Hi Everyone,
Some time ago I carried out some research on buffer tanks, LLH and PHE, and watched some quite interesting YouTube videos, posted by people in the heating industry.
The conclusion was that heat pumps, and any of the above items do not make a good combination. Let me explain.
Heat pumps come with their own water pump, which unless you have a particularly large or expansive system should be adequate to pump the heat energy around your home. Installing any of the above equipment necessitates the requirement for a secondary water pump.
For PHE to transfer sufficient heat energy from the primary circuit to the secondary requires the LWT from the heat pump to be higher than would be necessary, and hence reduces overall efficiency. You are also running a secondary pump.
Buffer tanks and LLH would work okay if the water flow rate going in, was matched by the water flow rate coming out. This is hardly likely to be the case, since the heat pump will probably be varying the speed of the internal water pump, and hence the flow rate, to maintain the specified DeltaT. The end result is probable mixing of the flows within the BT or LLH, with resultant loss of heat energy getting to the heat emitters, and the controller or user raising the LWT to compensate.
If you need to know if your system has sufficient volume to cope without a BT or LLH. Measure the size of each radiator and note how many panels, then go to the Screwfix or similar website and find a radiator of the same size and type, look up the specification to find the volume in litres. Add up the volume of all your radiators and compare it with the minimum volume requirement specified for your heat pump. If the system volume is too low than add a volume chamber, or if you already have a BT, then remove one inlet and one outlet pipe and fit a connection pipe in between. Then plug the two ports on the BT.
Hive….. poor you. Quite possibly the worst on/off stat you can get.
Whereabouts in the property is the Samsung controller? Please don’t say ‘in the loft’
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@derek-m Thanks for your thoughts on buffer tanks. My research about them produced similar conclusions. The minimum volume for a Samsung 12kW ASHP is 50 litres and our radiators are well over 80 litres. This assumes that the heat pump can always access the secondary circuit during a defrost cycle, which Fergal claims it can't. If true, that sounds like a serious design fault. My concern with following your advice to bypass the buffer tank is that it may void my warranty, which Fergal says it will, even though the manual claims that a buffer tank is not required "...unless working on a very small house/flat..". Also my system suffers from short cycling which the buffer tank is supposed to eliminate.
Posted by: @mike-h@derek-m Thanks for your thoughts on buffer tanks. My research about them produced similar conclusions. The minimum volume for a Samsung 12kW ASHP is 50 litres and our radiators are well over 80 litres. This assumes that the heat pump can always access the secondary circuit during a defrost cycle, which Fergal claims it can't. If true, that sounds like a serious design fault. My concern with following your advice to bypass the buffer tank is that it may void my warranty, which Fergal says it will, even though the manual claims that a buffer tank is not required "...unless working on a very small house/flat..". Also my system suffers from short cycling which the buffer tank is supposed to eliminate.
Maybe you should ask Fergal why it is short cycling.
Posted by: @bataltoit might be in the manual (or was) but they've [Freedom/Fergal] told me it doesn't void the warranty as long as the system can work without. They add the LLH as it saves doing any actual calculations on if the system needs one or not. By adding it they by default don't need to check if it's needed - they said almost all of their installers are plumbers, so they just don't have the knowledge or capability to do that kind of technical analysis beforehand.
Posted by: @mike-hMy concern with following your advice to bypass the buffer tank is that it may void my warranty, which Fergal says it will, even though the manual claims that a buffer tank is not required
I rest my case. Not only do Freedom think their installers are thick (can't do sums), they think their end users are thick as well. It must be frightfully jolly being so clever when all around you are so thick.
I think the end result is we are are on our own here. Freedom clearly haven't got a clue. The manufacturers constantly hide and/or obfuscate information. No wonder 10% or less of installation are achieved without flaws. All credit due to @derek-m and all the others who have done their own research and made their findings available here for others to benefit from.
