Ecodan help with efficiency setup and design - removing manifold mixers, LLH and pumps
Hi all
After reading through others posts mainly all off "Ecodan. How to run this efficiently with zero understanding" I have decided I need to finally do something about my install.
background
back in 2021 we completely renovated the house new insulation was installed a MVHR full UFH upstairs and downstairs and new 8.5 KW Ecodan heat pump with 210l pre plumbed cylinder.
winter 2021 was expensive as weather compensation wasn't set up and every room (even open plan areas were zoned)
2022 was better as I learned more about weather compensation and combined all the downstairs open plan to one stat
this year has been about the same but it is in no way efficient.
The problem
The house is 3 bed (about 120 m2) and has 5 circulation pumps !! 🤡 the system is also controlled by 7 3rd party thermostats and the pre plumbed cylinder has a low loss header.
with weather compensation the circulation pumps never turn off even with the heatpump idling for hours and because we have so many I feel its costing a lot (using the energy monitor I think about 300w instant or 7KWh a day 😢
I have bought some amazon thermometers that I have installed on the low loss heater and noticed that the upstairs is receiving cooler water and had no real DT
The plan
After reading "How to correctly install heat pumps so that they work properly and efficiently" I think my ideal solution would be remove the manifold mixers and pumps, remove the circulation pumps, remove the low loss header, upgrade the one remaining pump that currently does the heat pump to low loss header so this can included all the UFH, I don't know if this is possible?
sorry if this post is a bit scattered I have tried to include as much information as I can I seem to have a lot of problems all going on at the same time I also think the heat pump maybe a bit oversized but that's its own problem. i've included some pictures bellow.
I am open to any ideas or knowledge you might have
Thanks for all your help
Rich
cylinder and low loss header
low loss header
manifold
manual showing cylinder
testing cheap amazon thermometers
example of normal running and +4 on the controller
I have sketched out my thought process to try and explain things easier. The hot water cylinder has a pre plumbed plate heat exchanger that I have tried to show.
The idea I think could work however I am not sure if one pump is powerful enough?
I also forgot to include the top setup has a bypass on both the upstairs and downstairs.
Thanks
I suppose the starting point would be to check the heat loss calculation for your home against the required Leaving Water Temperature (LWT) needed to meet this heat demand.
Since you have full UFH throughout your home I cannot, in principle, see any reason why you cannot remove the UFH mixing pumps and re-pipe the system as you propose.
You would probably need to check the specification of the main water pump to ensure that it can provide the required flowrate, with the head and size of pipework within your system.
You could probably keep the thermostats, but set them above desired room temperature to act as an over-temperature restriction.
You may also be able to keep the bypass valves provided that they do not bypass unless necessary.
Thanks for the reply
unfortunately all my knowledge has come along after install so I never asked or saw any heat loss calculations 🙄
the best I have is the MCS certificate that states 45c flow temperatures and 3.79 scop (I wish)
annual space heating 20,700 and water at 3,596
the EPC that was preformed after was 9,644 KWh heating and 2,954KWh water
with the weather outside colder now 0c the hes pump is reporting Lwt of 33c and the house is sat at 21c
The stats are currently set at 23 as temperature limiters that don’t ever get reached,
I’m not sure how I could guess the amount of pipework? again I did not ask enough questions at the time and relied on them being knowledgable so didn’t see the underfloor plan
Posted by: @richThanks for the reply
unfortunately all my knowledge has come along after install so I never asked or saw any heat loss calculations 🙄
the best I have is the MCS certificate that states 45c flow temperatures and 3.79 scop (I wish)
annual space heating 20,700 and water at 3,596
the EPC that was preformed after was 9,644 KWh heating and 2,954KWh water
with the weather outside colder now 0c the hes pump is reporting Lwt of 33c and the house is sat at 21c
The stats are currently set at 23 as temperature limiters that don’t ever get reached,
I’m not sure how I could guess the amount of pipework? again I did not ask enough questions at the time and relied on them being knowledgable so didn’t see the underfloor plan
If my understanding is correct, all this information should have been provided in a handover pack along with adequate training. If you did not receive a pack then I would suggest that you contact your installer and request one.
