Avoid the Heat Pump Villain: Why Low-Loss Headers and Buffers Can Sabotage Your Heat Pump's Efficiency
You are indeed correct, it may depend upon what the water pump(s) are doing.
I know that some of the heat pump controllers continue to run the water pump for a number of minutes after the compressor and fan(s) have stopped, and may also periodically operate the water pump for several minutes to equalise the water temperature around the heating system.
From observing my own heating system, it takes approximately 4 minutes to heat the radiators to the temperature calculated by the controller, after which the boiler and water pump is stopped. During colder weather conditions the required radiator temperature may be in the 40C to 45C range, and it may only take 10 to 15 minutes for the radiator temperature to reduce by approximately 5C, at which point the boiler and water pump is restarted. During milder weather conditions the radiator temperature may only need to be in the 30C to 35C, so it may then take 30 to 60 minutes for the radiators to cool sufficiently for the boiler and water pump to be restarted.This keeps the IAT at 21C +/- 0.2C under all conditions.
The point I was trying to make is that the location of the LWT and RWT sensors is very important, particularly if the water pump(s) do not run continuously when the heat pump is no longer producing thermal energy. Continuously operating the water pump to prevent the LWT and RWT sensors cooling too quickly probably would reduce the cycling frequency, but would use more electrical energy and may also transfer thermal energy from indoor to outside. I'm not certain if any controllers operate in this manner. It would be interesting to see how the different heat pumps control their water pumps and also the actual location of the LWT and RWT sensors, and the effect this may have upon the frequency at which cycling takes place.
As I have stated previously, one possible way to reduce cycling frequency could be to set the WC curve such that it causes the IAT to start to increase before the heat pump reaches the point when frequent cycling is likely to occur, and then use a room thermostat to start and stop the heat pump rather than the LWT and RWT sensors.
All Modern Heat Pumps will Cycle when operating BELOW the Minimum Inverter Power .
Here is a detailed graph of the Power my Heat Pump consumed during the evening of 23-March-24.
The Cycling Time, Run_Time ( Mark *) + OFF_Time ( Space *) = ~ 10.12 Minutes.
Here is a more detailed Graph of the Power consumed during the evening of 23-March-24, showing the Run Times.
The instantaneous RUN Time is , here, ~5.0 Minutes.
Here is the FFT of the Power consumed during the evening of the 23-March-24 , showing the Cycling Frequency.
The Frequency Maximum , here provides an Average Cycling Time of 9.96 Minutes.
The First Harmonic of the Cycling Frequency provides a Check, giving a 5.03 Minutes.
The RUN TIME CALCULATION **
My Heat Pump has a 50 Litre Buffer Tank fitted Across the output ports of my Heat Pump.
When Operating Below the Minimum Inverter Power of 2.5 Kw my Heat Pump is Cycling.
The Energy input into the Buffer Tank , when operating at the Inverter Minimum Power , kWh = Minimum_Power ( kW ) X Run_Time (Seconds)
The Energy Input Heats 56 Litres of Water to the Temperature Difference Across the Buffer, Delta_T .
The Energy Required to Heat 56 Litres of water to a Temperature of Delta_T is:
Energy Required to Heat 56 Litres of Water to ~4C = 4.18 X 50 X 4
Therefore, the 2.5 kW Minimum Power X Run_Time = 4.18 X 50 X 4
Therefore, Run _Time ( Seconds ) = (4.18 X50 X 4 ) /2.5 Seconds.
OR
Run_Time = (4.18 X 50 X 4 ) /(2.5 X 60 ) Minutes.
My Calculated Run_Time is Therefore , 5.57 Minutes
My Instantaneous Measured Run Time is ~5.00 Minutes.
My Average Cycle Time ( from FFT ) is 9.96 Minutes.
My Average Run_Time ( from FFT ) is 5.03 Minutes.
Is my Heat Pump STILL Short Cycling ?
* Sorry to use the Electrical Mark to Space Ratio Terminology
** Check the MCS Calculations in :
All Modern Heat Pumps use an Inverter to control Heat Pump Water Power.
All modern Heat Pumps have a Minimum Power BELOW which the HEAT PUMP WILL REVERT to Cycling.
The DECC, in 2012, produced a Report on the Effects of Cycling on the Heat Pump COP:
The DECC Report was produced at a time when Heat Pumps with Inverter Power control were in their infancy.
The Report is however still useful when operating an Inverter Heat Pump BELOW it's Minimum Inverter Power.