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay in fairness to freedom, they are B2B not B2C. They assume (I think correctly) that most installers don't actually understand what they are installing and make it as fool proof as possible for them to minimise call outs/troubleshooting for the end user. Is it the most efficient for the end user? No. Is it the easiest for the installers, yes. Actually trained people who understand these things are few and far between. Most fitters come from the world of gas boilers. Chuck it in, set it to 70 degrees and take the cash - no one cares about efficiency with gas (for some reason). The fact is my original fitter could have easily removed/not installed the LLH, but he didn't know what it did and wasn't sure what impact it might have. So in the end he refused to do it. It was Freedoms technical support who directed me to someone who would. They said themselves that pretty much every customer was ignorant of their system and how it worked. They wouldn't fit a LLH in an ideal world. An individual person is smart, but people are stupid. And people want hot rads and an easy life. Most couldn't tell you the flow rate or volumes of their rads and 99% of plumbers couldn't either. Most people with a gas boiler couldn't tell you their flow temperature and thats a problem.
Now gas isn't cheap I think we'll see a change and a lot of flow temperatures come down. But even now the focus in all media is about lowering your thermostat AND NOT lowering your flow temperatures. Arguably the latter will save far more gas, cost less and deliver a better consumer outcome. I would easily take a punt that 90% of housing stock in this country with gas could run at a flow temperature of 50 or 55 degrees with NO issues. But one thing I've noticed is people like red hot radiators, the idea they wouldn't be scalding to touch seems to be an anathema to many.
@batalto - I respect Freedom's right to be B2B (they said the same thing to me, when they were telling me to get lost) but that doesn't mean I think it is enlightened. There are other fields I operate in that involve technical matters of varying degrees of complexity and I generally find things work best when manufacturers/suppliers are prepared to talk to informed end users. Elsewhere I said I considered Freedom are arrogant, and it doesn't get much more arrogant that 'pretty much every customer was ignorant of their system and how it worked'. That's every customer, so that includes me and you as well!
I have a theory about why people like hot rads, I suspect it may be because hot rads also radiate as well as convect heat, and so you feel a sun like warmth when near one, and who doesn't like the warmth of the sun.
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay to be fair, I was pretty ignorant lol. It's only through self learning that I understand. I imagine most consumers wouldn't bother to understand the intricacies of weather compensation or low loss headers - nor would they want to, frankly.
For what it's worth, I managed to get through to Samsung technical support and had a call back from one of their engineers. The system volume that matters from a warranty point of view is the fixed volume - it does not include radiators with TRVs, only radiators that are on all the time plus the pipework. So he appears to back Fergal's stance. When I asked him how other manufacturers managed without buffer tanks, he said he used to work for one of those and they had lots of problems with their invertors breaking down. I think I will be keeping my buffer tank. Thanks for all the comments.
Just have to sort out the short cycling now......
@mike-h - none of this makes much sense. You might as well ask these 'engineers' what the best way to Tipperary is. I have a plate heat exchanger rather than a low loss header of buffer (and Freedom seem to think they are interchangeable, at least on Midea systems) and one of the 'good' points about a PHE is it keeps the clean primary circuit separate from the dirty secondary rad circuit. One consequence is that the ASHP primary circuit circulating volume is small, just ASHP to airing cupboard and back, maybe 6m each way, plus whatever is in the PHE or DHW heating coil. Go figure...
Midea 14kW (for now...) ASHP heating both building and DHW
And here are the figures: bore capacity of 28mm pipe (copper, mine is plastic, but will be near enough the same)= 0.54L/m x 12 = 6.48L plus whatever is in the PHE, which is in use >23 hours/day as DHW is on a 1300-1400 only timer, say 2L max, total 8.48L.
@batalto (and others) - I've just had a look at Freedom's latest Midea installation manual, available here, only to find the kiss your warranty goodbye message is there, albeit with slightly different wording:
"Every system must have hydraulic separation between the primary (heat pump) and secondary (heating circuit) pipe work. This can be via a buffer tank, low loss header or plate heat exchanger. If you install the unit without hydraulic separation, you will void the warranty."
Arrgghh...
