@ngillam No way to control defrost cycle, but that isn't your issue it only increased 5C in 30 mins before the defrost started that isn't normal, its as if you were emptying the tank as it was trying to heat it back up.
@gary That's a good observation on emptying the tank!! I wasn't at home but will check with the other half if she was up earlier than planned. Once again, you're a fountain of knowledge.
Does my flow and return seem nominal to you?
Thanks,
Neil
Flow and return are fine, what isn't is the rate at which it is changing.
If I look at my HW run last night to get from 37C to 42C flow mine took 5 mins yours took 30 mins, hence my comment on was the HW being used at that time, if you have never had an issue before with HW heating up in that time period there is some other factor here. See what happens tomorrow morning I guess
Is this a pump issue? What jumps out at me on the chart at the the time of the defrost cycle is that the return drops dramatically first, and pulls the flow temp down slightly with it. Two minutes later the flow drops right down and only then looks like a normal defrost cycle, but rather than the flow temperature bouncing straight back up at the bottom of the cycle it takes few minutes and in addition the tank cools slightly as the return temp goes up several degrees before the flow temp goes back up. None of that looks normal, but I can't think of an obvious cause. The latter bit looks like the HW pump might be running while the defrost is taking heat out.
I would expect a HW cycle to stop when a defrost is needed (I don't HW at night though) and then just restart. There is meant to be enough volume in the primary circuit to enable defrosts.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
@harriup @gary I really do need some help with this one. It seems my HW never gets up to 47 target now due to defrost cycle running every hour. It gets to 41 or 42 before defrost cycle (the controller shows inverted colour heat pump symbol) which seems to draw down the tank temp to 38ish before defrost cycle ends.
Gary, your comment on slow warm up, yours seems a lot quicker than mine, I have a 5kw but even allowing for your step up in power it still seems very slow. Thinking about it a historical comment of yours mentions enough heat throughout the day. My tank once up to temp seems to dwindle back down quite quickly, it's a pre-plumbed cylinder 210L, I have timers set to 24hrs on pumps and can only think all this is related.
Can I ask what other ECODAN owners have there settings on for defrost and settings for HW duration etc.
My partner went out last night so I had to put the HW on constant to ensure she had hot water for shower, checked in the early hours when she came in and immersion heater had stepped in, disappointing!
Suggestions welcome, it's only 2 degs outside but defrost seems to be really hampering our comfort at present.
Thanks,
Neil.
check what the HW pump is set to on the cylinder it should have 3 positions it should be on 3 which is the highest setting
@gary Yep, it's on 3. Here are the last two hours of info:
Every hour it does this, this is the first winter we've gone through since heat pump installation so first time it's seen these temps.
Thanks,
Neil.
I have two of these in the control room, one looks to be UFH manifold side and the other DHW. I have it set 24hr because if it isn't then outside of times it won't send hot water to taps/showers or bath.
My DHW settings:
Max temp - 47
Drop temp - 7
Max op time - 90mins
Mode Restrict - 55mins
Similar to yours?
Thanks,
Neil.
So it will only run for 90 mins before shutting off and that currently isn’t long enough to reach your set temp
In the HW schedule on the FTC when is that set for? .
Is a pump running constantly if you have that Heatmiser thermostat set to on 24hrs a day?
If so I’m wondering if you are circulating HW round a pipe which would explain why your hot water is losing temp quickly and won’t be helping with the hot water heating up
- 26 Forums
- 2,255 Topics
- 50.3 K Posts
- 323 Online
- 5,918 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Is it mad to think there should be a minimum SCOP for UK heat pump installs?
@jamespa, I don’t think that’s quite right. The regulat...
By Mars , 45 minutes ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
It is… in theory. But after some rather painful convers...
By Mars , 49 minutes ago
-
@agentgeorge That’s a ittle too inscrotumable for me… T...
By Toodles , 1 hour ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
We’re really excited to be recording a landmark Homeown...
By Mars , 2 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Thx, but Sven did the hardware development. My role (as...
By Mosibi , 2 hours ago
-
RE: Mitsubishi Ecodan R290 10kW performance
Are you using Havenwise for Hot Water? I have ...
By F1p , 3 hours ago
-
RE: PV Panels on roof in Conservation Area
@majordennisbloodnok Fnaargh, I was thinking about try...
By colinc , 3 hours ago
-
RE: Electricity price predictions
@jamespa Ah, you mean MPs that have not pro...
By Batpred , 4 hours ago
-
RE: Buying large amp bidirectional RCD and RCBO
Exactly @transparent , this type of RCBOs are not easil...
By Batpred , 5 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - though I realise I am a Canute, I have an...
By cathodeRay , 5 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
And just when I think great they’re coming next week to...
By Crimson , 7 hours ago
-
RE: Very Much Awake – Renewing the Heating Industry One Step at a Time
I feel that that attitude shared by Aadil from Heat Gee...
By Toodles , 8 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
and we have some of the strongest tidal flows anywhere ...
By Old_Scientist , 11 hours ago
-
RE: Radiator Sizing Dilemma: Vertical vs Type 33 for Low-Temperature Heat Pump Systems
This looks OK. Overall you have roughly the right amoun...
By Old_Scientist , 11 hours ago
-
RE: How can I programme a setback for my Samsung Gen6 8kW heat pump?
I'm not familiar with Hive thermostats/controllers, but...
By Old_Scientist , 12 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa mine seems changing albeit not by much, 3.21, ...
By AdamK , 1 day ago
-
@majordennisbloodnok The migration hasn't started in th...
By HCas , 1 day ago
-
RE: One room is colder than the rest of the house
@jamespa thanks for all the advice. Just so you know, ...
By AndrewJ , 1 day ago
-
RE: Daikin Octopus installation update - I saw my first defrost. 😍😂
My MMI is in the loft but I checked the pump flow rate ...
By RadWhisperer , 1 day ago