Effect of buffer tank or volumiser on heat pump system
Can someone please either confirm or put me right on the following:
My understanding is that a buffer tank will introduce mixing of flow and return water in a system and causes its overall efficiency to reduce as a higher flow temeperature is needed.
Do volumisers have the same effect? as an installer is telling my brother in law that it wont effect the efficiency and is there as a safe guard for the defrost cycle.
I also thought that if you add up the volume of the radiators and pipes you could then say whether a volumiser was needed or not.
Thanks in advance.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
You are basically correct in what you state.
A buffer tank may cause lower efficiency due to mixing unless the water flowrate both in and out is kept balanced.
A volumiser vessel, as the name suggests, just adds volume to the system. If you look in the heat pump manual it should state the minimum required volume for the system. If the heat emitters and pipework do not provide sufficient volume then a volume vessel would be required.
I suppose it also depends where the volumiser is located, since it will lose some thermal energy, which could add to the overall energy loss if located outside the buildings thermal envelope.
There will also be added cost.
@derek-m Thanks Derek. Apart from the cost issue, would you say it was better not to have a internal volumiser if there were sufficient volume of circulating water in the radiators or is cost the only downsize?
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoody@derek-m Thanks Derek. Apart from the cost issue, would you say it was better not to have a internal volumiser if there were sufficient volume of circulating water in the radiators or is cost the only downsize?
I don't know if anyone has actually performed any tests to see if having extra water volume within the system, could improve the defrost cycle. I suppose a further possible downside would be if the system contains anti-freeze, since more anti-freeze would also increase costs.
Unless the flow rate of each water pump is matched, then there could be mixing occurring within the LLH.
Probably the easiest way to optimise the system operation, would be to try to ensure that the primary water pump (the one at the heat pump side), is always supplying slightly more water flow than the secondary water pump.
@bontwoody I went with an inline volumiser. All you say is correct, it cannot detract anything from efficiency, whereas a buffer or LLH always does - you can only seek to minimise that inefficiency with 1ary/2ary side flow rate balancing but you'll never get to zero loss.
I believe tests have been done that show that the effect defrost with a volumiser can be a bit better because there is that higher volume of hot water circulating. I have the volumiser on the flow side of the CH circuit, between the HP and the rads, inside the house in the airing cupboard. my reasoning for this is that it stores water at the LWT when the HP shuts down, meaning that at the next startup there's 50L of water already in the circuit at the last LWT, which I think smooths startup a little bit. and any heat loss is into the house.
the main reason to have one though is if your system volume is too low . I was just over the min but decided to add one to be sure (and I wasn't sure about which TRV's I'd keep at the time either), no real downside other than buying it / fitting it / finding room for it .
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
I found this by Graham Hendra which is interesting around the siting of a volumiser.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody yes thats one of the ones I read when making my decisions.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Apologies for re-introducing this topic. I was persuaded by contributers on this forum, that I should remove the second CH pump and change the function of the buffer tank to use it as a volumiser.
I have forgotten how it was suggested that I should use the four connections on the tank in this configuration.
Existing connections are LHS: Top - From ASHP; Bottom - Return to ASHP RHS Top- To CH: Bottom - Return from CH
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 16kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
- 26 Forums
- 2,406 Topics
- 54.6 K Posts
- 186 Online
- 6,092 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Please help with the settings ecodan
Are you trying to address any particular performance is...
By Sheriff Fatman , 5 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
🤣 Well, I never managed to get the HA solis "...
By Batpred , 7 hours ago
-
RE: Experience - New Build / Complete New Heating System
Your sap clculations should give you a heat loss figure...
By JohnnyB , 7 hours ago
-
RE: Vaillant aroTherm not heating with many faults
@editor hmmm, our engineers Rae, Craig, Naz, Rob and Ry...
By ASHP-BOBBA , 8 hours ago
-
RE: Post-Traumatic Heat Pump Stress Disorder
@editor Hi Mars. I totally agree with your comments. ...
By Richard24738 , 8 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
Indeed! And my apologies, I should have expected you...
By Batpred , 8 hours ago
-
RE: I’m glad the cold spell is over!
@editor as a reply for this date the 6th of Jan in o...
By Nursethescreens , 9 hours ago
-
RE: Heat loss based on gas usage
@jamespa Thanks. The numbers posted above were jus...
By Bash , 9 hours ago
-
RE: Heat pump not reaching flow temperature
I would describe this as either a fault or a configurat...
By JamesPa , 10 hours ago
-
RE: New Daikin 11kW Altherma 3M install - is it working as it should?
I forgot to mention: Octopus measured our heat loss at ...
By Toodles , 13 hours ago
-
RE: Considering MLCP (Multi-Layer Composite Pipe) for ASHP
Thanks Mars and thank you for reaching out to so many p...
By iotum , 13 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: @davec Manufacturer: Peak Energy Mode...
By DaveC , 13 hours ago
-
RE: Rate the quality of your heat pump design and installation
Well, the guy came out, turned the heat pump to max, we...
By razz , 13 hours ago
-
Midea R32 setup and bizarre running with lengthy off periods?
Hi I am new to the world of ASHP and have just had a re...
By Countryman Helmsley , 14 hours ago
-
RE: Setback savings - fact or fiction?
Given the weather has been relatively stable, the empir...
By Batpred , 14 hours ago
-
RE: GSHP WOES! Midland based engineer recommendations?
@editor That is very kind! Thank you so much.
By johnbroome , 15 hours ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@wally Hi I am not sure how large your house is b...
By TechnoGeek , 16 hours ago
-
RE: Predicted Heat Loss & Needs from MCS calcs vs EPC vs actual
I've been thinking along similar lines to @tim441 from ...
By Sheriff Fatman , 17 hours ago
-
Thanks, @technogeek. Good to hear about the accuracy. ...
By Majordennisbloodnok , 17 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
In my case it was a very specific pattern of behaviour ...
By Sheriff Fatman , 18 hours ago