@cathyem1 - this isn't exactly beginner's level stuff, but it may nonetheless help you get your head around some of this. This is my system running on weather compensation over a recent seven day period as shown on the bottom horizontal axis (I have fairly detailed monitoring that collects this data):
Now at first glance I am sure it makes no sense. However, lets look at certain elements:
In the upper (temperatures) chart
(1) the dark brown purple line stuck on around 20 - that's my room temperature. Fairly steady, weather compensation working as it should.
(2) the green line under the room temperature line - that's the outside air temperature (OAT). Ranges between zero and ten degrees.
(3) the partially obscured red/orange line - that's the SET (target) LWT, as set by the weather compensation curve, not by me). Note how it changes in response to the OAT. When it gets colder outside, the SET LWT goes up, when it's warmer outside, it goes down.
(4) The teal/turquoise line - that's the ACTUAL LWT. For now, just notice how most of the time it is pretty close to the SET LWT. The heat pump is doing its job, without any intervention from me, room stats, timers, magic controllers, woo crystals or anything else (apart from one adjustment control I have which fine tunes the weather compensation curve, but that's another subject for another day for more advanced use). The only thing I did was set the ends points of the weather compensation curve, the heat pump controls did the rest.
Also out of interest in the bottom energy chart note how variable the energy in (used) per hour is (green bars), depending on the OAT, without corresponding large increases in energy out (heat supplied to the house, the red bars). This reflects the extra effort needed in cold weather, the heat pump has to work much harder to produce heat, and as a result its performance (COP, the blue line) falls sharply. They key take away is just how variable the performance is: this is how we know that when it gets milder as spring approaches, our energy use (and bills) will go down.
Edit: I should add that in cold weather there is a double hit: not only does the COP plummet because it is cold, the demand also increases because it is cold. Result: big bills. But equally in mild weather, the COP (performance) increases greatly and the demand is far less. Result: tiny bills. Over a heating season, the two cancel each other out.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathyem1I'm keen to save some money
Cathy, once you've followed the instructions from @cathoderay to get the WC curve set correctly,
there comes a point where further investigation of System Optimisation is effort being spent with diminishing returns.
Let's look forward in time to see what else you could do to save money:
1: Spent a bit of time to better insulate those pipes, and the attached valves.
We haven't yet seen a photo of the external pipework.
That could be throwing away 20% of your heat energy before it even gets into the house!
2: Reduce the cost of the electricity you're using to run the heat-pump.
Even without having PV Solar Panels, there is still a strong argument in favour of battery storage.
With a Time of Use (ToU) tariff, you could then recharge the battery from the grid during cheap periods.
Better still, the inverter could be wired so as to continue running some equipment during a power cut
- the heat pump
- a kettle
- lights
Only you can decide those priorities.
But I'm suggesting these issues with your husband in mind.
Save energy... recycle electrons!
Thanks for the photos.
That's in the top 10% of external HP installations which I've seen. 🙂
But it still looks like rain could enter through the gaps in the insulation for the two anti-freeze valves and the isolator with the blue handle above them.
Any rain which goes between the insulation and the pipe will absorb precious heat,
and then dump it on the ground!
I also don't understand why you only appear to have one lever-valve to isolate the external unit.
Save energy... recycle electrons!
@transparent the installer is returning soon to replenish the glycol and sort out my solar thermal so i’ll mention these points to him then. Thank you again
Posted by: @cathyem1I’ve changed both ends of the curve by 1° today and i’ll see how we get on.
That's the way to go. Over time you will get closer and closer to the ideal setting for your home. Don't be thrown by days when external factors like wind chill (happens to homes as well as people), solar gain (sun's warmth also contributes to warming your home) and human activity eg lots of cooking push the room temp a bit this way or that, just let it happen. There are ways of dealing with these things but for most people they are not necessary. For now, I suggest just concentrate of getting the weather compensation curve right, and of course making progress with @transparent's suggestions.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathyem1the installer is returning soon to replenish the glycol
If you are to have glycol added to the system, then I question why have also had (relatively expensive) anti-freeze valves fitted. 🤔
The anti-freeze valve detects when the system fluid is on the point of forming ice, and then opens to empty your pipework into the gravel below the heat-pump.
It should only occur if the software-controlled de-frosting method has failed to remove ice from the compressor circuit and radiator grid of the external unit.
Your heat-pump then stops working (of course) but it does at least avoid damage occuring.
I wouldn't usually expect to see anti-freeze valves on a system with glycol, because they would be dumping that chemical into the soil.
Glycol also has a lower thermal capacity than water.
Adding it to your system will reduce its ability to move heat into the house.
Thus the heat-pump has to work slightly harder and is less efficient.
Everything you're learning about your heat pump is demonstrating that there are balances to be made between alternatives.
It's the role of your installer to explain these rather than just implementing their own personal preference.
Save energy... recycle electrons!
@transparent The glycol is for the separate solar thermal water heating system not the ashp.
🤣 🤣 🤣
@cathoderay I’ve just realised the date on the control panel is now correct but the time isn’t. Could you tell me how to change the time please. I have looked through the user information and cannot find it. Thank you.
- 21 Forums
- 1,960 Topics
- 42.5 K Posts
- 55 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 16 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@johnr An extra rad was installed in the lounge when th...
By BAMi , 19 minutes ago
-
RE: SolarPV tables / online calculator
By Gary , 51 minutes ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Yes, that sounds correct. I would say try both options...
By Old_Scientist , 10 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 11 hours ago
-
RE: Setback savings - fact or fiction?
The great thing about science is that it doesn't care o...
By JamesPa , 12 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 14 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 15 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 18 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 19 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 20 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 23 hours ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 24 hours ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
-
RE: Baxi Air Source Heat Pump tips and tricks please
@cathyem1 - thanks for the update. Let us know how it g...
By cathodeRay , 2 days ago
-
RE: Low COP and unevenly heated rooms with 12kW Samsung AE120MXTPEH / AE260TNWTEH
@editor But do you wear your peaked cap the right way r...
By Toodles , 2 days ago
Latest Topics
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 16 minutes ago
-
SolarPV tables / online calculator
By MichelleC 7 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 19 hours ago
-
Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
By BAMi 22 hours ago
-
By Toodles 2 days ago
-
Solid manhole cover within r290 exclusion zone
By dbrb2 2 days ago
-
Towel rails. An unexpected final hurdle
By Davesoa 2 days ago