The Reports Recommendations are shown in the following :
Recommendations:
1) Recommended that Air Sourced Heat Pumps should be designed for a Minimum Run Time of 6 Minutes.
2) Run Times of ~ 8 Minutes gave COP Values close to the "Catalogue" Steady State Values.
3) 4 Pipe Buffer Tanks show a promising method of achieving the required Minimum Run Times without the need for "Excessive Buffer Volumes".
The Buffer here used was a Buffer fitted Across the Output ports of the Heat Pump :
Note also the Calculation of the Size of Buffer required:
Further note that these calculations are for an older control system, but , none the less valuable in the demonstration of a Buffer Tank fitted Across the Heat Pump Water output.
Also note that by present standards, Very Poor COP that were achieved.
Why can't Heat Pumps be Mathematically DESIGNED and tested using a program like H2X ??
Buffers as Batteries?
With the introduction of Timed Low Cost Tariffs , e.g. Octopus "Cosy" , Buffer Tanks/Volumisers can now be used to Store Energy during "Cheap periods" for use during more Expensive periods.
Buffers as Back-Up Heaters?
During winter, I need a Back-Up Heater for Only four weeks per year.
To meet this Limited Requirement I could either
Install a new, larger, Heat Pump
OR
Install a couple of Immersion Heaters into my Buffer Tank.
My Samsung already has a complete Back-Up Heater for just such a Requirement.
"Short Cycling ", Water Volume and Heat Pump Sizing?
My Heat Pump continues to "Short Cycle " with a RUN TIME period of ~ 5 Minutes.
The DECC Report says that Heat Pumps should NOT be designed for a RUN TIME of Less than 6 Minutes!.
Both Cycle Times and RUN _Times are determined by the Volume of Water within the pipe system, AND, the Minimum Inverter Power from the Heat Pump.
If the Volume is insufficient then a Buffer Tank/Volumiser should be installed.
If the Minimum Inverter Power is Too large then a Smaller Heat Pump would be required.
A smaller Heat Pump would, however, require a Back-Up Heater during Winter!
P.S Why can't Heat Pumps be Mathematically DESIGNED and tested using a program like H2X ??
@derek-m The carel controller in my ASHP allows me to specify three pump modes: Normal, Demand, Continuous...
Normal - pump shuts off when setpoint is reached. Use this when driving a buffer tank.
Demand - pump will 'sniff' for a bit to see if the water in the circuit has dropped below the setpoint. No idea when you'd use this mode.
Continuous - pump runs whenever the call-for-heat is active. Compressor/fan come on as required under the control of the PID in the heat pump.
I use mine in continuous mode as I only have the single pump and I don't have room stats.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Design & Measurements of Heat Pump Performance?
Wall Thermal Conductivity, U ...............abuse ?
Given my own experience, where my "installer" Altered the Wall Thermal Conductivity to justify the use of a particular Heat Pump Can I again ask the Question :
Why are Thermal Wall Heat Conductivities NOT Measured ?
Measurement would require the use of a standard Electric Fire attached to a Power Meter with TWO Thermometers , One indoor, the other Out Side.
From Experience, measuring U is far more accurate and Untainted by installer behaviour.
Measurement of the Performance of Heat Pumps?
Heat Pump Performance should be measured with an in -Water Power Meter !
Heat Pump Performance , COP should be Measured at the Start of the Piping System AND NOT at the Heat Pump itself.
Design
Heat Pump Systems should be designed with a Thermal Software e.g. H2x .
Measurements against the design?
Having completed a Software design the Performance MUST be tested against the Design!
Any deviations between the Design and Performance will bolster customer Confidence.
p.s. As William Thomson, Lord Kelvin , said " if ye canny Measure it .....ye don't understand it"
My Heat pump REAL COP ( that measured at the start of the Radiator pipe circuit ) and Heat Pump COP ( as shown by the Heat Pump itself ) are for 28/29 March:
-- Attachment is not available --
My REAL COP is therefore , circa 2.2 , while my Heat Pump COP is circa 2.9.
The Difference between My REAL COP and the Heat Pump COP is reflected in the Energy loss between the Heat Pump and my house:
-- Attachment is not available --
The Average Loss is therefore circa 26% without using the HOT WATER TANK.
"Short Cycling" is shown in the FFT of the Heat Pump Power consumption :
-- Attachment is not available --
With the Peak representing a Cycle Time of circa 10.11 minutes.
Peak Frequency = 157 Hz on a run of 95274 Seconds duration gives a Wavelength of ~95274/157 Seconds , or ~10.11 Minutes.
The Run Time is shown in the following :
-- Attachment is not available --
With the RUN Time here of 4.5 Minutes.
