Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Balancing a low loss header/buffer tank on a Grant Aerona 2 13kw r32 system
We can ignore the house heating load. Yes it's low on the ch side, it only needs 23° - 25° in the ufh to get to 19° in the room.
Grant ashp lowest setting is 23°, so for the time being we can ignore the wc curve and just set it to a temp. In our case we are having to set it to 28° - 30° to get ch side to the correct setting.
We have run through all the settings from setting the grant to its lowest, mid and highest flows and then taking the pumps though the 6/7 settings they have. Allow it to settle and check temp and nothing seems to make any difference.
I am now running the system on grants highest setting and two of the pumps are turned off. HP set tp 30°. This is what we get ORDER ABCD
Not sure exactly what the picture shows as there appear to be 8 readings. If its the bottom temp readings that are of interest, the they seem to be 29.2, 28.3, 27.5, 19.2 so A-> C now a bit less than 2. Isn’t this an improvement? D seems to indicate deltaT across UFH now 8C, which at current OAT seems quite high, so may be a problem when OAT drops but equally might not matter. However thats perhaps because the flow rate is low as you have only 1 pump running.
TBH I think you have run through all the simple options and Im not sure I can add much more. I have the impression you understand the principles, so its a bit of a case of play and see what happens, or wait until someone comes along with a magic solution, if indeed there is one without spending any significant money.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa sorry my bad. Yes it's the middle readings that have a temp probe. The are ordered as ABCD
I've just turned on all the pumps and set them to high load and noticed that B went down and D came up. So the CH is taking from the tank.
Once it stopped changing so much I lowered the speed of the CH pumps to 1 and will check again.
(I'm sure I had the HP set at its highest speed, but I didn't turn off any pumps last time I tried.)
If the above goes back to major differences then I'll just run the one pump tomorrow and if if things settle down.
- 27 Forums
- 2,733 Topics
- 64.2 K Posts
- 172 Online
- 7,139 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Questions about A2A for heating as well as cooling
Thank you for that very helpful and thorough response! ...
By donciccio , 2 hours ago
-
RE: Aircon - in listed buildings
@etchedpixels thanks for giving such a full and helpful...
By GrahamF , 16 hours ago
-
RE: Acond heat pump failed after four years - diagnostic quote £940 plus VAT
Another idea if the above don't work - there are compan...
By downfield , 18 hours ago
-
RE: Love veg, hate watering cans
They have their downsides but boreholes are great in th...
By ian33a , 19 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist The service engineer powered down the ex...
By Papahuhu , 20 hours ago
-
RE: Issue with Samsung Cascade System
@jamespa It's a funny system, but was out only option l...
By Renewables345 , 24 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Thanks, I like the chart, very helpful and this will de...
By baroquebank , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Production resumed to normal once the issue ...
By MK4 , 2 days ago
-
RE: Digest of UK Energy Statistics
That sounds painful. It would be much better to charg...
By Transparent , 3 days ago
-
Hole diameter is small but hole length is also very sma...
By bobflux , 3 days ago
-
RE: Are Wind Turbines Really “Losers”?
We were sailing near a wind farm in the North Sea last ...
By Jeff , 3 days ago
-
@trebor12345 The idea is to ensure that Powerwall knows...
By Toodles , 3 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
'hard limited' could be in 'admin' password protected s...
By JamesPa , 4 days ago