Thanks I did not receive a pack so will contact again, I don’t have very high hopes as the company who did all the plumbing had a MCS certified person “inspect” and commission the system. I was with him during the commissioning as got a 2 minute lesson on the controller and told if you have problems he could come back and do advanced things like alter the weather compensation curve.
I have tried to contact the company last year I think and the response I got was that the MCS certified person had become extremely hard to reach even for them and was not really responding,
unfortunately it has been a lesson learned in doing more research before starting.
This is why I want to fix the system myself if possible unfortunately the whole thing has left me with little trust of the next person coming and fixing it correctly
No problem if you don't have all the details, but someone should have carried out heat loss calculations to be able to adequately design the system.
The fact that your system is operating with a LWT of 33C at an Outside Air Temperature (OAT) of 0C, would seem to indicate that you don't have any serious problems. What is your concern?
Yeah I hope some calculations were done I think the company just sent all the plans to Mitsubishi and they suggested this if I’m completely honest.
The system seems to do well when it’s cold outside and struggle more with warmer conditions,
my concern is due to the system running 24/7 in weather compensation the 5 pumps run constantly. I tried turning the temperature down so the heatpump turned off and measured the power before stopping the pumps and powering down and this difference was 300w or 7.2kwh per day I know it will take energy to move the water around the system but 1,500kwh in 6 months heating seems a lot ?
Posted by: @richYeah I hope some calculations were done I think the company just sent all the plans to Mitsubishi and they suggested this if I’m completely honest.
The system seems to do well when it’s cold outside and struggle more with warmer conditions,
my concern is due to the system running 24/7 in weather compensation the 5 pumps run constantly. I tried turning the temperature down so the heatpump turned off and measured the power before stopping the pumps and powering down and this difference was 300w or 7.2kwh per day I know it will take energy to move the water around the system but 1,500kwh in 6 months heating seems a lot ?
You are probably correct.
You should certainly be able to remove the mixing valves and UFH pumps, which would normally be required if you have a mix of UFH and radiators or a higher temperature boiler.
I would suggest that you ask your installer for details of the UFH pipework and capacity, since you may need to ensure the system has the minimum volume required by your heat pump.
As a test, you could try bypassing the Low Loss Header (LLH), remove the two circuit pumps after the LLH and put pipework in their place, then see if the main water pump is able to cope.
@rich seems to me like you should be able to do what you have drawn, yes the LLH is ruining your COP based on those temps you've measured.
the fact you are UFH throughout is great, means the temperature down-mixing valves not needed. your pump electrical usage to move the water is indeed excessive. don't stress too much about not knowing the heat loss or head loss, you can take an empirical approach. If after re-piping so that its all done by one of your existing pumps, that one pump isn't quite enough (it'll be obvious, some areas won't get flow) its trivial to buy 1 larger pump. you'll still gain a lot on electrical usage. worst case you may have to tolerate some part of the house not being warm enough until you're able to get and fit a larger pump. although, looking at your pictures one of the pumps mounted on the cylinder looks "bigger" so you might be ok - is that the one driving the primary from the heat pump outdoor unit? what type pump is it?
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Thanks for all the advice, I have contacted the original installer and asked if they can send over any information they might still have.
You are correct the pump that circulates the heatpump is different its a UPM GEO 25-85 130 I couldn't find a great deal of information about it online but did manage to find this chart.
I think as you have said my best approach is to do the modifications and monitor the results I remember reading you can check the flow using the FTC and I am fairly sure I could restrict the upstairs flow more to push it around other circuits as this always has a very low DT
I cant seen to upload the screenshot at the moment but I found the chart here on page 38
@rich a UPM 25-85 130 is fairly beefy, it may well be enough to run the whole thing. I run a 210m2 house on a single UPM 25-95 130.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
-
Ecodan ASHP - How to optimise my set up?