Conclusions:
1) With the DECC Report recommending a Minimum 6 Minute RUN TIME My Heat Pump is "SHORT CYCLING".
2) With the DECC Report recommending a Minimum 16 Minute CYCLE TIME My Heat Pump is "SHORT CYCLING".
Measuring Cycle and Run Times on a Heat Pump
I record the Power Consumed by my Heat Pump on a Daily basis.
For example , on 30 th March I get:
Clearly, my Heat Pump is suffering from "Short Cycling". The Question is "How Much"?
I can examine the "Short Cycling by taking the Fast Fourier Transform :
But , again , the "Short Cycling " , although much more prominent , with a peak at ~150 Hz , is still very Noisy!.
Also, the Run Time component of the cycle time is completely lost in the Noise!
Using the FFT as a filter for the Cycle Time gives:
Now a beautiful Noise free Sinusoid giving the exact Cycling Time as 10.12 Minutes!
On using the FFT as a filter for the RUN TIME :
Again a Beautiful Noise free Sinusoid giving the exact RUN TIME as 4.3 Minutes.
All Graphical work was performed using "SCILAB " on a LINUX PC.
Many congratulations to "Dassault " in France for rebuilding Scilab after a absence of Three Years!
Scilab will , probably work on "Windows" , probably!
ian
Is my Heat Pump Too SMALL for Winter AND TOO BIG for Spring?
My Heat Pump does Not supply ENOUGH Power HEAT DURING Winter .
-- Attachment is not available --
Notice the HEAT PUMP is permanently ON , Controlled by the Inverter.
My Heat Pump does Supplies TOO MUCH Power IN Spring!.
-- Attachment is not available --
Notice the HEAT PUMP is "Short Cycling" , Controlled under Cycling !.
The RANGE of the Inverter , between Minimum Inverter Control and Maximum Inverter Power is TOO SMALL!
The Solution Would be to provide a Backup Electric Immersion Heater inside my Volumiser Tank.
Why Do Manufacturers NOT Provide the MINIMUM AND MAXIMUM INVERTER POWER?
Heat Pumps: Hypothermia & Bankruptcy
Having spent ~£14k on a Heat Pump I am now , a 76 year old , Am I Now faced with Heat Pump Hypothermia ?:
-- Attachment is not available --
My "Installer" has now been STUCK-OFF for the THIRD TIME with the NIC making the comment that
" YOU ARE NOT GOING TO LIKE THIS ........................BUT NOTHING CAN BE DONE "
The NIC have said that they are "Sorry" but that they have exhausted their efforts by the application of Further SANCTIONS against my "installer".
My Blood pressure is , on average, over the Winter 155/84 as shown in the following graph:
-- Attachment is not available --
I am paying ~£165 per month for the running costs of this Heat Pump !.
I am paying ~£42 per month for the "loan " repayment for a "Drawdown " Payment for this Heat Pump!
Heat Pumps: Hypothermia & Bankruptcy
Frenchmen, Germans and Blushing Heat Pump "Engineers!"
Over the past two years, visiting "Engineers" have produced the most extraordinary comments .
A visiting French Samsung "Engineer" produced the following classic:
"Only the Germans REALLY Understand How Heat Pumps work!"
A visiting Blushed to the roots of his hair saying to his colleague :
" Perhaps you cannot set the Water Temperature because of what is being displayed on the Front Screen !"
The Blushing "Engineer" had previously been found to have falsified my house Energy requirements to justify the installation of the wrong heat Pump.
Another "Engineer" said that :
"WE will Repair and , if necessary replace your Heat Pump IF YOU AGREE TO THE REMOVAL OF ALL METERING". I Declined the offer.
A visiting NIC "Engineer" said that "I , the user, should NOT INTERFERE WITH THE SETTINGS INSTALLED BY MY INSTALLER ".
A Visiting TRIO OF ENGINEERS , including a NIC Engineer succeeded in completely stopping my Heat Pump when trying to simultaneously set the Water Temperature using "Weather Compensation " AND Explicitly set the water Temperature using the Heat PUMP Field bit settings" :
" Long Silence ........" followed by the comment that " You, ( ME The USER ) HAVE INTERFERED WITH The Settings of the previous French Heat Pump "Engineer".
I reset, the , now faulty, Heat Pump about 30 minutes after the Trio left with their tails between their legs.
Finally, A visiting Father & Son pair of "Engineers" :
Father , Shouting : " I have never, in 30 Years experience with Heat Pumps ever installed a buffer Tank......."
