(@heatgeek)
Estimable Member Member
Joined: 5 months ago
Posts: 111
 

Posted by: @jamespa

Presumably mixing of return water with flow water to the emitters (and thus a reduction of ft to emitters) will however still occur if the primary pump throughput is less than the secondary,

This could be mitigated by putting a one way check valve on the top input so that flow is only downwards. Can't think of any detrimental effects.

Private individual. No affiliation with commercial "Heat Geeks" of same coincidental name.


   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2393
 

Posted by: @heatgeek

This could be mitigated by putting a one way check valve on the top input so that flow is only downwards. Can't think of any detrimental effects 

Or of course not having a buffer at all! 

Would an installer that wants to fit a buffer unnecessarily because 'thats what we do' or because of warranty reasons be prepared to fit a three way buffer with a one way check valve.  I suspect this would be a tiny minority!

It's ab interesting thought experiment though.

This post was modified 12 hours ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
SUNandAIR
(@sunandair)
Noble Member Member
Joined: 2 years ago
Posts: 487
 

Posted by: @heatgeek

 

 

3 Port Buffer Tank

@heatgeek I kind of get it… but aren’t you still in the same situation of having excess flow temp water at the bypass entering the buffer at circa 23 LPM.

In so doing, raising the return temp and narrowing the DT… ergo prompting a raising of the flow temp and inducing the cycling.?

Only now there are 2 pumps?

(It isn’t like it’s just trickling into the buffer, is it? And the return pump will want to maintain the flow rate, for sure!)

Also on 4 port systems I’m not convinced that PWM pumps can cope with matching actual water flow rates, at variable speeds on either side of the hydronic circuits - since there is already believed to be a compromise or resistance to flow on the emitter side. Yet that’s possibly the very reason why buffers are being proposed. 

Is there a proper definition as to why buffer tanks are being specified and what exact problem is expected to be overcome?

 

 

 

This post was modified 10 hours ago 2 times by SUNandAIR

   
ReplyQuote



Page 23 / 23
Share:

Join Us!

Trusted Installers

Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.

✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available

👉 Find your installer now!

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security