Failing heat pump system - seeking thoughts on a rebuild
A few years ago for our new build house we put in a split system that uses one bit of kit for the DHW and another main ASHP for the underfloor heating.
one part of this system is failing and the point of this post is to gather constructive ideas on what I might do next, not to publicly vilify the manufacturer / supplier. They’ll be visiting on Tuesday, so I want to give a fair chance for them to deal with the problem (although they’ve given me their remote diagnosis already and it’s not promising).
Since the system is a few years old, the main ASHP uses the older R410a refrigerant. It’s 12kW and just about copes with keeping the house warm in winter. House is about 260sqm, single storey, all UFH. There’s also a 200 litre buffer tank in this setup.
The separate hot water system is likely end of life (TBC). It includes a 300 litre tank. It is currently entirely separate from the main ashp system, although co-located to all the pipe work, etc in the same plant room.
Even if I wanted to try to have the current ASHP plumbed into the hot water supply, experience has shown that the current ASHP is not going to cope with that much demand IMO.
So if it is proven that the current hot water system is EOL, it potentially has a knock on that means the working ASHP would need replacing aswell. I would need to get a new ASHP able to provide both DHW and UFH.
So that’s where I think I’m at currently. Slightly at a loss and daunted with what I’ll need to go through to get a new (expensive) system installed. Feel free to chuck any comments you may have at me, but here’s a bunch of questions floating around my head so far…
Can a new high heat (or is it medium?) Ashp, use the existing pair of flow / return pipes into the plant room?
Can I use the ‘intelligent’ water tank as a dumb hot water tank for a rebuilt system?
Would installers be interested in using the viable parts of the system I’ve got already got here to make a working system with? Obvs people like to warranty based on all new, but trying to find a cost effective way through this.
Am I right in thinking I’m going to pay top dollar for a new ASHP, because any government support applies to new systems or gas replacement? If so, that’s painful…
Thanks for reading. I welcome any thoughts on system (re)design given that most of the knowledge I probably had gathered a few years ago is outdated or been filed away in dusty corners of my brain and might not be any use!
A couple of thoughts:
What size are the flow/return pipes pipes ?
What are you currently using for DHW heating? Which part of this is at the EOL?
Do you have an EV or are thinking of getting one?
Is improving your house insulation possible?
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody I think flow / return are 1 inch. I should probably double check that.
EV - yes, 3 currently! Old Leaf going to be sold. New Kia Niro. And my DIY EV conversion of my old VW campervan. Plenty of solar PV on the roof. But cars are pretty low mileage.
How much detail I go into on the failed DHW probably needs to wait until the visit on Tuesday. Not trying to be mysterious, just want to be fair to the supplier. But as it stands it’s seems it’s the part that heats the water and likely unrepairable - tbc. But might still leave me with a viable 300l water tank for the next system to make use of.
House insulation is pretty good, although don’t ask me for numbers. Amazing how quick all that stuff evaporates when you move on to new projects. It’s a new build timber frame. Not passiv haus, but good enough.
What's failing more precisely? I think the way forward rather depends on this.
I have several ideas but without knowing what must be replaced it's difficult to advise.
My instinct is to delete the buffer at which point you can likely reduce the flow temp from the ashp by a few degrees, thus createing some more headroom on output, and this combine the systems into one. But without more detail this is nothing more than a wild guess.
Do you have any data from the last year or two which might help inform the way forward.
But the key question remains, What's failing more precisely.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @cleardene-ashpmileage.
How much detail I go into on the failed DHW probably needs to wait until the visit on Tuesday. Not trying to be mysterious, just want to be fair to the supplier. But as it stands it’s seems it’s the part that heats the water and likely unrepairable - tbc. But might still leave me with a viable 300l water tank for the next system to make use of.
Ok just read this.
So basically dhw is failing. First of all I'd say fix that, but if not delete buffer on main system, gain perhaps 10% output capacity because you can run at a lower flow temp, add diverter valve, use main system to do everything. Tank may not have the coil you need in which case fit phe and circulator pump. This setup will likely cost less to run because of buffer deletion. Then when main heat pump reaches eol in perhaps 10 years time, update.
Problem may be that nobody will want to guarantee that, people often want to guarantee only completely new systems or ripping everything out. Personally I'd accept the guarantee limitation because it's fair.
Is it in or out of warranty?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@cleardene-ashp I'm particularly interested in DHW because you mentioned it was smart. Is it a mixergy cylinder?
I use one to heat my hot water overnight on an EV tariff very cheaply.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@jamespa thanks for your thoughts.
Whether DHW is fixable will be found out on Tuesday, but they suggest not so far.
I’m sure it’s obvious, but what’s ‘phe’ please?
One thing I will need to find out is whether the current ashp can deliver the heat for DHW aswell. As I said in the intro, I kind of doubt it based on it only just delivering enough UFH heating in winter when set to 38C. But that temp was based on guidance from the supplier when there was a separate DHW system in place. Maybe it can work, albeit less efficiently.
Out of warranty.
Thanks. It’s all useful to start my grey cells to start processing my possible options.
@cleardene-ashp OK. Well the same logic still applies. If it is able heat water with an immersion heater and you can access octopuses 7p per kWh overnight then that's the equivalent financially to a 3.5 ish COP for hot water. That just leaves heating your house to worry about.
