[Solved] Ecodan. How to run this efficiently with zero understanding.

286 Posts
17 Users
104 Reactions
49.2 K Views
Si Fillo
(@si-fillo)
Trusted Member Member
262 kWhs
Joined: 2 years ago
Posts: 36
 

@mjr no, you are right. Dip switch 1 has 8 switches and 7 & 8 only are on for me.

I still don't understand how 192=11000000 though but not to worry. At least your theory is correct! Although don't know what the readout problem with my dip switch 5 is.

Screenshot 2023 02 15 13 32 15 80 f541918c7893c52dbd1ee5d319333948

 


   
ReplyQuote
(@derek-m)
Illustrious Member Member
15283 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4429
 

As humans we have been taught to count using the decimal (denary) systems as shown below.

  (100's)    (10's)     (1's)

      1            9           2

For operational reasons, computers count, and store data, using the binary system as shown below.

(128's) (64's) (32's) (16's) (8's) (4's) (2's) (1's)

    1        1        0        0       0      0      0     0

So 192 in decimal is actually stored as 11000000 in binary in a computer.

Since 8 bits equals 1 byte, it is possible for a computer to store the position of 8 switches using just 1 byte of memory, rather than using 1 byte for each switch. Human's are not too happy counting in binary, so on the computer display a number would normally been shown in decimal.

In your particular screen display I am surprised that the developer did not lay it out differently. Had I been creating the display I would have done it as shown below.

                                        Posn 

DipSwitch          (8)  (7)  (6)  (5) (4)  (3)  (2) (1)

      1                On  On  Off  Off  Off  Off  Off  Off

      2                On  Off  Off  Off  Off  Off  Off  Off

      3                Off  Off  Off  On  Off  Off  Off  Off

      4                Off  Off  Off  Off  Off  Off  Off  Off

      5                Off  Off  Off  Off  Off  Off  Off  Off

      6                Off  Off  Off  Off  Off  Off  Off  Off

 

Simples. 😎 

 


   
👍
1
ReplyQuote
(@john-connett)
Trusted Member Member
166 kWhs
Joined: 2 years ago
Posts: 20
 

Posted by: @derek-m

@davew

According to the wiring diagram on page B35 of the large manual, the control signal for the main water pump should be connected to CNPWM, which is located in the upper right-hand section of the circuit board.

What is this large manual of which you speak? I've looked at the Installation Manuals for the FTC5 and FTC6. Both have circuit board illustrations that feature the CNPWM connector but no description of its use. It has three terminals which suggest it might be suitable for pump control. I'm looking with colleagues at a FTC5 installation with a Grundfoss pump which is PWM capable but doesn't currently have a PWM cable connected. The system provides underfloor heating in a museum building and we're keen to reduce our running bills.

 

This post was modified 2 years ago by john.connett

   
ReplyQuote
(@derek-m)
Illustrious Member Member
15283 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4429
 

What is this large manual of which you speak? I've looked at the Installation Manuals for the FTC5 and FTC6. Both have circuit board illustrations that feature the CNPWM connector but no description of its use. It has three terminals which suggest it might be suitable for pump control. I'm looking with colleagues at a FTC5 installation with a Grundfoss pump which is PWM capable but doesn't currently have a PWM cable connected. The system provides underfloor heating in a museum building and we're keen to reduce our running bills.

 

The large manual is the 'AIR TO WATER HEAT PUMP SYSTEMS' Data Book, which unfortunately I can no longer post a copy on the forum. It is now deemed too large.

To help reduce running bills it would probably be useful to improve insulation if at all possible. The heat pup should be operated in weather compensation mode, with the lowest water temperature that meets the heat loss.

 


   
ReplyQuote
(@john-connett)
Trusted Member Member
166 kWhs
Joined: 2 years ago
Posts: 20
 

Posted by: @derek-m

The large manual is the 'AIR TO WATER HEAT PUMP SYSTEMS' Data Book, which unfortunately I can no longer post a copy on the forum. It is now deemed too large.

To help reduce running bills it would probably be useful to improve insulation if at all possible. The heat pup should be operated in weather compensation mode, with the lowest water temperature that meets the heat loss.

Looks like this may be it: Air to Water Heat Pump Systems Databook Vol. 5.3 R32

Download it as a PDF if you want to be able to search it.

The building is a recent refurbishment of an industrial unit. Almost everything replaced apart from the steel frame and (substantial) concrete floor. Good insulation and underfloor heating. The heat pump seemed to be using quite a lot of electricity during the summer when it should have almost nothing to do (It doesn't supply DHW).

Pump appears to be a Grundfoss UPS3. Mitsubishi provide minimal information about PWM. Would it just work if a cable was connected from the pump to CNPWM or is there more configuration required?

 

This post was modified 2 years ago by john.connett

   
ReplyQuote
(@harriup)
Reputable Member Member
1073 kWhs
Joined: 3 years ago
Posts: 107
 

@john-connett  PWM control has been discussed elsewhere and I think the opinion is that it is not functional in the Mitsubishi system. Perhaps the board was designed with it mind, possibly it is just residual having been adapted from another product, but either way unless the software is written to use it, it won't function. The FTC settings have an option to set 5 different pump speeds but nothing referring to PWM.

