ASHP Heat Loss Calculations with Log Burner
Hi Folks
I've been an avid follower for a while and found some really useful info so thanks to all contributors.
We've had a heat loss survey conducted, and it has got a huge (2000W) requirement for the small lounge which has a wood burning stove installed.
The surveyor said it was due to it being classed as an 'open flue' which it technically is when the burner is lit (and kicking out heat 🤔), but the rest of the time the air vent is shut which I thought would be similar to an air brick in the wall (i.e. not taken into consideration).
Removing the wood burner from the calcs cuts the power requirement in half which is much more achievable with either simple UFH or rad.
The wood burner is a nice feature and we won't be relying on it for heat, but it seems a very expensive luxury!
Has anyone come across this before? Should we just remove the log burner (at least from the calcs!) or is the open flue calculation correct?
Hi @AndyOrchard2, I would definitely challenge your surveyor on that one. Chances are whatever software they are using only has an open flue/open fire option. A log burner with stove plate draws very little combustion air, hence why units of less than 5 or 6kW (I forget which) don't require fixed ventilation inlet openings. Compared to stoves, open fires draw much more air up a chimney, several times more, due to the induction effect of warm air rising from the fire drawing in colder room air. That's why log burners are so much better space heaters, they are more efficient at combustion, and also much less cold air is drawn into the room the stove is in from cooler areas, because they only ingest air required for combustion with almost no induction of air.
We have an ASHP + 5kW log burner in the sitting room, the log burner was not factored into our heat loss estimate, as it's room sealed (or as good as) when not lit and the vents closed. Our sitting room came out at 1.5kW heat loss, but has two large glazed windows + two external walls. We changed two existing 1992 double panel rads for longer, lower, and higher capacity Stelrad K2s. They do the job nicely without the log burner on with CH flow temperature set to a maximum of 45degC.
One of the concerns of oversizing ASHPs is minimum turn down capacity. An ASHP will spend the vast majority of time in operation below maximum nameplate kW rating on part load. ASHPs modulate down to about 25%. Too large a unit with a minimum output higher than the house heating demand will then cycle on and off as the only way it can reduce output below minimum turn down. This isn't that efficient as the compressor is not chugging quietly away under inverter control, it is switching on and off, and each time it starts it's playing catch up and working a little harder, due to pre-programmed on-off cycle times that limit the number of compressor starts per hour.
If you have a log burner you have cost-effective secondary source of heating, which can be used to boost temperature quickly if need be, or to supplement your ASHP during particularly cold spells. Remind your installer of that and ensure they 'right size, but don't oversize'
Thank you @allyfish for the really useful reply.
It does seem a case of 'computer says no' which could be an MCS thing as the calcs work fine without the flue.
The driver appears to be the air changes as the calculator assumes 5 air changes an hour when including an ‘open flue’ compared to 1.5ac/hr without.
Your insight is great proof that an effective ASHP set up can be achieved with a log burner in situ given the ability to close vents etc., so hopefully some pragmatism can be applied to the model – although I’m not holding my breath…
Overall, it increases the space heating demand for the entire house by 27% (from 3.65kw to 4.76kw) so pretty fundamental to the overall design, but maybe not a show stopper based on your comment re ASHPs being able to modulate down c.25% which would be about right for real world comfort!
The original design was set at 50C flow temp too (as a result of this fandango around the flue) so your caution of oversizing is even more of a reason to tweak the model.
Your response was exactly what I was hoping to read so thanks again – much appreciated.
-
ASHP install contract and BUS grant money
6 days ago
-
Compute heat loss from energy used
6 days ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
1 week ago
-
Savings - using Weather Compensation & Time of Use Tariffs
2 weeks ago
-
Heat Pump starting current
1 month ago
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 46 Online
- 2,277 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
@jamespa thanks, it's way off of the MCS performance es...
By big_si , 12 minutes ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@jamespa Agreed. I think it’s a case of much over muchn...
By Mars , 2 hours ago
-
@eliuccio Unfortunately, whilst I agree with a lot of...
By JamesPa , 3 hours ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@bami I think if the heat loss documentation matches a ...
By bontwoody , 3 hours ago
-
RE: What is the best strategy for operating a very oversized heat pump?
@jamespa I'm afraid that's over my head but if anyon...
By IRMartini , 4 hours ago
-
RE: Setback savings - fact or fiction?
And here in case any one wants it is the code I used in...
By cathodeRay , 4 hours ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 4 hours ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 6 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 8 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 10 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 22 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 1 day ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 1 day ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 10 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 11 hours ago
-
SolarPV tables / online calculator
By MichelleC 18 hours ago
-
By Toodles 2 days ago