first place. That is all of downstairs UFH and all radiators upstairs.
The filter itself didn’t look dirty, but the technician drained some fluid, stuck it in a tube that checks how clean/dirty it is and it suggesting the system may need a clean as well (odd as the entire system/house is 3.5 years old). However the technician still believes we need to change the pump first (it doesn’t “sound right” to him). So I continue to wait for Mitsubishi to send him the pump. Will update this thread then with the new rate and whether it helps the issue.
Mitsubishi Ecodan 11.2kW ASHP
@sunandair Yup, I wait for the new pump.. then see if that helps the flow rate. If not then a clean of the system. By that point the flow rate should be right and that will be the moment of truth on whether the flow rate is the cause of the cycling.
Will be back once I have some news. Thanks to you both
Mitsubishi Ecodan 11.2kW ASHP
@greekgoddj yours is like our Ecodan 11.2 looked like a year ago (but less regular). This year I've turned up the two room-stats (upstairs and down) to 2C over the day/evening target on our all-radiator system and turned all the TRVs to max. Now I'm tweaking the w/c settings ever downward. COP has improved from 3.0ish to over 4 most days and the house is a little on the warm side. Here is this morning at 4C OAT- not always quite so flat as there are occasional defrosts:
Have you tried lowering the WC curve to see if that has an effect?
The pump is stopping because the flow temperature is rising to its desired limit - as the return is only a couple of degrees below the flow this is happening very quickly. If you reduce the target the heat pump won't put as much heat into the exchange unit and so the water will heat up leww quickly, and even if it does continue to cycle it should be less frequent.
With a higher flow rate from a new circulation pump then that flow should be able to take the heat out of exchanger with a lower rise in temp. Your dT is quite narrow, usually slowing the pump speed creates a greater dT, but perhaps returning to a faster speed will get your system back in balance - as currently the pumps through the UFH won't have slowed to allow more heat to be given up and reduce the return temp.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
-
Ecodan ASHP - How to optimise my set up?
10 hours ago
-
Ecodan DHW Settings missing
5 months ago
-
Ecodan - optimal external installation?
5 months ago
-
Ecodan help with efficiency setup and design - removing manifold mixers, LLH and pumps
6 months ago
-
Ecodan wont heat with mild outside temps
7 months ago
- 25 Forums
- 1,513 Topics
- 31.8 K Posts
- 23 Online
- 1,283 Members
Join Us!
Latest Posts
-
RE: Additional Battery v Wind Turbine v Ripple
I should add, being an investment, the value of your in...
By Old_Scientist , 4 hours ago
-
RE: Ecodan - flow rates, sensors, settings
Achieving an accurate flow measurement is probably the ...
By Derek M , 8 hours ago
-
RE: Ecodan ASHP - How to optimise my set up?
Again, thank you for another thorough post, @derek-m - ...
By rhh2348 , 10 hours ago
-
RE: Delivering a smart and secure electricity system: government consultation
@Transparent.Now that I am represented by a new MP I th...
By IanMK13 , 12 hours ago
-
RE: Vaillant aroTHERM plus not level or flat - what base is best under an external unit?
Similar thread here
By Johnmo , 13 hours ago
-
RE: VDI 2035 heating water specification
Been looking and it seems a good little project. Ever...
By Johnmo , 2 days ago
-
RE: Do I accept an ASHP and Solar Panel retrofit under the HUG 2 scheme?
Will do. I'm currently waiting for another survey / vis...
By dssr , 2 days ago
-
The company that did the borehole were expecting us to ...
By Johnmo , 2 days ago
-
-
RE: The Misquote That Ruined the Heating Industry
@abernyte manufacturer training is pretty average. They...
By Mars , 2 days ago
-
-
RE: ECO4 Scheme and EPC ratings
@mellow Thanks. Given there is a scheme requirement to ...
By Old_Scientist , 3 days ago
-
RE: Do I just go with the lowest quote for my heat pump?
@jancold To me its a no-brainer then, a max 40C flow te...
By bontwoody , 3 days ago
-
-
RE: Heat Pump Books Beginners – Bodge Buster & From Zero To Heat Pump Hero
@editor Presumably he had some good weather Compensatio...
By Toodles , 4 days ago
-
RE: New Vaillant 7kW aroTherm ASHP or oil boiler dilemma/decision??
Storage capacity really is dependent on storage tempera...
By Johnmo , 4 days ago
-
RE: HP Cycling, Expected or Undesirable
Just a little update. I ordered a longer shielded twin ...
By bontwoody , 4 days ago
-
RE: Domestic hot water timer doing crazy things on my Grant Aerona3 10kW air source heat pump
Thanks @allyfish for the pics and info. Spoke to the in...
By Mellow , 4 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
It's been a busy day for calls and emails from Aira. I ...
By MikeH , 4 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Hmm. A bit of a nuanced answer, methinks. As I've alr...
By Majordennisbloodnok , 4 days ago
Latest Topics
-
Ecodan - flow rates, sensors, settings
By rhh2348 10 hours ago
-
Replacing mains water with well water
By Johnmo 2 days ago
-
Additional Battery v Wind Turbine v Ripple
By bontwoody 2 days ago
-
By jamespipe 3 days ago
-
VDI 2035 heating water specification
By Johnmo 3 days ago
-
Do I just go with the lowest quote for my heat pump?
By Jancold 5 days ago
-
The Misquote That Ruined the Heating Industry
By Alec Morrow 5 days ago
-
Battery Storage Wiring Gauge Question
By Puff 6 days ago
Members Online
No online members at the moment