Cooling with Samsung Gen6 and Flow error
HI
I've got a Samsung gen6 ASHP, which I am trying to use for cooling. I have a large Harnitek fan assisted radiator in my main living room. Whenever I put the cooling on after about an 40 mins I get the e911 flow error.
I've checked the flow sensor its working fine, and on a cooler day a few weeks ago I put the heating on for a couple of hours and it works fine. So is this a pump problem, is it struggling due to the cold water and increase viscosity, thus can't pump it round effectively. Maybe a pump with bigger head would help?
Any thoughts would be much appreciated?
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
I see that these fan coil radiators either come with a two-way or three-way control valve built into them. What does the valve do? Well from a quick read of yhe operator instructions, it appears the control board can close off the valve in certain preset conditions (e.g. timer mode).
I suggest you look into your fan coil units (radiator) operator parameters to see what the current settings are. I take it that you are selecting cooling mode on the radiator as well as the ashp?
@iaack I've got cooling mode on the radiator selected, and I've disabled the valve mode on it, so they are open all the time.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@ecobaker I'm still thinking that something is triggering the valve to close.
In cooling mode on the rad, what are you setting as the rad target temperature? What is the typical room temperature and water flow temp. when the problem occurs?
Is the condensate outlet clear? Air cond units have float switches to monitor the condensate level and can shutdown the cooling function if they detect an unusual rise in condensate level.
@iaack The system isnt running long enough for any condensation buildup, also I've got the flow temp set above the current due point temp. I don't think its the radiator
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 72 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Midea ASHP – how to set weather compensation
Yes. They cost about £400 to buy or you might be able ...
By JamesPa , 23 minutes ago
-
RE: COP is not the only measure of efficiency
If that's the case then you are right to be sceptical, ...
By JamesPa , 35 minutes ago
-
Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
We’re pleased to announce that Havenwise are now joinin...
By Mars , 2 hours ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 3 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@ashp-bobba Well done for stepping in where most would ...
By JamesPa , 5 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
I have automated this decision. I have a heat pump with...
By jamespetts , 13 hours ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 14 hours ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 14 hours ago
-
RE: Buffers, hot water and cooling
I agree it seems like a lot of work particularly as its...
By JamesPa , 15 hours ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 19 hours ago
-
RE: 300 Liter Tank - Do I have to heat it all?
The size of DHW tank affects the anti-legionella cycle....
By Transparent , 20 hours ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
@scalextrix Name plate capacity
By HCas , 23 hours ago
-
RE: Solar Thermal DHW and ASHP
I was originally contemplating a solar thermal installa...
By jamespetts , 23 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
My system installed in July 2024 has produced 6.4mWh in...
By jamespetts , 24 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@judith thanks for your suggestions. Starting from col...
By GrahamF , 2 days ago
-
RE: Inventor (Midea) Heat Pump short cycling advice
I switched to "fan coil mode" to be able to set water t...
By immunity , 2 days ago
-
RE: DESNZ doing a survey which asks the right questions!
Without a survey their only source of data is probably ...
By JamesPa , 2 days ago
-
RE: Can you help with our research: solar panels, EV chargers, home batteries, heat pumps?
Just done your survey!
By Judith , 3 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
@cleardene-ashp just thinking about your issues here. Y...
By Judith , 3 days ago