@ngillam No way to control defrost cycle, but that isn't your issue it only increased 5C in 30 mins before the defrost started that isn't normal, its as if you were emptying the tank as it was trying to heat it back up.
@gary That's a good observation on emptying the tank!! I wasn't at home but will check with the other half if she was up earlier than planned. Once again, you're a fountain of knowledge.
Does my flow and return seem nominal to you?
Thanks,
Neil
Flow and return are fine, what isn't is the rate at which it is changing.
If I look at my HW run last night to get from 37C to 42C flow mine took 5 mins yours took 30 mins, hence my comment on was the HW being used at that time, if you have never had an issue before with HW heating up in that time period there is some other factor here. See what happens tomorrow morning I guess
Is this a pump issue? What jumps out at me on the chart at the the time of the defrost cycle is that the return drops dramatically first, and pulls the flow temp down slightly with it. Two minutes later the flow drops right down and only then looks like a normal defrost cycle, but rather than the flow temperature bouncing straight back up at the bottom of the cycle it takes few minutes and in addition the tank cools slightly as the return temp goes up several degrees before the flow temp goes back up. None of that looks normal, but I can't think of an obvious cause. The latter bit looks like the HW pump might be running while the defrost is taking heat out.
I would expect a HW cycle to stop when a defrost is needed (I don't HW at night though) and then just restart. There is meant to be enough volume in the primary circuit to enable defrosts.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
@harriup @gary I really do need some help with this one. It seems my HW never gets up to 47 target now due to defrost cycle running every hour. It gets to 41 or 42 before defrost cycle (the controller shows inverted colour heat pump symbol) which seems to draw down the tank temp to 38ish before defrost cycle ends.
Gary, your comment on slow warm up, yours seems a lot quicker than mine, I have a 5kw but even allowing for your step up in power it still seems very slow. Thinking about it a historical comment of yours mentions enough heat throughout the day. My tank once up to temp seems to dwindle back down quite quickly, it's a pre-plumbed cylinder 210L, I have timers set to 24hrs on pumps and can only think all this is related.
Can I ask what other ECODAN owners have there settings on for defrost and settings for HW duration etc.
My partner went out last night so I had to put the HW on constant to ensure she had hot water for shower, checked in the early hours when she came in and immersion heater had stepped in, disappointing!
Suggestions welcome, it's only 2 degs outside but defrost seems to be really hampering our comfort at present.
Thanks,
Neil.
check what the HW pump is set to on the cylinder it should have 3 positions it should be on 3 which is the highest setting
@gary Yep, it's on 3. Here are the last two hours of info:
Every hour it does this, this is the first winter we've gone through since heat pump installation so first time it's seen these temps.
Thanks,
Neil.
I have two of these in the control room, one looks to be UFH manifold side and the other DHW. I have it set 24hr because if it isn't then outside of times it won't send hot water to taps/showers or bath.
My DHW settings:
Max temp - 47
Drop temp - 7
Max op time - 90mins
Mode Restrict - 55mins
Similar to yours?
Thanks,
Neil.
So it will only run for 90 mins before shutting off and that currently isn’t long enough to reach your set temp
In the HW schedule on the FTC when is that set for? .
Is a pump running constantly if you have that Heatmiser thermostat set to on 24hrs a day?
If so I’m wondering if you are circulating HW round a pipe which would explain why your hot water is losing temp quickly and won’t be helping with the hot water heating up
- 26 Forums
- 2,149 Topics
- 47.1 K Posts
- 26 Online
- 5,667 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Electricity price predictions
I do think this is in part locational, there is far too...
By Scalextrix , 28 minutes ago
-
RE: is a home battery without an EV worth it?
@jamespa hmm sounds like a case of suppliers profiteeri...
By AdamK , 6 hours ago
-
RE: Who's your electricity provider and what's your tariff?
I am pleased to see the change. We definitely need t...
By Jeff , 11 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@jamespa Crossing sheep with kangaroos?
By Toodles , 14 hours ago
-
RE: Octopus tariffs - a quick comparison
I'm on Intelligent Go . Only since start of Feb. Before...
By Tim441 , 18 hours ago
-
RE: How Do I Know When the Hot Water Has Run Out?
@transparent that is a very interesting suggestion, tha...
By GrahamF , 1 day ago
-
RE: The good, the bad and the not that great – my heat pump installation
Sorry to resurrect this thread, but it is sort of relev...
By cathodeRay , 2 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
I missed your 22nd June post on this. I am sure it can ...
By cathodeRay , 2 days ago
-
Now posting on the right topic.... With general build...
By benson , 2 days ago
-
RE: How to waste energy (and time) playing with AI.
I’m sure like many software toys that it is addictive! ...
By Judith , 2 days ago
-
RE: Does anyone have experience of a smart water meter?
@judith With Anglia Water it was a compulsory upgr...
By TechnoGeek , 2 days ago
-
RE: Balancing financial efficiency and comfort using the Octopus Cosy tariff
We’re high energy users other than the ashp so the OVO ...
By Judith , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
Something isn't right here, you don't design ufh to wor...
By JamesPa , 3 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
No I'm not mining anything @drei but I am doing R&...
By Transparent , 3 days ago
-
RE: Rodents! A word of warning for heat pump owners
Wasps caused frequent tripping of my lighting circuit a...
By JamesPa , 3 days ago
-
RE: Ecodan & MelCloud scheduling
Yes, the 2 are separate. To add to the complex desig...
By HCas , 5 days ago
-
I should clarify that the FoxESS web interface is not l...
By Old_Scientist , 5 days ago
-
RE: Mitsu Wireless Controller and MelCloud
@robs Hi Rob, At the end of a note to Mitsu UK, thank...
By DavidAlgarve , 6 days ago
-
RE: Why so many sigenergi installer recommendations?
@adamk Tesla is a great option, it’s also one we instal...
By SAEnergy , 6 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As a potential heat pump customer, it would be good to ...
By Temperature_Gradient , 6 days ago