Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan Zones/Wireless controller
Hi, I've recently moved into a new build which has an Ecodan PUZ-WM60VAA set up with DHW, Zone 1 > UFH, Zone 2 > rads.
There's one Heatmiser stat for the rads upstairs. UFH has stats in each room.
This is obviously setup like an old-school boiler, inefficient for a heat pump and leads to short cycling.
I purchased a couple of the wireless Mitsubishi stats and set them up, put the system into room temp mode (auto adapt?). However, I soon learned that the Heatmiser stats do actually call for heat and the system will not stop heating until it hits their limit, even when the wireless stats are showing a temp higher than the target.
I disabled 2 dip switches (SW2-1 & SW3-1) which prevents the stats controlling the heat and just act as pump control. This seems to work for the UFH however, Z2 will not heat independent of Z1 and with Z2's pump running will not put any heat into the radiators even while Z1 is flowing at 40c.
It seems the solution to this is: "For 2-zone temperature control, check DIP SW2-7 is set to ON (2-zone temperature control) and DIP SW2-6 is set to ON (With Mixing Tank)"
These are both off, I'm assuming I don't have a mixing tank and cannot just enable these?
I'm looking for a solution, maybe I need to hound the developer?
Tank image:

There’s quite a lot going on here, so we'll try to break it down with some unofficial insights from Mitsubishi. It sounds like your system is set up with two zones at the same design temperature rather than two zones with different temperatures. If that’s the case, SW2-6 & SW2-7 (which are for systems with a mixing tank) wouldn’t apply here. Instead, it seems SW3-6 is managing the two zones with the same temperature settings, and that’s correct for your system as it stands.
When it comes to third-party stats like Heatmiser, they usually work best when the Ecodan’s weather compensation is set up properly. The stats can then manage room temperatures and schedules. One potential tweak might be to check if the Heatmiser stats allow you to adjust the hysteresis (basically the delay between on/off signals). Widening this could help reduce short cycling. Another workaround some people use is combining zones or removing actuator heads to simplify the system and move towards an open-loop design, which can also reduce cycling.
For the Mitsubishi stats, Zone 1 should be fine in Auto Adaptive mode, but Zone 2 has to either follow the weather compensation curve or run in fixed flow mode. To get Zone 2 heating independently, you’ll probably need to look at what’s controlling its pump. It might require adjusting the signal cables or wiring, but it’s hard to say without seeing the full setup.
At this stage, it might be worth getting a heating engineer to take a closer look – they’ll be able to advise on pump controls, wiring changes or any other tweaks to get everything working smoothly. Mitsubishi’s Homeowner Helpline (0161 866 6064) could also be helpful for further advice.
Also, this video might help:
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
- 27 Forums
- 2,783 Topics
- 65.6 K Posts
- 4,743 Online
- 7,187 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Getting closer to a finished Haier system
Theres comprehensive instalation and service manuals (I...
By Singlespeed , 5 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
There is now a new Secretary of State for Energy Securi...
By Transparent , 5 hours ago
-
RE: Do I add Air Con or MVHR to existing A2W ASHP?
@rob-of-york Looks like an impressive bit of kit. Just ...
By Batpred , 6 hours ago
-
RE: DIY Heat Pump Installations: Navigating Legal and Regulatory Hurdles
The idealist in me says pioneers in this space should b...
By Batpred , 6 hours ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
@ashp-bobba, I thought it was an interesting parallel. ...
By Mars , 9 hours ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent No it was my baby, entirely delivered by m...
By bontwoody , 11 hours ago
-
RE: How should the Boiler Upgrade Scheme be reformed?
Ah, that makes sense when a combi is in place. The boil...
By Batpred , 1 day ago
-
RE: Replacing Storage Heaters with a Heat Pump in a Stone Cottage
@bobflux Thanks, that gives me something to check the i...
By Paul1098 , 1 day ago
-
RE: Tesla Powerwall (2) Calibration Cycles
For Powerwall calibration, avoid forcing repeated deep ...
By EnergyStorageTech , 2 days ago
-
Over the years, due to the non barrier PEX underfloor h...
By bobflux , 2 days ago
-
RE: battery storage without solar
Indeed, current on the grid input = current used for ch...
By bobflux , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
@papahuhu @papahuhu A lot of tears and sweat went into ...
By Andris , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
We have the same problem, 12 mature trees clip the morn...
By Papahuhu , 4 days ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
I had a battery and inverter installed a while ago, my ...
By Batpred , 5 days ago
-
RE: Is This Initial Free Quote From Octopus Trusted Partner Reasonable?
@ltron2 The EPC on our house is A-92, however that i...
By Rob of York , 5 days ago