2 months ago
-
Ecodan DHW Settings missing
7 months ago
-
Ecodan - optimal external installation?
8 months ago
-
Have Consumers Been Lied to About the Efficiency of Heat Pumps Made in China?
8 months ago
-
Ecodan wont heat with mild outside temps
10 months ago
- 25 Forums
- 1,615 Topics
- 34.8 K Posts
- 64 Online
- 1,887 Members
Join Us!
Latest Posts
-
RE: Interesting new product for woodburners - Recoheat
It’s not the most polished design in the world. We don’...
By Mars , 3 hours ago
-
RE: alternative to Homely - HavenWise. Anyone used it?
@editor I'll watch with interest. My LG ashp does not h...
By Tim441 , 3 hours ago
-
RE: Has anyone seen this problem before? Huge anticycling times
I’m sorry - I thought I had replied but I don’t see it!...
By cg360 , 4 hours ago
-
RE: Which liquid is used in the central heating loop?
@trbob Ah! Now, what you are referring to (R32) is the ...
By Toodles , 5 hours ago
-
RE: Will heat pump heat hot water without increasing the temp in my home?
Thankfully I do have a electricity smart meter thing so...
By Ellyse , 6 hours ago
-
RE: How to Solve Mould and Mildew Issues in Renovated Properties
MEV - Mechanical Extract Ventilation. A central extract...
By Johnmo , 6 hours ago
-
RE: In the middle of an ASHP installation - a few questions (and issues)
Thanks all. To cover all the points and advice: 1. Pa...
By benson , 8 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Update from our Aira install. We've just had an enginee...
By MikeH , 10 hours ago
-
RE: Calculating inverter size to match battery size
Erm... yes, but that's bad practice. As GB moves towa...
By Transparent , 12 hours ago
-
RE: Ecodan - flow rates, sensors, settings
I am assuming you are aware of the FTC(6, I think) pump...
By rhh2348 , 16 hours ago
-
RE: Determining correct flow rate for a heat pump
Assume so too. I think my pipes are at 150mm centres,...
By rhh2348 , 16 hours ago
-
RE: Midea ASHP – how to set weather compensation
Many thanks @mphb and @cathoderay. Didn't expect so qui...
By iWolf , 18 hours ago
-
RE: British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
@jancold My day 1 of install over. It started at 7 wi...
By Lucia , 1 day ago
-
RE: Undersized Vaillant ASHP and abandoned by installer
Ps to the above. The requirements on the heat pum...
By JamesPa , 1 day ago
-
The greenhouse tomatoes have ,as usual, done well but t...
By Jancold , 1 day ago
-
RE: Locational electricity pricing
@transparent Phew! ok have skim read despite hectic d...
By Lucia , 1 day ago
-
'If you are not part of the problem there's good money ...
By AllyFish , 2 days ago
-
RE: Suitability of 45C flow temp with existing pipework
I've ordered a cheap borescope online and I'm going to ...
By Alex_N , 3 days ago
-
RE: Agile: average import cost vs other tariffs?
@tim441 Last year I ‘netted’ about £400 that way so I h...
By Toodles , 3 days ago
-
RE: Gas Combi to ASHP - Making sense of survey results and proposal.
@irmartini I think that @editor might sympathise with t...
By Toodles , 4 days ago
Latest Topics
-
Which liquid is used in the central heating loop?
By TRBob 10 hours ago
-
Interesting new product for woodburners - Recoheat
By Tim441 10 hours ago
-
alternative to Homely - HavenWise. Anyone used it?
By Tim441 10 hours ago
-
Calculating inverter size to match battery size
By Homonid 2 days ago
-
Agile: average import cost vs other tariffs?
By Tim441 4 days ago
-
Suitability of 45C flow temp with existing pipework
By Alex_N 4 days ago
-
Setback for Vaillant Arotherm Plus
By JWilliams89 4 days ago
-
By Toodles 4 days ago
-
By Jeff 5 days ago