Effect of buffer tank or volumiser on heat pump system
Can someone please either confirm or put me right on the following:
My understanding is that a buffer tank will introduce mixing of flow and return water in a system and causes its overall efficiency to reduce as a higher flow temeperature is needed.
Do volumisers have the same effect? as an installer is telling my brother in law that it wont effect the efficiency and is there as a safe guard for the defrost cycle.
I also thought that if you add up the volume of the radiators and pipes you could then say whether a volumiser was needed or not.
Thanks in advance.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
You are basically correct in what you state.
A buffer tank may cause lower efficiency due to mixing unless the water flowrate both in and out is kept balanced.
A volumiser vessel, as the name suggests, just adds volume to the system. If you look in the heat pump manual it should state the minimum required volume for the system. If the heat emitters and pipework do not provide sufficient volume then a volume vessel would be required.
I suppose it also depends where the volumiser is located, since it will lose some thermal energy, which could add to the overall energy loss if located outside the buildings thermal envelope.
There will also be added cost.
@derek-m Thanks Derek. Apart from the cost issue, would you say it was better not to have a internal volumiser if there were sufficient volume of circulating water in the radiators or is cost the only downsize?
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoody@derek-m Thanks Derek. Apart from the cost issue, would you say it was better not to have a internal volumiser if there were sufficient volume of circulating water in the radiators or is cost the only downsize?
I don't know if anyone has actually performed any tests to see if having extra water volume within the system, could improve the defrost cycle. I suppose a further possible downside would be if the system contains anti-freeze, since more anti-freeze would also increase costs.
Unless the flow rate of each water pump is matched, then there could be mixing occurring within the LLH.
Probably the easiest way to optimise the system operation, would be to try to ensure that the primary water pump (the one at the heat pump side), is always supplying slightly more water flow than the secondary water pump.
@bontwoody I went with an inline volumiser. All you say is correct, it cannot detract anything from efficiency, whereas a buffer or LLH always does - you can only seek to minimise that inefficiency with 1ary/2ary side flow rate balancing but you'll never get to zero loss.
I believe tests have been done that show that the effect defrost with a volumiser can be a bit better because there is that higher volume of hot water circulating. I have the volumiser on the flow side of the CH circuit, between the HP and the rads, inside the house in the airing cupboard. my reasoning for this is that it stores water at the LWT when the HP shuts down, meaning that at the next startup there's 50L of water already in the circuit at the last LWT, which I think smooths startup a little bit. and any heat loss is into the house.
the main reason to have one though is if your system volume is too low . I was just over the min but decided to add one to be sure (and I wasn't sure about which TRV's I'd keep at the time either), no real downside other than buying it / fitting it / finding room for it .
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
I found this by Graham Hendra which is interesting around the siting of a volumiser.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody yes thats one of the ones I read when making my decisions.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Apologies for re-introducing this topic. I was persuaded by contributers on this forum, that I should remove the second CH pump and change the function of the buffer tank to use it as a volumiser.
I have forgotten how it was suggested that I should use the four connections on the tank in this configuration.
Existing connections are LHS: Top - From ASHP; Bottom - Return to ASHP RHS Top- To CH: Bottom - Return from CH
- 26 Forums
- 2,123 Topics
- 46.7 K Posts
- 52 Online
- 4,531 Members
Podcast Picks
Latest Posts
-
RE: Is your heat pump insured?
My home insurance renewal is due soon meaning I am doin...
By cathodeRay , 13 hours ago
-
New Vaillant aroTherm Plus in black - When will it come to the UK?
It looks like Vaillant are updating the aroTherm plus l...
By Sandy , 16 hours ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 16 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Ive called most of them over the years. By far the best...
By dgclimatecontrol , 16 hours ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 20 hours ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
I've certainly seen that on their Ts & Cs page but ...
By Majordennisbloodnok , 2 days ago
-
RE: ASHP heat output monitoring
@carlo - not much better, is it. It looks more like a u...
By cathodeRay , 2 days ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 2 days ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 3 days ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@dgclimatecontrol I don't know, but they were not happy...
By DavidAlgarve , 3 days ago
-
RE: Why do we need pressurised systems?
A good question @toodles. My old open thermal store and...
By AllyFish , 3 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
Cross references for @martingale Background discussi...
By Transparent , 4 days ago
-
@ecobaker May I ask a question of you please. I too hav...
By Papahuhu , 4 days ago
-
It's unclear to me how the Smart Control project work b...
By Transparent , 4 days ago
-
RE: Have Consumers Been Lied to About the Efficiency of Heat Pumps Made in China?
@pavel, this isn't about discrediting Chinese products....
By Mars , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
We had an excellent four months (11/3 to 15/7) generati...
By JulianC , 6 days ago
-
RE: Is this just haze or something more?
I think the present somewhat cooler hazy days show the ...
By Judith , 7 days ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
All noted and accepted and as I say I am sorry that you...
By JamesPa , 7 days ago
-
I think it is very much me that is sitting outside the ...
By Grantmethestrength , 7 days ago