Son , Quietly : " I am well aware that fitting a Buffer Tank is used to reduce the excessive "Short Cycling" that you clearly have experienced , my only comment would be the Size and position of the Buffer/Volumiser tank".
Why Do some, ( MOST !) "Heat Pump Engineers" , have such a low opinion of themselves , their industry, and their fellow competitor "Engineers"?
It's a bad day for buffer tanks. @heacol is officially the Head of Domestic Heat Pump Design Net Zero at British Gas. He's tasked with getting BG engineers to improve design and installation quality. It's a big move on Brendon's part, and hopefully, one that will lead to a speedier transition to higher ASHP installation quality on a mainstream basis.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Follow our sustainability journey at My Home Farm:https://kirstenandmars.com
-
6 Red Flags to Avoid When Considering a Heat Pump Installation
2 weeks ago
-
Ecodan DHW Settings missing
7 months ago
-
Hacking a heat pump to increase heating range over 38C
7 months ago
-
Running my heat pump for half the cost of a gas boiler
8 months ago
-
Samsung 5kW R32 Monobloc Gen 6 ASHP
9 months ago
- 25 Forums
- 1,612 Topics
- 34.8 K Posts
- 46 Online
- 1,887 Members
Join Us!
Latest Posts
-
RE: British Gas versus Octopus: Two possible heat pump routes - how to evaluate them?
@jancold My day 1 of install over. It started at 7 wi...
By Lucia , 9 hours ago
-
RE: Undersized Vaillant ASHP and abandoned by installer
Ps to the above. The requirements on the heat pum...
By JamesPa , 9 hours ago
-
The greenhouse tomatoes have ,as usual, done well but t...
By Jancold , 9 hours ago
-
RE: Locational electricity pricing
@transparent Phew! ok have skim read despite hectic d...
By Lucia , 9 hours ago
-
RE: How to Solve Mould and Mildew Issues in Renovated Properties
The answer if you’re doing a major renovation is a MVHR...
By Judith , 9 hours ago
-
RE: In the middle of an ASHP installation - a few questions
@toodles thanks. What I have is an old and dirty lookin...
By benson , 11 hours ago
-
RE: Will heat pump heat hot water without increasing the temp in my home?
Do you have a reference for that directive @toodles ? ...
By Transparent , 11 hours ago
-
RE: Calculating inverter size to match battery size
I expect your Seplos kit came with some guidance as reg...
By Toodles , 13 hours ago
-
RE: Determining correct flow rate for a heat pump
It’s clear from what you say, above and what we have ex...
By SUNandAIR , 17 hours ago
-
RE: Midea ASHP – how to set weather compensation
@mphb - thanks, a useful link. Using google translate, ...
By cathodeRay , 21 hours ago
-
'If you are not part of the problem there's good money ...
By AllyFish , 22 hours ago
-
RE: Suitability of 45C flow temp with existing pipework
I've ordered a cheap borescope online and I'm going to ...
By Alex_N , 2 days ago
-
RE: Ecodan - flow rates, sensors, settings
Hi @rhh2348 , coming late to this thread as our Ecodan ...
By SUNandAIR , 2 days ago
-
RE: Agile: average import cost vs other tariffs?
@tim441 Last year I ‘netted’ about £400 that way so I h...
By Toodles , 3 days ago
-
RE: Gas Combi to ASHP - Making sense of survey results and proposal.
@irmartini I think that @editor might sympathise with t...
By Toodles , 3 days ago
-
RE: Heat pumps don't work: debunking myths & misconceptions
I applied for my G99 last November. Largely as a resul...
By IanMK13 , 3 days ago
-
Setback for Vaillant Arotherm Plus
Currently our Vaillant Arotherm Plus is set in fully We...
By JWilliams89 , 3 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
Unfortunately @burtis James is right. MCS is the Gove...
By Transparent , 4 days ago
-
-
RE: How can I programme a setback for my Samsung Gen6 8kW heat pump?
@simonh Im not sure how useful they are but Ive attache...
By bontwoody , 5 days ago
Latest Topics
-
Calculating inverter size to match battery size
By Homonid 1 day ago
-
Agile: average import cost vs other tariffs?
By Tim441 3 days ago
-
Suitability of 45C flow temp with existing pipework
By Alex_N 3 days ago
-
Setback for Vaillant Arotherm Plus
By JWilliams89 3 days ago
-
By Toodles 4 days ago
-
By Jeff 4 days ago
-
By dssr 5 days ago
-
Solar Edge Inverters, returns recycling policy
By AllyFish 6 days ago