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayAnd here are the figures: bore capacity of 28mm pipe (copper, mine is plastic, but will be near enough the same)= 0.54L/m x 12 = 6.48L plus whatever is in the PHE, which is in use >23 hours/day as DHW is on a 1300-1400 only timer, say 2L max, total 8.48L.
@batalto (and others) - I've just had a look at Freedom's latest Midea installation manual, available here, only to find the kiss your warranty goodbye message is there, albeit with slightly different wording:
"Every system must have hydraulic separation between the primary (heat pump) and secondary (heating circuit) pipe work. This can be via a buffer tank, low loss header or plate heat exchanger. If you install the unit without hydraulic separation, you will void the warranty."
Arrgghh...
I think that you may need to ask Freedom to clarify exactly what they mean by 'hydraulic separation', since of the three items listed, only a PHE will provide true hydraulic separation, in that the liquid in the primary circuit is completely separate from the liquid in the secondary circuit. Both a buffer tank and a LLH use the same liquid.
-
First time wall mounting an ASHP
2 weeks ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
3 weeks ago
-
Rodents! A word of warning for heat pump owners
1 month ago
-
Retrofitting: moving to ASHP old oil boiler in large old property - experience/advice please on MSC calcs
2 months ago
-
How to choose Towel Rails for an ASHP
2 months ago
- 26 Forums
- 2,300 Topics
- 51.6 K Posts
- 228 Online
- 5,965 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Firstly you are getting your units mixed up which is a ...
By JamesPa , 42 minutes ago
-
RE: Electricity price predictions
Until people understanding the problem with electricity...
By Diverted.Energy , 43 minutes ago
-
RE: Buffer tank bypass on EDF Ideal heat pump installation
I would bypass the buffer tank in one of flow or return...
By JamesPa , 56 minutes ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira
I agree with all of that. 220 pages is perhaps 210-215...
By JamesPa , 1 hour ago
-
RE: Why Millions of UK Homes Struggle With Heat Pumps
One of those brilliant ideas that is obvious with hinds...
By Lenny , 1 hour ago
-
RE: Don’t Install a Heat Pump Until You Read This
@davidnolan22 Perhaps you could post some more info a...
By JamesPa , 1 hour ago
-
RE: Help me keep the faith with my air source heat pump installation
OK. I have 2.8 for DHW and 3.4 for space heating runni...
By JamesPa , 1 hour ago
-
RE: 10kw heat pump run in 24*7 data?
Some observations: 1. I for one don't know the Vailla...
By cathodeRay , 2 hours ago
-
Heat Pump on Flat Roof Low Frequency Noise from Detached Neighbor
Hi, I have been noticing a steady 120Hz noise inside ...
By People_Noise , 9 hours ago
-
RE: Commencing on an ASHP Installation Process
Given that this thread ultimately turned out to be a di...
By Sheriff Fatman , 11 hours ago
-
Ecodan - Flow temperature spiking causing shutdown
Hi everyone, looking for some help. I am in a new bu...
By Gl3484 , 12 hours ago
-
Solis AI is on the right track to leverage the battery:...
By Batpred , 14 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Thanks James, its honestly hard to keep it tog...
By Crimson , 15 hours ago
-
RE: Extend the colder range of the weather compensation curve?
Thanks for replies. That's good to hear and wanted to ...
By TheBinMan , 15 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: KevB Manufacturer: Ideal Model: 5kW ...
By KevB , 17 hours ago
-
RE: DHW heat loss through pumps.
Hi @ngillam I don't have anything as sophisticated for ...
By Marzipan71 , 19 hours ago
-
RE: Has anyone seen this problem before? Huge anticycling times
For the information of others. Vaillent came today, che...
By jamesh , 20 hours ago
-
RE: Here is my heat pump installation with questionable COP in Italy
Hi, and welcome to the forum. I cant quite u...
By JamesPa , 1 day ago
-
I signed up to Havenwise control on the day after the h...
By Sheriff Fatman , 1 day ago
-
That's not always the case.Let's see what they say once...
By Transparent , 2 days ago