Something we use to boost our heating in a cold room was an air conditioning unit. Inexpensive and would reduce the load on an ASHP unit.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @cleardene-ashpWhether DHW is fixable will be found out on Tuesday, but they suggest not so far.
OK. It will help if they tell you why and whats actually broken
Posted by: @cleardene-ashpI’m sure it’s obvious, but what’s ‘phe’ please?
Plate heat exchanger., basically like a coil in water but a different geometry.
There are two ways to heat a DHW tank, The first is a coil within the tank through which water from the heat pump/boiler is passed. I dont know what coil you have. If its suitable that's the simplest way. The second way is to fit a PHE, pump water from the tank through the PHE, and use the heat pump to pump water from the heat pump through the other side of the PH,E thus transferring heat to the water from the tank. This can actually be more effective if you use the right PHE.
Posted by: @cleardene-ashpOne thing I will need to find out is whether the current ashp can deliver the heat for DHW aswell. As I said in the intro, I kind of doubt it based on it only just delivering enough UFH heating in winter when set to 38C. But that temp was based on guidance from the supplier when there was a separate DHW system in place. Maybe it can work, albeit less efficiently.
If you remove the buffer which is probably unnecessary unless your HP is very old you will almost certainly eliminate a likely temperature drop across the buffer. This means that you could reduce the flow temp from the HP whilst still achieving the same FT at the UFH. This will very likely increase the max output of the HP providing headroom for the DHW. All of this is a bit dependent on the HP, but the basic effects described are pure thermodynamics, so most HPs will follow them unless the firmware deliberately restricts output (some do). If you can do this your efficiency will increase because you will be operating the HP at a lower FT.
You may have enough capacity anyway without removing the buffer (you definitely will on most days). Need to do some calcs to verify that based on your DHW usage and heat pump output on the coldest days.
Are you certain that its the heat pump that's currently limiting the heating? Do you have any data from the heat pump? What model is the HP. Is it modulating or fixed output?
Posted by: @cleardene-ashpOut of warranty.
Well that helps, you have nothing to lose by changing things and moving them in a more modern direction (subject to compatibility with your equipment)
If they declare the DHW unfixable I would spend a bit of time thinking about options, if you can. You want to be heading in the right long term direction for any investment you make in repairing the failed system.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
It would be helpful to know a bit more about the central heating. You say that it struggles to keep the house warm in winter:
- Are you confident that the UFH has been designed adequately?
- How are you controlling the primary and secondary heating circuits? Are you using weather compensation, or room thermostat, or a combination of the two?
- Are you running it continuously 24 hours per day? Do you set back the temperature at night?
I am wondering whether the heating might be constrained by the heat pump itself, the emitters (UFH), distortion due to the buffer tank, or possibly the way it is being operated.
Grant Aerona 290 15.5kW, Grant Smart Controller, 2 x 200l cylinders, hot water plate heat exchanger, Single zone open loop system with TRVs for bedrooms & one sunny living room, Weather compensation with set back by room thermostat based load compensation
@grahamf System was designed and installed by the supplier of the entire DHW and UFH heating. I don’t claim to be the expert on this, so ‘am I confident’ is hard to answer.
Primary and secondary circuits - I’m obviously going to show my ignorance here. Not sure how I apply that question to what I have here. I would have said the UFH is all one circuit, although there are 2 manifolds with various room specific pipe runs from each. Each room has a thermostat. I have a profile I use to set a temp for the different rooms. Generally 21, but sometimes warmer in the lounge.
yes the night time temps are set lower, although in winter I’ll try to make use of low night time tariffs to get the most heat for the cheapest price.
its only in the coldest months we’d run all the time.
I guess my point on whether it’s struggling and/or capable of also doing DHW is that with the flow temp set to 38 max (as advised, but perhaps it can change), I know in cold winter, we’d struggle to get reach that 38 set threshold. So expecting it to also hit 50 - 55 for DHW seems a stretch to me. But it’s possible there’s more scope to achieve higher temps with what I have when I talk to the company.
All of this discussion I’ve insisted here is possibly a bit premature because I first need to reach the point of the company formally agreeing what problem I have. Only then can I start to push on possible alternatives. But I’m doing all this just so I can start to have a slightly informed, practical discussion with them about what next steps might be when I have them captive in my house!
So I appreciate all the input so far.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 600 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
That’s my pleasure, @andrewj. The only challenge now is...
By Majordennisbloodnok , 2 hours ago
-
RE: Electricity price predictions
@toodles @skd Then there is not going to be much from t...
By ChandyKris , 2 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
@batpred I reckon Andy might know a thing or 2 about...
By Bash , 3 hours ago
-
RE: What determines the SOC of a battery?
@batpred Ironically you didn't have anything good to...
By Bash , 4 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Here’s a current graph showing a bit more info. The set...
By benson , 4 hours ago
-
RE: Setback savings - fact or fiction?
True there is a variation but importantly it's understa...
By RobS , 4 hours ago
-
Below is a better quality image. Does that contain all ...
By trebor12345 , 4 hours ago
-
Sorry to bounce your thread. To put to bed some concern...
By L8Again , 4 hours ago
-
@painter26 — they (the analogue gauges) are subtly diff...
By cathodeRay , 5 hours ago
-
Our Experience installing a heat pump into a Grade 2 Listed stone house
First want to thank everybody who has contributed to th...
By Travellingwave , 9 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 12 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 13 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 1 day ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 1 day ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 1 day ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 1 day ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...