ASHP Heat Loss Calculations with Log Burner
Hi Folks
I've been an avid follower for a while and found some really useful info so thanks to all contributors.
We've had a heat loss survey conducted, and it has got a huge (2000W) requirement for the small lounge which has a wood burning stove installed.
The surveyor said it was due to it being classed as an 'open flue' which it technically is when the burner is lit (and kicking out heat 🤔), but the rest of the time the air vent is shut which I thought would be similar to an air brick in the wall (i.e. not taken into consideration).Â
Removing the wood burner from the calcs cuts the power requirement in half which is much more achievable with either simple UFH or rad.Â
The wood burner is a nice feature and we won't be relying on it for heat, but it seems a very expensive luxury!
Has anyone come across this before? Should we just remove the log burner (at least from the calcs!) or is the open flue calculation correct?Â
Hi @AndyOrchard2, I would definitely challenge your surveyor on that one. Chances are whatever software they are using only has an open flue/open fire option. A log burner with stove plate draws very little combustion air, hence why units of less than 5 or 6kW (I forget which) don't require fixed ventilation inlet openings. Compared to stoves, open fires draw much more air up a chimney, several times more, due to the induction effect of warm air rising from the fire drawing in colder room air. That's why log burners are so much better space heaters, they are more efficient at combustion, and also much less cold air is drawn into the room the stove is in from cooler areas, because they only ingest air required for combustion with almost no induction of air.
We have an ASHP + 5kW log burner in the sitting room, the log burner was not factored into our heat loss estimate, as it's room sealed (or as good as) when not lit and the vents closed. Our sitting room came out at 1.5kW heat loss, but has two large glazed windows + two external walls. We changed two existing 1992 double panel rads for longer, lower, and higher capacity Stelrad K2s. They do the job nicely without the log burner on with CH flow temperature set to a maximum of 45degC.
One of the concerns of oversizing ASHPs is minimum turn down capacity. An ASHP will spend the vast majority of time in operation below maximum nameplate kW rating on part load. ASHPs modulate down to about 25%. Too large a unit with a minimum output higher than the house heating demand will then cycle on and off as the only way it can reduce output below minimum turn down. This isn't that efficient as the compressor is not chugging quietly away under inverter control, it is switching on and off, and each time it starts it's playing catch up and working a little harder, due to pre-programmed on-off cycle times that limit the number of compressor starts per hour.
If you have a log burner you have cost-effective secondary source of heating, which can be used to boost temperature quickly if need be, or to supplement your ASHP during particularly cold spells. Remind your installer of that and ensure they 'right size, but don't oversize'Â
Thank you @allyfish for the really useful reply. Â
It does seem a case of 'computer says no' which could be an MCS thing as the calcs work fine without the flue.
The driver appears to be the air changes as the calculator assumes 5 air changes an hour when including an ‘open flue’ compared to 1.5ac/hr without.
Your insight is great proof that an effective ASHP set up can be achieved with a log burner in situ given the ability to close vents etc., so hopefully some pragmatism can be applied to the model – although I’m not holding my breath…
Overall, it increases the space heating demand for the entire house by 27% (from 3.65kw to 4.76kw) so pretty fundamental to the overall design, but maybe not a show stopper based on your comment re ASHPs being able to modulate down c.25% which would be about right for real world comfort!
The original design was set at 50C flow temp too (as a result of this fandango around the flue) so your caution of oversizing is even more of a reason to tweak the model.
Your response was exactly what I was hoping to read so thanks again – much appreciated.
-
First time wall mounting an ASHP
1 week ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
3 weeks ago
-
Rodents! A word of warning for heat pump owners
1 month ago
-
Retrofitting: moving to ASHP old oil boiler in large old property - experience/advice please on MSC calcs
2 months ago
-
How to choose Towel Rails for an ASHP
2 months ago
- 26 Forums
- 2,289 Topics
- 51.4 K Posts
- 348 Online
- 5,949 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Sorry if it wasn't clear. I have set all TRVs open, th...
By AndrewJ , 3 minutes ago
-
Hi all, I have an Ecodan 5kw ASHP with 210litre pre-p...
By ngillam , 11 minutes ago
-
RE: Electricity price predictions
Whilst agreeing that we need to place storage batteries...
By Transparent , 20 minutes ago
-
As promised, I am posting back with an update. I even...
By Eliuccio , 25 minutes ago
-
RE: Confusion over Octopus Tariffs
That's sounds great. I have no ASHP, but 15kwh storage....
By Batpred , 30 minutes ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Locked environments are difficult to manage, it also me...
By Batpred , 36 minutes ago
-
RE: Ecodan ASHP Low COP and Unstable Compressor Frequency
its a little odd that your UFH comes back warmer than t...
By davidnolan22 , 3 hours ago
-
RE: Do Heat Pumps need to start up at Full Power?
@steelbadger Attached is the plot for various parameter...
By Toodles , 4 hours ago
-
RE: Has anyone seen this problem before? Huge anticycling times
Hi all, I had a 15kw installed 3 weeks ago. The past we...
By jamesh , 5 hours ago
-
Adia Therma - 'autopilot for heat pumps'
Thought I'd pop this one in here as the Adia proposal a...
By seatonian , 19 hours ago
-
RE: Mitsubishi Ecodan R290 10kW performance
Don't know answer to final question. Your contract p...
By JamesPa , 20 hours ago
-
RE: 10kw heat pump run in 24*7 data?
0.65. Heating curve of course depends on rad...
By JamesPa , 20 hours ago
-
RE: New Fogstar 15.5kWh upright solution
Ah, it seems PACE BMS are easy to source on AliExpress,...
By Batpred , 20 hours ago
-
RE: Vaillant water pressure gauge vs Analogue gauge
@jamespa Agreed I don't feel concerned about this, espe...
By jeegnesh , 22 hours ago
-
RE: Heat Pumps Without Grants: Would You Have Installed One & Will You Now?
@toodles Yep, and it is not even a sticking plaster ...
By Jeff , 23 hours ago
-
RE: Renewables & Heat Pumps in the News
I agree, imperfect systems like voting for politicians ...
By Batpred , 1 day ago
-
RE: Gov wants to alter our FIT contracts from rpi to cpi
The consultation is just part of the normal process for...
By Jeff , 1 day ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@mairie - Your constituency member, Dr Zubir Ahmed MP, ...
By Transparent , 1 day ago
-
@transparent @old_scientist Quick update, I submitted...
By Batpred , 2 days ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Lol. I know they CAN be calibrated, it’s just ...
By Crimson , 2 days ago