Avoid the Heat Pump Villain: Why Low-Loss Headers and Buffers Can Sabotage Your Heat Pump's Efficiency
Next year, we have another episode of our podcast dedicated to the buffer tank. It’s going to be a real in-depth plunge, and I’m assembling a really competent panel to get definitive answers and examples.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @editorNext year, we have another episode of our podcast dedicated to the buffer tank. It’s going to be a real in-depth plunge, and I’m assembling a really competent panel to get definitive answers and examples.
That will be fun!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Yes, it should be fun, depending on your definition of the word. 😂 I was aiming for a really balanced discussion. Ironically, every installer I know who strongly advocates for buffers has declined to join, including over 15 Aira engineers. That’s a strong message in itself.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Posted by: @editor@jamespa Yes, it should be fun, depending on your definition of the word. 😂 I was aiming for a really balanced discussion. Ironically, every installer I know who strongly advocates for buffers has declined to join, including over 15 Aira engineers. That’s a strong message in itself.
That's a shame as I was looking forward to the fireworks, but as you say it's a strong message which needs to be heard.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @editorevery installer I know who strongly advocates for buffers has declined to join, including over 15 Aira engineers. That’s a strong message in itself
Very telling!
Midea 14kW (for now...) ASHP heating both building and DHW
@mars - have you considered 'empty-chairing' the buffer tank advocate. It would send a very powerful message throughout the video without you having to repeat it.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
My Heat Pump consumes 40% more Energy than the Gas boiler it replaced
Having kept my Gas consumption records before switching to a Samsung Heat Pump I can compare Energy Consumption between Gas Boiler and Heat Pump.
The Energy consumed on Sept,Oct, and Nov 2024 by my Heat Pump was 42% ,33% and 37% of the Energy consumed by my Gas Boiler between Sept and Nov 2021.
With Electricity costing 3.8 times the Cost of Gas the Heat Pump becomes uneconomic.
My Heat Pump is consuming ~40% more Energy than the Gas boiler it Replaced. ( and that's before the energy Increases !!)
Can anyone supply the name of an affordable Software Design package for Heat Pumps comparable to SPICE in Electrical Engineering.
Definitive mathematical solutions using differential equations .................... competent modelling !!
With definitive mathematical answers ,I will then decide if Buffer tanks, Heat Ex-changers , Volumisers are useful or not!
Perhaps you should sort out /have someone else sort out your system and then you’ll will know what matters. I know several posters here have told you what to do.
Then you can model it knowing some data points. Until then it is GIGO.
Our system is running a cop in region of 5 and the cost is considerably lower than our gas previously. So yours is demonstrated to be poor. Just fix it, modelling not needed.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC
Posted by: @iantelescope
@editor
My Heat Pump consumes 40% more Energy than the Gas boiler it replaced
Having kept my Gas consumption records before switching to a Samsung Heat Pump I can compare Energy Consumption between Gas Boiler and Heat Pump.
The Energy consumed on Sept,Oct, and Nov 2024 by my Heat Pump was 42% ,33% and 37% of the Energy consumed by my Gas Boiler between Sept and Nov 2021.
With Electricity costing 3.8 times the Cost of Gas the Heat Pump becomes uneconomic.
Shouldn't the headline be My Heat Pump costs 40% more to run than the Gas boiler it replaced
The heat pump energy input (kWh, I assume) is only about 40% of the gas consumption but the big difference in unit cost between electricity and gas makes electricity more expensive (unless you get on a heat pump friendly tariff). Add in an annual heat pump service at ~£250 and the situation will look even worse.
Running costs:
Yes John , I stand corrected again .You are of course perfectly correct .....forgive my anger ..........
I meant to say that My Heat Pump costs 40% more to run than the Gas boiler it replaced.
This 40% figure excludes the fuel increases !!
Building Heat Pump costs
Again ,you are perfectly correct in pointing to the building costs of circa £16000 .
The Scottish Govt having repaid some £3000 MY up front Building costs are currently ~£13000 !!!
Service costs:
Because of the extensive Sawing , hammering and general abuse of the Pipe Work I have had BOTH of my pipe circuits Flushed at a costs of ~£600.
Further damage has been done by 18 months of "Short Cycling " caused by my Heat Pump being wrongly adjusted for a 10 minute cycle .
The 10 minute cycle was originally attributed to the Water Volume in the primary circuit being insufficient.
Further damage has undoubtedly been caused by running the Primary Water circuit with an "insufficient WATER VOLUME" .
The Water Volume was increased by my Installer advised by Samsung when fitting a 50 L "Volumising tank" .