If you are taking energy use from the readings on the FTC controller, then just don't! There seems to be a minimum recorded level of energy consumption even when less is being used, this is particularly noticeable over summer when no heating is being done. This can amount to a reading of 90kWh per month even though only around 15kWh has actually been drawn.

Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV


   
ReplyQuote



(@derek-m)
Illustrious Member Member
15283 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4429
 

Posted by: @john-connett

Posted by: @derek-m

The large manual is the 'AIR TO WATER HEAT PUMP SYSTEMS' Data Book, which unfortunately I can no longer post a copy on the forum. It is now deemed too large.

To help reduce running bills it would probably be useful to improve insulation if at all possible. The heat pup should be operated in weather compensation mode, with the lowest water temperature that meets the heat loss.

Looks like this may be it: Air to Water Heat Pump Systems Databook Vol. 5.3 R32

Download it as a PDF if you want to be able to search it.

The building is a recent refurbishment of an industrial unit. Almost everything replaced apart from the steel frame and (substantial) concrete floor. Good insulation and underfloor heating. The heat pump seemed to be using quite a lot of electricity during the summer when it should have almost nothing to do (It doesn't supply DHW).

Pump appears to be a Grundfoss UPS3. Mitsubishi provide minimal information about PWM. Would it just work if a cable was connected from the pump to CNPWM or is there more configuration required?

 

Don't quote me on this, but I assume that the system may work in the following manner:-

The 240v ac supply is provided to the water pump from TBO.1 terminals 1 & 2, or from connector CNP1. This will start and stop the water pump as required.

If the installed water pump is capable of PWM control, a second control cable would be connected to connector CNPWM to vary the water pump speed. It may be that the pump speed is not continually variable, but can be set to one of five speed settings.

Don't forget that there will probably be water pumps associated with the UFH system, which may entail balancing flow rates.

The attached youtube video clearly shows that the pump speed can be varied, provided that the correct equipment has been installed.

As far as energy usage is concerned, how are you operating your system? Are you operating the heat pump in weather compensation mode? How are you controlling the UFH?

 


   
ReplyQuote
(@fazel)
Reputable Member Member
1085 kWhs
Joined: 2 years ago
Posts: 124
 

Posted by: @harriup

The FTC settings have an option to set 5 different pump speeds but nothing referring to PWM.

 

PWM is how the pump speed step(1-5) is controlled from the controller.

 

Version 5.8

https://library.mitsubishielectric.co.uk/pdf/book/Ecodan_ATW_Databook_R32_Vol5_5

 


   
ReplyQuote
(@john-connett)
Trusted Member Member
166 kWhs
Joined: 2 years ago
Posts: 20
 

Posted by: @fazel

Posted by: @harriup

The FTC settings have an option to set 5 different pump speeds but nothing referring to PWM.

PWM is how the pump speed step(1-5) is controlled from the controller.

 

The Grundfoss UPS3 is a smart pump with a number of control modes, including three fixed speeds, proportional pressure and underfloor mode. PWM makes some sense with the fixed speed modes but, maybe, not with the others. I wonder if the pump is smart enough to ignore the PWM signal when it is working to its own priority to maintain proportional pressure (for radiators without an automatic bypass) or constant pressure (for underfloor mode)? I don't know which mode the museum's UPS3 is using, the underfloor mode might be the best match. Perhaps the UPS3 is smarter than the FTC5?

The Grundfoss ALPHA3 is even smarter and can be programmed using Bluetooth from an app on a mobile phone.

 


   
ReplyQuote
(@john-connett)
Trusted Member Member
166 kWhs
Joined: 2 years ago
Posts: 20
 

Posted by: @john-connett

Posted by: @fazel

Posted by: @harriup

The FTC settings have an option to set 5 different pump speeds but nothing referring to PWM.

PWM is how the pump speed step(1-5) is controlled from the controller.

 

The Grundfoss UPS3 is a smart pump with a number of control modes, including three fixed speeds, proportional pressure and underfloor mode. PWM makes some sense with the fixed speed modes but, maybe, not with the others. I wonder if the pump is smart enough to ignore the PWM signal when it is working to its own priority to maintain proportional pressure (for radiators without an automatic bypass) or constant pressure (for underfloor mode)? I don't know which mode the museum's UPS3 is using, the underfloor mode might be the best match. Perhaps the UPS3 is smarter than the FTC5?

Oops! Wrong pump. I have been informed that we have Grundfoss UPM3 HYBRID 25-70 180 ACA pumps. Sorry for the confusion. According to UPM3 Installation and operating instructions, page 13, the UPM3 HYBRID offers a choice of 19 control modes, including three constant pressure modes. Interesting that This item is no longer in production! We are sorry, but we did not find a replacement in our online catalogue.

 


   
ReplyQuote
Page 24 / 24
Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security