Ecodan Zones/Wireless controller
Hi, I've recently moved into a new build which has an Ecodan PUZ-WM60VAA set up with DHW, Zone 1 > UFH, Zone 2 > rads.
There's one Heatmiser stat for the rads upstairs. UFH has stats in each room.
This is obviously setup like an old-school boiler, inefficient for a heat pump and leads to short cycling.
I purchased a couple of the wireless Mitsubishi stats and set them up, put the system into room temp mode (auto adapt?). However, I soon learned that the Heatmiser stats do actually call for heat and the system will not stop heating until it hits their limit, even when the wireless stats are showing a temp higher than the target.
I disabled 2 dip switches (SW2-1 & SW3-1) which prevents the stats controlling the heat and just act as pump control. This seems to work for the UFH however, Z2 will not heat independent of Z1 and with Z2's pump running will not put any heat into the radiators even while Z1 is flowing at 40c.
It seems the solution to this is: "For 2-zone temperature control, check DIP SW2-7 is set to ON (2-zone temperature control) and DIP SW2-6 is set to ON (With Mixing Tank)"
These are both off, I'm assuming I don't have a mixing tank and cannot just enable these?
I'm looking for a solution, maybe I need to hound the developer?
Tank image:

There’s quite a lot going on here, so we'll try to break it down with some unofficial insights from Mitsubishi. It sounds like your system is set up with two zones at the same design temperature rather than two zones with different temperatures. If that’s the case, SW2-6 & SW2-7 (which are for systems with a mixing tank) wouldn’t apply here. Instead, it seems SW3-6 is managing the two zones with the same temperature settings, and that’s correct for your system as it stands.
When it comes to third-party stats like Heatmiser, they usually work best when the Ecodan’s weather compensation is set up properly. The stats can then manage room temperatures and schedules. One potential tweak might be to check if the Heatmiser stats allow you to adjust the hysteresis (basically the delay between on/off signals). Widening this could help reduce short cycling. Another workaround some people use is combining zones or removing actuator heads to simplify the system and move towards an open-loop design, which can also reduce cycling.
For the Mitsubishi stats, Zone 1 should be fine in Auto Adaptive mode, but Zone 2 has to either follow the weather compensation curve or run in fixed flow mode. To get Zone 2 heating independently, you’ll probably need to look at what’s controlling its pump. It might require adjusting the signal cables or wiring, but it’s hard to say without seeing the full setup.
At this stage, it might be worth getting a heating engineer to take a closer look – they’ll be able to advise on pump controls, wiring changes or any other tweaks to get everything working smoothly. Mitsubishi’s Homeowner Helpline (0161 866 6064) could also be helpful for further advice.
Also, this video might help:

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
- 26 Forums
- 2,112 Topics
- 46.4 K Posts
- 34 Online
- 3,408 Members
Latest Posts
-
RE: Wood burner with ASHP - direct air?
Hi Topher, Thanks for the tag Mars. I am.indeed o...
By Sune , 26 minutes ago
-
RE: No-code, plug-and-play monitoring for your heat pump
I think I have found “The One!” Waveshare ESP32-S3-POE-...
By Grantmethestrength , 14 hours ago
-
RE: Buffers, hot water and cooling
@prunus, @jamespa is correct, but removing the buffer ...
By Brendon Uys , 18 hours ago
-
@downfield and @toddles, this isn’t in the settings cur...
By Mars , 2 days ago
-
RE: Homely launched for Grant Aerona ASHP control
I haven't bought the Aerona Smart Controller (£700!) bu...
By Prunus , 2 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
For the record, Grant supply ethylene glycol for their ...
By Prunus , 2 days ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer amazing. Well done!
By Mars , 2 days ago
-
RE: Say hello and introduce yourself
Hi @topher - you might be interested to see this very r...
By Transparent , 3 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Ebac 5kw - Monobloc R32. Developed and made in UK - Mit...
By marcinwloch69@gmail.com , 4 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Just another thought - it might be worth thinking about...
By JamesPa , 4 days ago
-
RE: BUS Grant: removal of all other fossil fuel heat sources
@rikiarn - just have a think as to how much it will cos...
By Transparent , 5 days ago
-
Don't do much digging around.That's best left to the pr...
By Transparent , 5 days ago
-
Hi all, I was wondering if anyone had an idea of how th...
By Wh0am3ye , 5 days ago
-
RE: EBAC re-entering the ASHP market in 2023
@toodles confirm i have Ebac 5kw ASAP + homely and it w...
By marcinwloch69@gmail.com , 5 days ago
-
RE: Compute heat loss from energy used
@jamespa Ebac must be similar to Mitsubishi as they buy...
By marcinwloch69@gmail.com , 5 days ago
-
@pie_eater I have been thinking of adding cooling to my...
By TechnoGeek , 7 days ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
Agree, but you may have a hard time convincing them, as...
By JamesPa , 1 week ago
-
RE: Seal the Deal: Don't Let Your Heat Pump Leak Energy
Hi - fyi - there's a dead image link in the 'Optimal In...
By seatonian , 1 week ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
@chandykris Horses and beggars…. 😉 Toodles.
By Toodles , 1 week ago
-
RE: Cleaning up after gas meter removed
@agentgeorge Likewise in the loft space; we have 300mm ...
By Toodles , 1 week ago