E121 error code on Samsung 12kw gen 6
I've had this error pop up after changing back from a flow temp only setting to a WC setting.Â
The fitting manual tells me to check PCB connector CN41 and it would appear nothing is plugged in there.Â
I've found videos of older Samsung units and it's a setting in the menu telling it to check but as there is no sensor it comes back as open circuit. It appears this might be what is happening with mine but I can't find the settings to turn it off. Can someone tell me how please?Â
I also appear to have an issue with the Teva out sensor as that is reading -50. Not sure if the two are connected. ThanksÂ
Â
Hi Craig,
When you changed to fixed LWT, I believe that you also changed the setting for the External Room Thermostat, 2091 or 2092.
I suggest that you check the settings and put them back to their original values.
When changing settings always keep a record.
Â
I did change these, but these settings are all back to what they were originally. I take photos on my phone of all settings before and after. That way they are date stamped too so I can go and check a particular day.Â
The part that I have changed that I believe is correct is Indoor Zone Option, standard temperature. I've changed this to indoor and not water outlet.Â
When changing this from Water Outlet to indoor, that is when I get the error.Â
@craig1980 It should be set on Water Outlet if you are using an external thermostat. If you are using the wired remote controller as your thermostat (the one in your airing cupboard), then you set it to indoor, but I believe when you do that there is an additional step required, quite what I don't know! Possibly FSV 2092 or 2093
Posted by: @craig1980I did change these, but these settings are all back to what they were originally. I take photos on my phone of all settings before and after. That way they are date stamped too so I can go and check a particular day.Â
The part that I have changed that I believe is correct is Indoor Zone Option, standard temperature. I've changed this to indoor and not water outlet.Â
When changing this from Water Outlet to indoor, that is when I get the error.Â
Hi Craig,
Is your system working? What are the present settings of #2091, #2092 and #2093?
Â
@mike-h I'd be happy to run it on the wired controller rather than external stats. I'm led to believe that's how they like to run. I'm not using room stats as on/off but as a back stop to WC to stop it going too warm.
@derek-m yes, system is working, still doing 20 secs - 8 min thing though. When the error shows is when you change "standard temperature" from water outlet to indoor. Although Mike has pointed out that it should be set on Water Outlet with my current set up using room stats.
As for #2091,2 and 3 they are all set on "Room temp. On/off or WL interlink on/off (water pump 3).Â
Hi Craig,
I have been giving the page from the manual that you posted, a closer inspection, and although, in typical Samsung fashion, the text is about as clear as mud, the diagrams throw a little more light on the subject.
The first diagram #2092 2 would indicate that when #2092 is set to the value 2, the heat pump will stop when the LWT achieves the value set by the WC curve (WL), but the water pump should continue to run for a further 1 minute.
When #2092 is set to the value 3, the water pump continues to run after the heat pump has stopped, the on - off of the water pump possibly controlled by the thermostat, but that is not specified.
When #2092 is set to the value 4, when the heat pump stops, the water pump should run for a further 3 minutes, then the water pump is stopped for 7 minutes, then runs for a further 3 minutes ad infinitum, until the heat pump restarts.
This seems to tie in to some extent to the way your system is stopping and starting.
The manual does not clearly state the value to which #2091 or #2093 should be set, so you may have to try different combinations.
I would suggest that you try changing #2092 to the value 2, and possibly also #2091. Then try the value 3 and then value 4, noting the operation each time.
Â
@derek-m I've now set 2091, 2 and 3 to Room temp. On/off or WL interlink on/off (water pump 2).
Am I right to assume this is value 2? I'm not sure how to tell which is value 1, 2, 3 and 4
@derek-m yeah, I'm in field settings in 2091 but there are 5 choices that you can scroll through.Â
Not use
Use signal only on/off
Use (signal on/off) or WL interlink off (water pump 1)
Use (signal on/off) or WL interlink off (water pump 2)
Use (signal on/off) or WL interlink off (water pump 3)
I wasn't sure which of these was which value 1-4. I'm guessing not use is 0 and the others are the corresponding numbers so pump 2 would be value 3.Â
Â
- 26 Forums
- 2,148 Topics
- 47 K Posts
- 35 Online
- 5,666 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: What crazy nonsense are inverter limits and why are they imposed?
No I'm not mining anything @drei but I am doing R&...
By Transparent , 2 minutes ago
-
RE: How Do I Know When the Hot Water Has Run Out?
What @jamespa said. Or: some DHW tanks have multiple te...
By HCas , 19 minutes ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
Yes, the 'global warming potential' GWP of R32 is quote...
By Temperature_Gradient , 33 minutes ago
-
RE: Rodents! A word of warning for heat pump owners
Wasps caused frequent tripping of my lighting circuit a...
By JamesPa , 40 minutes ago
-
This is one of my biggest bugbears these days, how AI d...
By cathodeRay , 2 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - @jamespa has anticipated my next steps bu...
By cathodeRay , 2 hours ago
-
RE: Electricity price predictions
The gas standing charge went up as some of the network ...
By Jeff , 15 hours ago
-
RE: Ecodan & MelCloud scheduling
Yes, the 2 are separate. To add to the complex desig...
By HCas , 2 days ago
-
I should clarify that the FoxESS web interface is not l...
By Old_Scientist , 2 days ago
-
RE: Mitsu Wireless Controller and MelCloud
@robs Hi Rob, At the end of a note to Mitsu UK, thank...
By DavidAlgarve , 3 days ago
-
RE: Why so many sigenergi installer recommendations?
@adamk Tesla is a great option, it’s also one we instal...
By SAEnergy , 3 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As a potential heat pump customer, it would be good to ...
By Temperature_Gradient , 3 days ago
-
RE: Octopus replacing the fixed 15p/kWh export rate with a market tracking one
@trbob I have just extracted the details for Agile Expo...
By Toodles , 4 days ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
The Ultimate Guide to Heat Pumps is less than a month a...
By Mars , 4 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@editor Hi Mars, We have just installed a Grant Aerona...
By GrahamF , 5 days ago
-
RE: Sanity check please. Battery storage and inverter sizing.
There are MCS guidelines about how close to the edge/ri...
By Old_Scientist , 5 days ago
-
RE: Balancing financial efficiency and comfort using the Octopus Cosy tariff
I estimated our usage on the following basis. The mos...
By Old_Scientist , 5 days ago
-
@editor Something changed in this last 12 months, they ...
By ASHP-BOBBA , 6 days ago
-
RE: Does anyone have experience of a smart water meter?
Just to give a sense of scale, I've used the CCW water ...
By Majordennisbloodnok , 7 days ago
-
RE: Powerwall 3 or Myenergi or something else?
We have a Tesla Powerwall 3, recently installed, so I m...
By Old_Scientist , 1 week ago