The Justification for the 50l tank was later modified to that of reducing the build up of ICE on the fins of the Heat Pump itself.
Measurements: Lets get numerate!
COP has a limited meaning .............what Should ALSO be measured is the REAL COP !
REAL COP is the Ratio of Energy available at the start of the Radiator Circuit , kWh ,to the total input Energy, kWh.
REAL COP = Energy available at the Start of the Radiator circuit / Total Input Energy:
Here the Blue line represents the COP at the Heat Pump Output . Here an average of 3.06 over the last two or more months !!
Here, the RED line represents the REAL COP at the Start of the Radiator circuit.: Here an average of 2.4 over the last two more months !!
A REAL COP of 2.4 is totally uneconomic when the ratio of Electrical Energy to that of Gas is 3.8 :1 !!
The king is in the altogether .....................Heat Pumps have many unspoken problems.
@editor Will Brendon Uys be on the panel? I understand he is head of design within British Gas and I've seen videos with him in advocating against buffers in most situations, so I'd be interested to why they are still being included in quotes without any obvious reason.
I had BG do a quote in the past couple of weeks which I have accepted, but only after asking for the buffer to be removed. It's a single zone house, 22mm copper pipework between floors, 15mm to radiators and enough volume for defrost, so no reason that I can see for a buffer.
The initial reason I was given was that Vaillant require a buffer but after I pointed out that plenty of Vaillant's are installed without one the surveyor (who was very good otherwise, no complaints there) quickly removed it and I saved just under £600 and a huge amount of space in a cupboard.
@sandy Brendon will almost certainly be on it, unless there’s a scheduling issue. He’s been driving change at BG, but interesting what you’ve mentioned about your recent quote… glad to see to the buffer was removed though. Well done for flagging this.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
-
British Gas Heat Pump Installation Complaint
4 weeks ago
-
Heating Turned Off but Radiators Still Warm
1 month ago
-
Samsung Heat pump with Yonos Pico circulating pump running all the time
2 months ago
-
Samsung 5kW R32 Monobloc Gen 6 ASHP
2 months ago
-
Ideal Logic 10kW Heat Pump Pipes Noisy and Very Expensive to Run
10 months ago
- 26 Forums
- 2,323 Topics
- 52.1 K Posts
- 227 Online
- 5,979 Members
Join Us!
Podcast Picks
Latest Posts
-
@f1p, sorted, on a android phone Just swaped from ...
By @sand , 3 minutes ago
-
RE: Electricity price predictions
The Renewal Obligation is the early subsidy that was gi...
By Jeff , 8 minutes ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
No worries Modbus may also work over the dongle WiFi...
By Batpred , 30 minutes ago
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
@trebor12345 Good data, will examine more closely befor...
By JamesPa , 37 minutes ago
-
RE: Here is my heat pump installation with questionable COP in Italy
@jamespa Sorry for the late reply, I apologize for the ...
By materox345 , 1 hour ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
With UFH downstairs, I couldn’t let my Cosy6 go for it ...
By AgentGeorge , 1 hour ago
-
-
RE: Trying to understand my Nibe F1245
First of all you have one of the best geothermal heat p...
By greenlight , 2 hours ago
-
@batpred your signature says you have an Ohme Pro wha...
By AgentGeorge , 2 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
@editor Yes BUT that was 3 years ago installed in Janua...
By rob heatpump bob , 12 hours ago
-
Thanks for your response. I have UFH downstairs and ...
By GeorgeA , 13 hours ago
-
RE: Grant Aerona Short Cycling
Hi, I have a Grant 10kW (nominal 9kW for the UK), whi...
By MikeFl , 15 hours ago
-
RE: Home energy storage & battery register
2 days uninterruptible power supply (at the moment) wit...
By Batpred , 16 hours ago
-
We have a Vaillant aerotherm with sensocomfort. We have...
By Newbie , 17 hours ago
-
@trebor12345 Yes, expect defrost cycles to initiate at ...
By IaAck , 17 hours ago
-
I would probably have them in white as that would match...
By Grantmethestrength , 18 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Owners
@sim0n0 Sorry to hear that. Putting the past aside w...
By JamesPa , 18 hours ago
-
RE: MelCloud "Mixing tank temperature"
This post, on my 'diary' thread, might be of interest i...
By Sheriff Fatman , 18 hours ago
-
RE: 10kw heat pump run in 24*7 data?
UPDATE: Very happy wife, since 24*7 I've actually had t...
By jeegnesh , 18 hours ago
-
RE: Heat Pump Training vs. Real-World Installation
Thank you for doing that, @editor, and for writing this...
By Majordennisbloodnok , 20 hours ago