Choice of heat pump - Help needed - Vaillant Arotherm versus Samsung versus Logic Air versus Grant Aerona
I have a quote from an installer with a choice of 4 heat pumps:
Vaillant Arotherm 3.5 kW
Samsung R290 5 kW
Logic Air R32 4 kW
Grant Aerona 6 kW
The house has a heat loss of about 3.3 kW. Price-wise there is surprisingly little difference.
I have a couple of questions:
1. I have air bricks which I believe would prevent using the R290 heat pumps since the heat pump would be next to an outside wall. How do manufacturers expect these heat pumps to be used since it seems like a very common scenario to have air bricks and a heat pump next to an outside wall.
2. With the first two ruled out and the Grant seemingly a bit rubbish (inefficient, noisy and ugly), that leaves the Logic Air. By the specs the Logic has very good SCOP values and is very quiet but I'm struggling to find real world opinions on it. Does anyone have it istalled or have an opinion on what it is like?
Thanks

I'm far from an expert, @dorkypark, but my understanding is that openings like air bricks are only an issue if within 1m of the bottom of an R290 heat pump. As a question to everyone reading this, if you have an air brick inside that area, is it possible to get it moved further along the wall? @Dorkypark, if moving an air brick along wouldn't cause any problems to the way the building ventilates itself, is that something you might have space to do?
Looking at the list you gave, Samsung are getting a bit of a panning on this forum for their rather high-handed customer service attitude. Irrespective of the quality of their kit, I'd avoid them on that alone, personally.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; suus solum profundum variat"
I'm far from an expert, @dorkypark, but my understanding is that openings like air bricks are only an issue if within 1m of the bottom of an R290 heat pump.
The Vaillant requires 2.1m to 3.1m. See the attached picture. My air bricks seem to be spaced about 1.5m apart so I guess it would be a case of blocking them up rather than moving them. Probably easier to get an R32 heat pump!
Posted by: @dorkyparkthe first two ruled out and the Grant seemingly a bit rubbish (inefficient, noisy and ugly), that leaves the Logic Air. By the specs the Logic has very good SCOP values and is very quiet but I'm struggling to find real world opinions on it. Does anyone have it istalled or have an opinion on what it is like?
Inefficient noisy, not sure where that statement comes from?
How efficient the heat pump is down purely to system design, many things screw with this figure - positive or negative. Especially the design temperature, zones, use of a buffer or volumiser etc.
If it was as simple as pick the best make, the whole thing would be easy. Best to work through the design advantages or shortfalls and not get too fixated on makes or models, that's the last decision to make, not the first.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
@dorkypark, welcome to the forums! To be blunt, there’s not a huge difference between most branded heat pumps themselves. What really sets them apart is the quality of their controls and, more importantly, the competence of the installer. If the system is well-designed and the installer understands the ins and outs of the heat pump they’re fitting, you’ll likely end up with a solid system regardless of the brand.
That said, I encourage homeowners to heavily consider after-sales support from the manufacturer. On that basis, I often steer clear of Samsung, as their manufacturer-side support is notoriously poor. Grant and Vaillant, on the other hand, have strong reputations for reliability and support. I can’t comment on Logic Air.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @johnmoInefficient noisy, not sure where that statement comes from?
I guess I'm wrong about the efficiency but the sound power level of the Grant is 65 dB vs 54 dB for the Vaillant and 52 dB for the Logic. More than 10 dB makes a big difference, though who knows if they used the same measurement method.
Thanks @johnmo and @editor for the information. I'll certainly be reading up further about what makes a successful heat pump installation (beyond simply aiming for a low flow temperature...).
@dorkypark please start by vetting your installer(s) and check their reviews and see if they can give you references to recent projects they've completed. Low temperature systems are the way to go for inefficiency, but you need that system designed and installed correctly.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor dont you mean efficiency (not inefficiency) Mars? 🙂
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
We’ve just had a Vaillant installed (literally finished today) and the installer (Heatgeek elite) and Vaillant support has been excellent. So personally an established brand versus an unknown of LogicAir is an easy decision. I agree with discounting Samsung and Grant.
But you still need an installer who knows his stuff and such a wide choice makes me question Why?
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
Posted by: @judithunknown of LogicAir
OP missed the make, Ideal from the model name 'LogicAir'
So not really unknown
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.

Posted by: @editor...
To be blunt, there’s not a huge difference between most branded heat pumps themselves. What really sets them apart is the quality of their controls and, more importantly, the competence of the installer. If the system is well-designed and the installer understands the ins and outs of the heat pump they’re fitting, you’ll likely end up with a solid system regardless of the brand.
...
@dorkypark, I don't think it's possible to overstate what @editor has said here.
As I'm sure you're aware, a heat pump is just a great big fridge, extracting heat from the air outside and heating water. How that water is then used is the clever bit, and tailoring it to a particular home is the key. Design and implementation, not brand, and that requires an installer who knows what he or she is doing and is prepared to be professional about it.
It's perfectly technically possible to put a factory-tuned Ferrari V8 engine into a Reliant Robin. It doesn't mean you'll end up with a good result at the end of the exercise.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; suus solum profundum variat"
@majordennisbloodnok As I understand it, a Robin Reliant is hardly the most stable vehicle even with its’ own intended engine on board! Now, a V8!? Eeeek! What about a conversion to a 3 motor E-Reliant? 🤯 Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 56 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 20 minutes ago
-
RE: What is the best strategy for operating a very oversized heat pump?
Something else... that works for some people... LG ha...
By Tim441 , 26 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
OMG, the attached schematics (even with incorrect room ...
By BAMi , 1 hour ago
-
RE: Setback savings - fact or fiction?
@cathoderay I see you are continuing to misquote from t...
By SUNandAIR , 2 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
So I turned my thermostats down last night And w...
By Joshua , 2 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 3 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 4 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 14 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 17 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 19 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 21 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 22 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 23 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 3 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 4 hours ago
-
SolarPV tables / online calculator
By MichelleC 10 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 22 hours ago
-
By Toodles 2 days ago